Calculating Symmetric Components in a Three Phase 4 Wire System

Click For Summary

Discussion Overview

The discussion revolves around calculating the symmetric components of currents in a three-phase, four-wire system when one phase (Phase C) is disconnected. Participants explore the implications of this disconnection on the currents in the remaining phases and the corresponding symmetrical components.

Discussion Character

  • Technical explanation
  • Homework-related
  • Debate/contested

Main Points Raised

  • One participant proposes that the phase voltage is 230V and calculates the phase current based on this voltage and the resistive load.
  • Another participant questions the interpretation of phase voltage versus line voltage, suggesting a potential misunderstanding in the calculations.
  • Some participants discuss the effect of the blown fuse on the currents in the remaining phases, with varying interpretations of how to calculate the new currents and the role of the neutral.
  • There is a suggestion to use symmetrical components to analyze the new voltage phasor after Phase C is disconnected.
  • One participant mentions that the zero sequence components should not exist if there is no current through the neutral, leading to further discussion on the nature of symmetrical components in this scenario.
  • Multiple participants present different calculations for the symmetrical components, leading to discrepancies in results and interpretations of the phase angles.
  • There is an acknowledgment of confusion regarding the conventions used for phase angles and the importance of consistency in calculations.

Areas of Agreement / Disagreement

Participants express differing views on the calculations and interpretations of the phase currents and symmetrical components. There is no consensus on the correct approach, and various models and calculations are presented without resolution.

Contextual Notes

Some participants note limitations in their understanding due to a lack of practice and clarity in their course materials. There are also unresolved questions about the implications of the neutral connection on the calculations of symmetrical components.

Who May Find This Useful

This discussion may be useful for electrical engineering students or professionals interested in three-phase systems, symmetrical components, and the effects of load imbalances in electrical circuits.

CasterSkux
Messages
16
Reaction score
0
Hello fellow engineers!
I am a student doing a simple course in Electrical Engineering.

I've got an enquiry regarding this question

"
1. In a three phase 4 wire system with phase to neutral voltage of 230V, a balanced set of resistive loads of 8 ohms are connected between each phase and neutral.

If the fuse cartridge of phase “C” blows, what will be the currents in the corresponding phases and the symmetrical components of the load currents?
""

We use a program to calculate the symmetric components. I believe I need to construct the resultant phasor of this system and derive the symmetric components

This is my approach:

1) Assume this is a star connected load, therefore the phase voltage is Vp = Vl / sqrt(3) = 230/sqrt(3) = 132.7906 V

2) Calculate the balanced current that flows through each resistor I = V/R, I = 132.7906V/8 = 16.5988.

3) If Phase C is eliminated from the fuse, I think that the line/phase voltages stay the same (as there is a neutral) and hence the current is the same.

4) Therefore Phase A is 16.5988 amps and so is Phase B. Phase B is offsetted by 120 degrees taking A as the relative point.

5) Phase C is 0 and it's on the 240 degree mark on the phasor diagram.I was wondering if this is all right in approach?
 
Physics news on Phys.org
CasterSkux said:
This is my approach:

1) Assume this is a star connected load, therefore the phase voltage is Vp = Vl / sqrt(3) = 230/sqrt(3) = 132.7906 V
Didn't you say phase to neutral voltage was 230 V?
 
  • Like
Likes   Reactions: CasterSkux
Yes, oh have I overlooked something?
 
You should show by using symmetrical components what is new voltage phasor between phase B and star neutral after phase C is gone. Looks like a typical homework problem .
 
  • Like
Likes   Reactions: CasterSkux
zoki85 said:
Didn't you say phase to neutral voltage was 230 V?
Ah I ,maybe somehow I've interpreted "phase" as the "line", so the current is simply 230/8 = 28.75 amps.

Indeed It's a typical homework problem, the problem is my course is an online one: they didn't go through the basics as through as I would've liked and we hardly do math problems, so I'm not as well practiced unfortunately.

Zoki85, do you mean the new Phase A?
 
I was under the impression I work backwards to find the symmetrical components, not the other way around?
 
CasterSkux said:
Ah I ,maybe somehow I've interpreted "phase" as the "line", so the current is simply 230/8 = 28.75 amps.

Indeed It's a typical homework problem, the problem is my course is an online one: they didn't go through the basics as through as I would've liked and we hardly do math problems, so I'm not as well practiced unfortunately.
230 V is a common phase voltage (phase to neutral) in LV networks in Europe, so I guess it isn't mistake. This is simple situation and can be quickly solved even without method of symmetrical components. Phase to phase voltage is 230×√3 ≈ 400 V. Since phase C is open, current flowing through phases A and B is the same current that flows through series resistance 8+8=16 Ω. Current has magnitude 400/16=25 A. Note that in a phase diagram currents in phase A and phase B have same magnitude but are in phase oposition (angle difference between phasors is 1800 ).

Cheers
 
Last edited:
  • Like
Likes   Reactions: CasterSkux
Hello Zoki85,

Thanks for the reply. I was wondering if we should've considered current flowing to the neutral? would the phase C being broken, cause the load to be unbalanced and because it's (I assume a star connection): would cause current to flow into the neutral?

Cheers,
 
Indeed, I forgot you were referring to the case with connection between neutral points of two stars. In that case you were right! Current through the phase A: IA= VA/R=230/8=28.75 A, and current through the phase B: IB=VB/R= 28.75 ∠1200 A.
By Kirchoff's law, current through the neutral is I0=IA + IB. That would give I0= 28.75 ∠60° A (if I didn't make mistake without pencil&paper). For excersise, find from that, for both cases, direct, inverse, and zero sequence components of currents.
 
  • Like
Likes   Reactions: CasterSkux
  • #10
I started my calculation when nobody was on the web. Now some of the correspondents already answered [partially in my opinion].

