Is 18/2 Doorbell Wire Safe for Wiring 110v to SSR?

  • Thread starter Thread starter iambo
  • Start date Start date
  • Tags Tags
    Wiring
Click For Summary

Discussion Overview

The discussion centers around the safety and suitability of using 18/2 doorbell wire for wiring 110v to a solid-state relay (SSR) controlling a device that draws 2 amps. Participants explore various aspects of wire gauge, safety standards, and practical considerations in high voltage applications.

Discussion Character

  • Debate/contested
  • Technical explanation
  • Conceptual clarification

Main Points Raised

  • Some participants express concern that 18 gauge wire is not safe for use at 120 volts, suggesting it is typically rated for lower voltages.
  • Others argue that while 18 gauge wire can handle low currents, it is advisable to use a fuse for safety.
  • One participant mentions that in factory settings, wiring for 120 volts typically does not use anything smaller than 14 gauge, citing safety standards.
  • There are discussions about the practicality of using larger gauge wires, with some suggesting that using a larger wire can be beneficial for short runs.
  • Participants share experiences about wiring practices in residential versus industrial settings, noting that larger wires can be cumbersome but may be necessary in certain situations.
  • One participant emphasizes the importance of adhering to local building codes and having electrical work inspected.
  • Another participant raises the need to ensure that the insulation of the wire can withstand 120V AC, highlighting the importance of checking the wire jacket for specifications.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the safety of using 18/2 doorbell wire for the specified application. Multiple competing views remain regarding the appropriate wire gauge and safety practices.

Contextual Notes

Some participants reference specific wire gauge standards and practices in industrial settings, while others focus on the practical aspects of the project at hand. There is uncertainty regarding the voltage rating of the doorbell wire and its suitability for high voltage applications.

Who May Find This Useful

This discussion may be useful for individuals involved in DIY electrical projects, particularly those working with high voltage wiring and solid-state relays, as well as those interested in safety standards and wiring practices.

iambo
Messages
3
Reaction score
0
I'm new to projects requiring high voltage, but I need to wire 110v to an SSR controlling a device that pulls 2 amps and all I can find in my shop is some 18/2 doorbell wire. Is this safe to use?
 
Engineering news on Phys.org
18 gauge wire is safe to use at low currents. It would be recommended to fuse it though. BUT, doorbell wire is not a safe option at 120 volts. Most likely it is not intended for use above 48 volts.
 
Thanks for the response Averagesupernova! I looked it up before I asked the question but the wire seemed too flimsy to me. I used the chart at http://www.powerstream.com/Wire_Size.htm which rated 18 gage at 2.3 amps. If I'm using insulated solid copper core wire, how do I determine the proper gage?
 
When wiring in factories, we don't use anything smaller than 14 gauge for 120 volts and when wiring for 480 volt we don't use anything smaller than 12 gauge. 120 volt wiring is typically rated for up to 600 volts I believe.

Maximum fuse/breaker size for 14 gauge is 15 amps.

Maximum fuse/breaker size for 12 gauge is 20 amps.

Using too big of a wire never hurts, especially for a short run and small application like yours. The factories use the bigger wires for the same reason you mentioned...the smaller wires are too flimsy.

Order some real wire online or go to your local hardware store. A 3 or 4 amp fuse will likely work for your application, or whatever the specs say on your controller. 15 amp breaker will protect your 14 gauge wire...the 3 or 4 amp fuse will protect your controller.
 
Last edited:
psparky said:
Using too big of a wire never hurts, especially for a short run and small application like yours.


That must have been what the previous idiot homeowner thought when he made an attempt at wiring in my garage. What is the sense of running #10 wires to ceiling lights? The larger the wires, the more difficult they are to handle, less room in boxes, etc. It amuses me when I see people doing a wiring project and they are going to 'do a really good job' and while they have good intentions they end up with crappy work.
-
Psparky, I realize you were not referring to the same thing I am and agree that when it is sensible it is better to be a size larger. It is likely that in this case the OP has enough room to use #16.
 
-
Psparky, I realize you were not referring to the same thing I am and agree that when it is sensible it is better to be a size larger. It is likely that in this case the OP has enough room to use #16.

Understood. Just saying these are the min sizes in certain factories for 120 volt wiring.
Having #10 wiring for lighting would piss me off too in a residential home.

I sometimes have to run #10 wire in factory lighting and sometimes even #8 when the lights are 500 feet away from the panels to avoid voltage drop. In rare cases I've had to use #4 wiring for lighting to avoid voltage drop...but this was for outside parking lights that were over a thousand feet from the panel!
 
iambo said:
I'm new to projects requiring high voltage, but I need to wire 110v to an SSR controlling a device that pulls 2 amps and all I can find in my shop is some 18/2 doorbell wire. Is this safe to use?

You must install the wiring according to your local building codes, and you must have it insptected by your city's building inspectors. In general, all electrical additions need to comply with local building codes, and be signed off by the inspectors.
 
psparky said:
Understood. Just saying these are the min sizes in certain factories for 120 volt wiring.
Having #10 wiring for lighting would piss me off too in a residential home.

I sometimes have to run #10 wire in factory lighting and sometimes even #8 when the lights are 500 feet away from the panels to avoid voltage drop. In rare cases I've had to use #4 wiring for lighting to avoid voltage drop...but this was for outside parking lights that were over a thousand feet from the panel!

Hmmmm. Think of all the cool things you could fit in a garage large enough to justify #10 or larger wire feeding a lighting sub-panel. :)
-
Iambo, what does your project involve? Is this SSR going into a box that plugs into the wall? Being replaced in existing equipment? I'd like to know more.
 
Hey guys, thanks for the assistance.

berkeman, I don't think I will need building inspectors to sign off on this project, but thanks for the advice.

Averagesupernova, my thoughts are to make a power cord that plugs into the wall, which routes to a PID and has one wire tied to the controlled device and one to the HV side of the SSR. The PID out will connect to the SSR for the signal and the controlled device connects to the HV side of the SSR.
 
  • #10
iambo said:
Hey guys, thanks for the assistance.

berkeman, I don't think I will need building inspectors to sign off on this project, but thanks for the advice.

Averagesupernova, my thoughts are to make a power cord that plugs into the wall, which routes to a PID and has one wire tied to the controlled device and one to the HV side of the SSR. The PID out will connect to the SSR for the signal and the controlled device connects to the HV side of the SSR.

Cool. Run at least #16 to the outlet and at least #16 in your cord. Woo hoo!
 
  • #11
As Average Supernova alluded to, you should check the jacket and make sure that the insulation can withstand 120V AC (that's 170V pk). You'll probably need a magnifying glass since the writing tends to be a little hard to read (but it should say on the cable jacket).
 

Similar threads

Replies
8
Views
2K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 7 ·
Replies
7
Views
953
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 28 ·
Replies
28
Views
17K
  • · Replies 4 ·
Replies
4
Views
4K
Replies
38
Views
7K
Replies
3
Views
849
  • · Replies 10 ·
Replies
10
Views
2K