A UPS has two ratings: apparent power (KVA) and real power (KW), with KW typically being lower due to power factor differences. The distinction arises because KW measures usable power, while KVA includes both real and reactive power. Power stations are rated in MW instead of MVA because they assume loads are predominantly resistive, reflecting the actual power available for work. KVA represents the total power capacity, including reactive components, but clients prioritize real power for practical applications. Understanding these differences is essential for effective power management and system design.
QwertyXP
Messages
66
Reaction score
0
UPS:
http://www.power-solutions.com/watts-va
From the above link, I have gathered that a UPS has 2 different ratings: for apparent power (KVA) and real power (KW). The KW rating is often less than KVA rating. Can anybody tell me why those ratings are different? Is it because the peak instantaneous power resulting from a power factor of 60% would be lower than the peak power when pf=unity?

Power Station:
Why are power stations rated in MW and not MVA? Do they assume that the load will be purely resistive, in which case the MW rating is actually a MVA rating?
 
Engineering news on Phys.org
You seem to already understand the essence of the problem:

kW is the power available; kVA is reactive power.
 
KVA are the units of apparent power, not reactive power. So the "power available" should be expressed in KVA..or shouldn't it?
http://www.justgenerators.co.uk/pages/FAQ.htm
it says 3-phase generators have KVA rating because their loads do not usually have unity pf. Why, then, do power stations not also have KVA rating?
 
Last edited by a moderator:
KVA or apparent power is the sum of 2 quantities: KW(real power) and KVAR (reactive power).

During the operation of your loads, take motor for example, the horse power that the motor can produce (and that you can feel) is the real power consumed by this motor, while this motor is also consuming another type of power which is reactive power but you don't have any return even it is consuming power.

So real power produce work, and is reflected on some action by the machine.

In power generation facilities, of course there is apparent power for the generation set, but your client (suppose you are the engineer designing the station) needs this amount of real power, because he needs work and he needs a power that he want to utilize, not just apparent power, so for this reason they mention this power generation is 300 MW or some thing else.
 
  • Like
Likes 1 person
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...