Pipe Pressure Increase: Investigating Unit Ventilator Valves in Reverse Loop

  • Thread starter Thread starter markymarkg123
  • Start date Start date
  • Tags Tags
    Pipe Pressure
Click For Summary

Discussion Overview

The discussion revolves around the observed increase in pipe pressure within a school's heating system when unit ventilator valves were turned off. Participants explore the implications of this phenomenon in the context of a reverse return loop with hot water, questioning the relationship between valve throttling and pressure dynamics as described by Bernoulli's principle.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant notes that shutting off all unit ventilator valves led to a significant increase in pipe pressure, which caused circulation pumps to back off.
  • Another participant suggests that at the pump end, the pump must work harder to maintain flow, and if all valves are shut, the pump may not be effectively moving water, potentially leading to issues.
  • There is a question about the meaning of "circulation pumps backing off," with a suggestion that it may relate to variable speed drives (VFDs) adjusting their speed based on pressure changes.
  • A participant emphasizes the need to clarify what type of pressure is being measured, distinguishing between velocity pressure, static pressure, total pressure, and differential pressure.
  • It is mentioned that Bernoulli's principle applies to static pressure measurements and steady flow, indicating that the observed pressure changes may not align with the principle's expectations if measurements are taken at different times.
  • One participant explains that when all valves are shut, the supply loop effectively bypasses the unit ventilators, which may contribute to the pressure increase.
  • Another participant discusses how pumps have performance curves that indicate that introducing a restriction leads to higher pressure and lower flow, drawing an analogy to blocking a garden hose outlet.

Areas of Agreement / Disagreement

Participants express varying interpretations of the pressure dynamics and the implications of valve throttling, with no consensus reached on the underlying reasons for the pressure increase or the relationship to Bernoulli's principle.

Contextual Notes

Participants highlight the complexity of the system and the need for a mathematical relation to better understand the pressure changes, indicating that assumptions about flow and pressure dynamics may not be fully resolved.

markymarkg123
Messages
3
Reaction score
0
Did an experiment in a school's heat system. Turned off the unit ventilator valves all at once. The pipe pressure raised significantly causing the circulation pumps to back off. Some notes, this is a reverse return loop, hot water flowing (not steam), unit ventilators are 2-pipe.

Question: why did pressure increase when uni-vents were throttled? I thought Bernoulli said that narrowing pipes would cause velocity to increase and pressure to decrease...shutting off all branches should narrow all flow to the supply line only, right?
 
Engineering news on Phys.org
Yeah, at the pipe sesction you are looking at, sure. Upstream at the pump end, the pump has to work harder to achieve the same amount of flow. In your case, if you shut all valves, there is no flow and the pump just spins the water in its casing around. Is that good for your pump? No bypass in your system?

causing the circulation pumps to back off
what does that actually mean.
 
256bits said:
what does that actually mean.
Probably that they are on variable speed drives and slowed down.
 
markymarkg123 said:
Question: why did pressure increase when uni-vents were throttled? I thought Bernoulli said that narrowing pipes would cause velocity to increase and pressure to decrease...shutting off all branches should narrow all flow to the supply line only, right?
What pressure, where? There's velocity pressure, static pressure, total pressure, differential pressure...

Bernoulli's principle is talking specifically about static pressure inside the venturi vs right next to it. So unless you are measuring the static pressure inside the valve itself, you won't see a drop. In your system, the control point is almost certainly the static pressure in the main, who's size you didn't change.

Bernoulli's principle is also talking about steady flow along a streamline: pressure difference between two parts of the same system at the same time. You measured one point on the system at different times.
 
Couple of answers. Water in the supply loop either goes through the uni-vent or continues to the end, where the return loop collects all uni-vent discharge and the supply loop remnants. Thus, the supply loop simply dumps into the return loop if the uni-vent valves all shut, which is the same as a bypass I guess. The circulation pumps are VFDs, and they spin faster when more pressure is needed and less when the pressure is higher than needed. Throttling all of the valves made the pressure increase, so the VFDs slowed down. I can't explain why, and am looking for a mathematical relation to help understand this.
 
Mentor, you are asking the right questions. This shows my ignorance in heating systems. The pressure differential is what tells the VFDs to slow down or speed up, and that is the pressure I am trying to understand. That pressure increased causing the VFDs to slow down. Do you know why?
 
markymarkg123 said:
That pressure increased causing the VFDs to slow down. Do you know why?
Pumps have performance curves. When you introduce a restriction against their flow, their performance follows the curve up and back, to a higher pressure and lower flow state. A similar thing happens when you put your thumb on the outlet of a garden hose. Slowing the flow allows the pressure to build.
 

Similar threads

  • · Replies 31 ·
2
Replies
31
Views
5K
  • · Replies 15 ·
Replies
15
Views
4K
  • · Replies 10 ·
Replies
10
Views
4K
Replies
0
Views
2K
Replies
1
Views
1K
  • · Replies 20 ·
Replies
20
Views
11K
Replies
6
Views
6K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 4 ·
Replies
4
Views
5K
  • · Replies 3 ·
Replies
3
Views
7K