NEC 408.3.E: 3-Phase Busbar Arrangement

  • Thread starter Thread starter MitYeltu
  • Start date Start date
Click For Summary
SUMMARY

NEC 408.3.E specifies that the phase arrangement on 3-phase buses must be A, B, C from front to back, top to bottom, or left to right, as viewed from the front of the switchboard or panelboard. In 3-phase, 4-wire delta-connected systems, phase B is designated as the phase with the higher voltage to ground. This configuration can lead to confusion, as it contradicts the expectation of balanced voltages across phases. The discussion clarifies that in a High Leg Delta configuration, it is impossible for all three legs to maintain the same voltage relative to ground.

PREREQUISITES
  • Understanding of NEC (National Electrical Code) standards
  • Knowledge of 3-phase electrical systems
  • Familiarity with delta-connected systems
  • Basic electrical terminology, including phases and legs
NEXT STEPS
  • Research the implications of High Leg Delta configurations in electrical installations
  • Study NEC 408.3.E in detail for compliance and application
  • Explore the differences between phase and leg terminology in electrical engineering
  • Investigate methods for balancing voltages in 3-phase systems
USEFUL FOR

Electrical engineers, electricians, and compliance officers involved in 3-phase system design and installation, as well as those ensuring adherence to NEC standards.

MitYeltu
Messages
8
Reaction score
0
NEC 408.3.E reads as follows

The phase arrangement on
3-phase buses shall be A, B, C from front to back, top to
bottom, or left to right, as viewed from the front of the
switchboard or panelboard. The B phase shall be that phase
having the higher voltage to ground on 3-phase, 4-wire,
delta-connected systems. Other busbar arrangements shall
be permitted for additions to existing installations and shall
be marked.

Have I missed the boat on this? A 3-phase system with a higer voltage on phase B than on phases A and C? I don't understand this. I thought a 3-phase system was, barring unbalanced impedances, balanced. What did I miss here?
 
Engineering news on Phys.org
MitYeltu said:
Have I missed the boat on this? A 3-phase system with a higer voltage on phase B than on phases A and C? I don't understand this. I thought a 3-phase system was, barring unbalanced impedances, balanced. What did I miss here?
Nothing. You are right. I have no idea why they said B is higher.
 
With High leg Delta configuration, ground is connected to the center tap of one of the transformers. It is then impossible to have all three legs at the same voltage in reference to ground. Which one you want to call A, B, or C is whatever someone decides.
-
When referring to buses, the terminology should be legs, not phases. A phase is a pair of conductors. Ideally all three phases will have the same voltage.
 
  • Like
Likes   Reactions: Asymptotic

Similar threads

  • · Replies 26 ·
Replies
26
Views
3K
  • · Replies 17 ·
Replies
17
Views
6K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
10
Views
15K
Replies
23
Views
6K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 8 ·
Replies
8
Views
2K
Replies
11
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 11 ·
Replies
11
Views
2K