Load Angle of Synchronous Motor at No Load

  • Thread starter Thread starter rob1985
  • Start date Start date
  • Tags Tags
    Angle Load
Join the discussion
Registration is free. Ask a follow-up in this thread, or start your own.
4 replies · 2K views
rob1985
Messages
24
Reaction score
0
hi all,

Just a quick question, what would the load angle be of a synchronous motor when running at no load. would it be 0 degrees or 45 degrees
 
Engineering news on Phys.org
to be honest I am really not sure, I suspect it is zero as there is no load so the magnetic field of the rotor is the same as the stator. am I on the right tracks
 
I agree w/ you, although I'm not sure I'd call it a "load angle" since there's no load :smile:
 
rob1985 said:
to be honest I am really not sure, I suspect it is zero as there is no load so the magnetic field of the rotor is the same as the stator. am I on the right tracks
Yes. Active power is proportional to the sine of the load angle. No load, no active power, hence zero load angle.
rob1985 said:
so the magnetic field of the rotor is the same as the stator
No. You can say rotor magnetic field and stator magnetic field are aligned, or in other words, rotor is aligned with the resultant magnetic field.
 