Phase to Ground Fault: 20MW, 13.8KV Analysis
The discussion revolves around the analysis of a phase to ground fault in a 20MW, 13.8KV wye generator that experienced damage due to a failure to connect the neutral grounding resistor. Participants are exploring the implications of this fault, including the current and voltage behavior during such an event, and the potential hazards involved.
  • Krishna describes the incident involving the generator and seeks to understand the current and voltage flow through the neutral during a phase to ground fault.
  • Some participants suggest that the current during ground faults can reach full supply levels, with voltage spikes potentially reaching several thousand volts.
  • There is a discussion about whether the generator's neutral was connected directly to ground or if there was no solid connection, which could affect fault current behavior.
  • One participant mentions that the fault current would likely exceed the phase current and could be intermittent, leading to voltage spikes.
  • Another participant provides a method to estimate fault current based on the generator's short circuit ratio and field current settings, noting that transient currents could be significantly higher than steady-state values.
  • Krishna clarifies that the neutral was not connected to the grounding resistor, which prevented the activation of the 51N protection relay during the fault.
  • There are references to external resources for calculating fault currents, including typical transient and subtransient reactances.
  • Participants express concern over the hazardous nature of the situation and emphasize the importance of proper installation and understanding of the system.
Participants express differing views on the specifics of the fault conditions and the implications of the neutral grounding setup. There is no consensus on the exact current flow or voltage behavior during the fault, and the discussion remains unresolved regarding the precise calculations and outcomes.
Participants note the complexity of calculating fault currents, highlighting the need for specific machine constants and the potential variability based on system configurations. The discussion includes references to transient and subtransient behaviors, which are not fully resolved.
This discussion may be of interest to electrical engineers, technicians involved in generator maintenance, and professionals working with power systems and fault analysis.
balevadu
Hi All,
Good morning. we had a 20MW, 13.8 KV wye generator and it has a neutral grounding resistor. Some how we failed to connect the neutral grounding resistor and during a rain storm we burnt the generator. Even though the neutral is not connected to the neutral grounding resistor it was in direct contact with the enclosure which is metal. I just want to know how much current and voltage flows through the neutral during phase to ground fault. Please some one help me.
Thanks in advance,
Krishna
The current can be upwards to the full supply current on ground faults, voltages can spike to several thousand in a short spike. Sort of like inductive kicks utilized by car starters.
Thank you very much for your response.
balevadu said:
Hi All,
Thanks in advance,
Krishna
20 megawatts? I just googled that, and find they run in the 5 to 10 million dollar range.
I'm not sure you will get a specific answer at this forum.
When you purchase your next generator, you should have the manufacturer make sure everything is wired up correctly. Round trip airline tickets for a qualified electrician to fly anywhere in the world are probably a lot cheaper than $10,000,000.00
20MW/13.8 KV=1450 amps
Short circuiting your generator --> i >>>>>>>> 1450 amps
which translates to "the current will have been much much much much greater than 1450 amps."
ps. Current flows, voltage doesn't.
Are you saying the Gen Neutral was connected directly to ground - or there was no (solid) connection between the Gen Neutral and Ground?
I am curious because if there was no connection - then you would need 2 fault locations to get a ground fault - although the insulation level between the neutral conductor may not have been rated for full line voltage. I have seen many faults get repaired and turned on - only to immediately fail again ( now with people standing around watching) because the original situation was not fully understood.
The amount of fault current available would have been much more than the phase current - and a ground fault can be intermittent / sparking - that can cause the V spikes Mordred mentions .
Nevertheless - the situation sounds to have been extremely hazardous - and I would say very lucky to have not caused a fatality. Please have a qualified person review the repair and final installation. It is my experience that these situations do not come about via a single error or lapse of judgment - but a series of mistakes in thought, judgment and physical mistakes. And arrogance leads to them all.
So do i understand you had a phase to ground fault while the neutral was grounded by accident?
Were you connected to grid at the time?
Was voltage regulator in manual or automatic?
If in manual, the current that flows is about (rated amps X machine's short circuit ratio), short circuit ratio ratio being probably slightly less than 1.
Short circuit ratio should be in your generator manual and given as either S C R (abbreviation for short circuit ratio), or synchronous impedance which is reciprocal of short circuit ratio.
If in auto, multiply the above result by ratio of maximum field amps (which is set by a voltage regulator limit) to normal field amps for generator rated output.
That's the quick and dirty way to get a ballpark answer.
Your generator people will do a better calc using transient and subtransient impedances to calculate the short term transient currents and that'll will be higher than above method. Method above will give steady state current. Transient will be maybe 3X-10X higher, but too brief to do much welding.
But above gets you in ballpark for the machine's contribution. If you were connected to grid some more came in backward through transformer.
I hope your metering was working okay - that kind of trouble can lead to overflux...
http://www.ccj-online.com/archives/special-issue-outage-handbook/2011-outage-handbook-generators/
good luck -
old jim
Thank you for the replies.
The neutral of the generator was supposed to be connected through the neutral grounding resistor. Our electricians forgot to make this connection. The unit was running perfectly and is on grid. as the neutral is not connected to the neutral grounding resistor the 51N never got activated. what ever damage that can happen has already happened. the neutral cable was touching the frame of the grounding resistor. I just want to know how to calculate the amount of current that flows through the neutral in case of a phase to ground fault.
Thanks
So did or did not a phase to ground fault occur , in addition to your accidental neutral to ground connection?
See
http://www.geindustrial.com/publibrary/checkout/GET-3550F?TNR=White Papers|GET-3550F|generic
page 5 gives approach, page 15 starts detailed procedure for that calculation.
You'll have to find some of your machine constants.
