Overhead transmission line protection failure

AI Thread Summary
A 13.8 kV overhead transmission line in Saudi Arabia fell to the ground while still live, leading to the death of over 30 camels. The Earth Fault Relays (EFR) and Over Current Relays (OCR) failed to operate, likely due to high soil resistance in the dry sand, preventing a good ground fault from being detected. If both wires fell together, the current may have appeared balanced, further complicating detection. The incident highlights the need for improved relay settings and protection strategies in desert environments. Suggested solutions include adjusting relay settings to account for high ground impedance and considering alternative protective measures for arid conditions.
Tee
Messages
8
Reaction score
0
Hello everyone ,

I am still new to the protection field so i would appreciate if you can help me with analysis of the following,

A 13.8 Kv OHTL was cut and fell on ground , the cable was still live although being protected by Earth fault relays and Over current relays(Instantaneous and Time delay) , but for some reason they failed to operate.

This incident caused death of over 30 camels in Saudi Arabia.

This line was located in the desert and the marks on the sand showed that it stayed on ground for longer than one day.

What do you think could possibly cause EFR and OCR not to operate?

All opinions are much appreciated.

Thank you in advance
 
Engineering news on Phys.org
The Earth ground fault will only trigger if there is a good ground fault, so if the wires landed on dry sand or dirt, the GFCI may not trip. Also, if both wires fell together, then the current might have looked differential, and again the GFCI would not trip.
 
I agree with berkeman. High resistance of the soil(sand) could cause both relays to not sense the downed lines. The gound potential rise near the lines would cause the animals to be killed. With there long steps, there would be a large potential difference between the legs.
 
Thanks for the replies , that was really helpful.
 
Also:

Non directional ground relays may operate is the setting is below the current unbalance setting. Normally they set above to prevent inadvertent tripping during high demand period, typical in feeder circuits fro their neutral protection.

Tansmission system are trated as a balance circuit which can be set much lower in percentage terms to feeder circuit rating and often can be set to operate for broken conductor or single line to groundf ault with very low fault current on dry terrain or high ground impedance ... abnormal case for setting describe above.
 
good analysis
but
what are the suggested solutions for this problem in desert ?
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...

Similar threads

Replies
2
Views
2K
Replies
3
Views
9K
Replies
3
Views
16K
Replies
4
Views
8K
Replies
33
Views
6K
Replies
49
Views
7K
Back
Top