A 13.8 kV overhead transmission line in Saudi Arabia fell to the ground while still live, leading to the death of over 30 camels. The Earth Fault Relays (EFR) and Over Current Relays (OCR) failed to operate, likely due to high soil resistance in the dry sand, preventing a good ground fault from being detected. If both wires fell together, the current may have appeared balanced, further complicating detection. The incident highlights the need for improved relay settings and protection strategies in desert environments. Suggested solutions include adjusting relay settings to account for high ground impedance and considering alternative protective measures for arid conditions.
Tee
Messages
8
Reaction score
0
Hello everyone ,

I am still new to the protection field so i would appreciate if you can help me with analysis of the following,

A 13.8 Kv OHTL was cut and fell on ground , the cable was still live although being protected by Earth fault relays and Over current relays(Instantaneous and Time delay) , but for some reason they failed to operate.

This incident caused death of over 30 camels in Saudi Arabia.

This line was located in the desert and the marks on the sand showed that it stayed on ground for longer than one day.

What do you think could possibly cause EFR and OCR not to operate?

All opinions are much appreciated.

Thank you in advance
 
Engineering news on Phys.org
The Earth ground fault will only trigger if there is a good ground fault, so if the wires landed on dry sand or dirt, the GFCI may not trip. Also, if both wires fell together, then the current might have looked differential, and again the GFCI would not trip.
 
I agree with berkeman. High resistance of the soil(sand) could cause both relays to not sense the downed lines. The gound potential rise near the lines would cause the animals to be killed. With there long steps, there would be a large potential difference between the legs.
 
Thanks for the replies , that was really helpful.
 
Also:

Non directional ground relays may operate is the setting is below the current unbalance setting. Normally they set above to prevent inadvertent tripping during high demand period, typical in feeder circuits fro their neutral protection.

Tansmission system are trated as a balance circuit which can be set much lower in percentage terms to feeder circuit rating and often can be set to operate for broken conductor or single line to groundf ault with very low fault current on dry terrain or high ground impedance ... abnormal case for setting describe above.
 
good analysis
but
what are the suggested solutions for this problem in desert ?
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...

Similar threads

Replies
2
Views
2K
Replies
3
Views
9K
Replies
3
Views
16K
Replies
4
Views
8K
Replies
33
Views
6K
Replies
49
Views
7K
Back
Top