230 V it is the voltage phase-to-neutral [your declaration].So phase-to-phase will be sqrt(3)*230=400 V [as usual].

The current in phase A [let's take it as origin of the angles] will be IA= 230/8=28.75<0;

IB=28.75<-120=28.75<240 and IC=0.Neutral current will be IN = - (IA+IB+IC) = -28.7*{[cos(0)+cos(240)]+j*sin(240)}

cos(0)=1; cos(240)=cos(pi()/180*240)=-0.5; sin(240)=-0.866

IN=-28.75*(0.5-0.866j)=-14.38+24.9j
 
  • Like
Likes   Reactions: CasterSkux
  • #11
Hello Zoki and Babadag!, Thanks for the help! This was vaguely what I thought I was supposed to do.

I got Zoki's answer of 28.75 ∠60° by converting everything to the complex number and adding, but that's only because I used the convention that all the phase angles are referenced from Phase A and rotate counterclockwise. Babadag you're also right and I know that convention of everything anticlockwise of A is negative and clockwise is positive.

You're both legends!
 
  • #12
The symmetric components are (if I take 28.75 arg(60)) for this question are:

Zero =19.2 arg(60)
Positive = 19.2 arg(-60)
Negative = 9.58 arg(0)

The symmetric components are (if I take 28.75 arg(240)) for this question are:

Zero = 0
positive = 0
Negative = 28.8

Interesting differences.

Cheers,
 
  • #13
Just been told that there shouldn't be any zero sequences through the neutral, don't know why?
 
  • #14
CasterSkux said:
The symmetric components are (if I take 28.75 arg(60)) for this question are:

Zero =19.2 arg(60)
Positive = 19.2 arg(-60)
Negative = 9.58 arg(0)

The symmetric components are (if I take 28.75 arg(240)) for this question are:

Zero = 0
positive = 0
Negative = 28.8

Interesting differences.

Cheers,
?
Symmetrical components here you get from known phase currents IA,IB,IC .
Zero sequence phasor definitelly isn't 0 due to fact sum of the currents in phases A and B isn't 0.
I see that in my calcs I took oposite way of system rotation, and not the convential, counterclockwise one (like Baba did) .
Better stick to the convention to avoid confusion with arguments
 
  • Like
Likes   Reactions: CasterSkux
  • #15
Sorry I made a mistake in the inputting to calculate the symmetrical values.

Start again: the resultant phasor values are (using Badabung's convention):

Ia = 28.75 arg(0)
Ib = 28.75 arg(240)
Ic from Badabung =-14.38+24.9j = 28.75 arg(-60) = 28.75 arg(300) = this is the resultant neutral phasorThe calculator for Symmetric components gave me

I0 = 19.2 arg(-60)
I1 = 9.60 arg(0)
I2 =19.2 arg(60)
 
  • #16
bjREj2l.png
 
  • #17
CasterSkux said:
Start again: the resultant phasor values are (using Badabung's convention):

Ia = 28.75 arg(0)
Ib = 28.75 arg(240)
Ic from Badabung =-14.38+24.9j = 28.75 arg(-60) = 28.75 arg(300) = this is the resultant neutral phasor

Oh dear, Ic = 0. Phase C is dead broken (remember?) and no current can be flowing through it. You should really learn basics of this stuff...
 
  • Like
Likes   Reactions: CasterSkux
  • #18
Sorry I've attached Ic as the resultant vector of A + B, it's a terminology error. I'd like to learn more but we don't get enough practice excersizes unfortunately:(
 
  • #19
I really do appreciate your help though Zoki!
 
  • #20
Hello again, I was wondering if anyone can confirm my answer?
 
  • #21
IA= 28.75 A
IB= 28.75 ∠240° A
IC= 0 A
Use formulae:)
 
  • Like
Likes   Reactions: CasterSkux
  • #22
Ah the take home lesson I guess is to "always allocate A B and C to their appropriate phases and you MUST do so" I made Ic = In subconsciously because I thought it would be needed in a Phasor diagram, but these Phasor Diagrams are strictly for Phase A, B and C - something that I wasn't so brought on about.

Thank you heaps Zoki85, I've learn't more from you about these diagrams than reading them bit by bit in a year!
 
  • #23
Hello all:)
Have to revive this thread just to clarify a new question:

Now we must answer the same question, but with no Neutral, this was answered without intention in the beginning of the post

230 V is a common phase voltage (phase to neutral) in LV networks in Europe, so I guess it isn't mistake. This is simple situation and can be quickly solved even without method of symmetrical components. Phase to phase voltage is 230×√3 ≈ 400 V. Since phase C is open, current flowing through phases A and B is the same current that flows through series resistance 8+8=16 Ω. Current has magnitude 400/16=25 A. Note that in a phase diagram currents in phase A and phase B have same magnitude but are in phase oposition (angle difference between phasors is 1800 ).

I can do the maths involved, but I don't know how the phasors are 180 degrees apart and I don't know how to mathematically derive it. I'm under the impression that Phase A and B are still 120 degrees separated.

I was wondering how A and B can be 180?
 
  • #24
With no neutral, and phase C open, the line currents add at the "centre junction" to equal zero. ( Σ current in = Σ current out )

So ##\mathbf{I_A = -I_B}## (equal and opposite means 180° apart)

The voltage across one load is ##\mathbf{V_A - V_B}## and across the other load it's ##\mathbf{V_B - V_A}##

Construct the phasor diagrams and you'll see these phase relationships.
 

Similar threads

  • · Replies 4 ·
Replies
4
Views
3K
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 2 ·
Replies
2
Views
6K
Replies
7
Views
2K
Replies
11
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
Replies
2
Views
4K