Actually, I am trying to visualize as much as possible the damages/degradations/effects induced in ex-core detectors in case of being water surrounded, and I believe in some way the flooding may pose serious threat to correct neutron detection ( keeping the other effects of flooding aside, and only concentrating on the effect on detector).
well actually our source range detectors, BF3 type, are a sealed unit with about eighteen feet of metal jacketed cable attached by weld to top of cylindrical measuring chamber.
They work fine underwater, in fact for a backup indication at refueling time we hang one or two with longer cables down into the reactor vessel , under perhaps thirty five feet of water..
It's affectionately called 'dunking chamber' or 'rubber ducky' after the bath toy.
Water causes trouble in source range when it gets into the connections between the metal sheathed detector cable and the ordinary plastic cables going up to control room. That connection is just below floor of refueling cavity so leaks on the hatch covers are a leading cause of that trouble.
But that's a good fifteen feet above detector location.
Moisture in the source range cable connector let's the high voltage sputter and arc, we call it "corona", and it gives a false high reading that masks true neutron count. An insidious failure, and you can't get to it during refueling for repair because the hatches are under thirty feet of water...
Water in the intermediate range detector cables interferes with the miniscule currents you are trying to measure. It degrades cable insulation and the current meanders away .
Water on power range detectors , meh, it's a miliamp or so of signal hence pretty tolerant of degraded cable .
The detectors themselves and their affixed cabled are sealed aluminum or stainless steel, so surrounding them with water would keep them cool.
It's the other stuff in your measurement system like wiring that's sensitive to water.
As with all electrical equipment - just keep it clean and dry
hope this helps.
why invent new troubles? It's the old ones that need attention.
Is this a research project?
Why not visit a facility and spend some time with the guys who fix the equipment?
You'll find they really resent spending effort on imaginary problems.
old jim