This link has some tables of "typical" transient and subtransient reactances.
http://www.magergy.com/documents/Ebooks/Electrical%20Engineering%20for%20Oil%20and%20Gas/96316_03.pdf
see figs 3.5 thru 3.12
lessee 20 mw at 13.8kv = 836 amps? If that's at .8pf, it's a 1045 amp machine? Let's call it a kiloamp.
Subtransient reactance gives the initial spike, see fig 3.9
If we guess at 12% that'd be 1/.12 = 8.33 X rated , or 8.33 kiloamps
Initial spike decays and transient reactance takes over in a very few cycles.
See subtransient time constant in fig 3.10. Maybe two cycles, 33 msec for initial spike?
Transient reactance is higher than subtransient, see fig 3.7 . Maybe 25% ?
So after subtransient , current would become 1/.25 X rated, maybe 4 kiloamps.
That'd go on maybe a half second - see transient time constant in fig 3.8.
Transient reactance dies out leaving synchronous reactance in charge, fig 3.5. Maybe 150%?
So steady state current would settle, after subtransient and transient time constants, at 1/1.5 X rated = 666 amps.
...EXCEPT THAT the voltage regulator will be raising excitation trying to restore voltage,
and the transformer may be backfeeding the fault. So current will be higher - so the analyst will have to figure out how your particular voltage regulator responds.
AND generator protection should have tripped it by now.
Those calculations are tedious , and honestly i did not do them in my work. I only knew and worked with people who did.
This "back of the envelope" will give you ballpark answers
but
for anything approaching accurate , you need details about the machine and transformer impedances and somebody who is well versed in that type calculation.
~8300 amps initially , plus some from the transformer - That's the best i can do for you.
How did the damage look around that accidental neutral ground?
You said "burnt the generator"
- we melted the end out of one- I hope yours was less spectacular.
If all you had was alittle sparking there from neutral displacement, you might be okay.
old jim
Thank you very much for your response jim.
neutral is not grounded accidentally. the neutral was never connected to the grounding resistor, from which the 51N gets activated when ever there is flow of current through the neutral. as the neutral is not connected the 51N relay never got activated. what i was thinking was the neutral grounding resistor will dissipate the energy in case of a ground fault. if there is no neutral grounding resistor then there might be a huge explosion if the neutral is touching the ground during a ground fault in the generator. Correct me if i am wrong.
Thanks
Krishna
Ahhh, so we did not have a flash-boom after all. I feel better, thanks.
Yes, that is its purpose. It limits the current that flows through a phase-ground fault to perhaps ten or twenty amps so there's not much arc-welding inside the machine.
Now - ten amps at 13.8kv is 138kw, so the resistor is physically quite large.
The voltage across an arc is probably only forty volts or so, so at twenty amps you're putting less than a kilowatt into damaging the machine.
You are exactly right. During a fault...nothing limits the current except the machine constants as i described above.
Vaporized copper expands by the same gas laws as dynamite vapor.
You've heard the "BOOM" from electrical explosions?
Now - let's think about what situation i think you are saying you had, the neutral wire grounded instead of tied to resistor.
That's just bypassing the neutral resistor, eh?
So this question becomes '...what if neutral resistor is bypassed, ie your neutral wire touching touching ground in absence of a phase-ground fault?
What current flows then ?'
Well, let us think about it - aloud.
First thought step will be Kirchoff's Current Law:
The current that flows into the neutral from ground is the sum of the currents that flows out of the individual phases into ground.
What path do those currents take?
Those currents flow mostly through the distributed capacitance of your generator windings, transformer windings and interconnecting wiring. That's the only connection...
So the dominant impedance is that capacitance.
Next thought step - Tesla's gift to EE's- remember the three phases are 120 degrees out, so those capacitive currents add to zero.
So neutral current will be quite small so long as there's not much imbalance. I'd wager it's less than an amp. Well, maybe two... carry on...
Next thought step: Fourier's gift to EE's - remember your generator does not make a perfect sine wave, it has harmonic content like any other real genertor. Probably two or three percent in a machine that small.
And much if not all of that will be third harmonic.
Aha ! Third harmonic - that's 180 hz, only 5.555 milliseconds for a whole cycle , 360 degrees at 180 hz.
Aha^2 ! 5.555 milliseconds is also 120 degrees (1/3 cycle)at 60 hz.
What that means is this - the third harmonic of each generator phase is in phase with the third harmonic of the other two phases.
Aha^3 ! So the third harmonic currents flowing into the neutral do not cancel out as did the fundamental, they directly add.
SO ------- in normal operation, the current returning in the neutral is largely third harmonic.
I have measured this with a spectrum analyzer and find neutral current to be maybe thirty percent third harmonic, maybe the majority like 85%. It doesn't look a lot like the 60 hz sinewave produced by the machine.
Using the amplitudes and ratios of fundamental to third harmonic in both phase voltage and neutral current, you can get a pretty good guess at what is the distributed capacitance of your generator-transformer system.
>>> Don't Give Up On Me Yet - I haven't forgot your question...<<<
I'm going to guess that in normal operation you'll find an amp or two of neutral current , at least 50% of it third harmonic. Harmonic content goes up with excitation.
Now - what happens if you bypass the neutral resistor with no phase fault present?
Basically, nothing. The dominant impedance in the circuit is still the distributed capacitance. Neutral current will change very little.
Incidentally that's how you size a grounding resistor, make it a few times smaller than the impedance of your distributed capacitance.
This is all described very clearly in IEEE's "Green Book", standard 142 i think it is.
Every power plant guy needs to have his own personal copy. Ask your company to get you one.
Thanks
Krishna
Well, thanks for listening. Helps an old guy feel useful.
I'm sorry the answer turned out so long -
it's just that i was trained by a stern mentor to always "answer the question that was asked"
and i hope this seemingly endless post helped.
old jim
  • · Replies 38 ·