Question about generating split phase power

  • Thread starter Thread starter hapster57
  • Start date Start date
  • Tags Tags
    Transformer
Click For Summary
SUMMARY

The discussion centers on the complexities and dangers of sharing a neutral wire between two single-phase inverters connected to a home panel board in a split-phase transformer setup. It is established that while theoretically possible, sharing the neutral can lead to significant issues, such as the neutral wire carrying excessive current due to phase drift, which can create a fire hazard. Participants strongly advise against this practice and recommend consulting a licensed electrician for safe installation and compliance with local building codes.

PREREQUISITES
  • Understanding of split-phase transformer configurations
  • Knowledge of single-phase inverter operation
  • Familiarity with electrical load balancing and neutral current behavior
  • Awareness of local electrical codes and safety standards
NEXT STEPS
  • Research safe methods for connecting multiple inverters to a home electrical system
  • Learn about electrical load calculations for split-phase systems
  • Study the implications of phase drift in electrical systems
  • Explore local building codes regarding inverter installations
USEFUL FOR

Homeowners, electricians, and renewable energy enthusiasts looking to safely integrate multiple inverters into residential electrical systems while ensuring compliance with safety regulations.

hapster57
Messages
3
Reaction score
1
in a split phase transformer, how is the neutral wire shared. since the split phases of the hot wired are 180 apart, what happens in the neutral wire. my question stems from having two single phase inverters and wanting to hook them up to a home panel board with a common neutral the two inverters will be randomly out of phase with each other, but can they share the neutral wire?
 
Engineering news on Phys.org
In theory, yes, but there will be problems, and traps for the beginner.
A couple of which might be;

1. You will be unable to run equipment at double voltage from the two hot wires, since the unknown phase drift will make it a low frequency.

2. The neutral wire will at some times have only half the section required. You would have to halve the power drawn from each of the hot wires. That is because the current in the neutral from the two hot separate wire circuits do not cancel in phase like normal.

This is a dangerous game. I recommend you avoid it.
If you don't know what you are doing, call a local electrician.
 
  • Like
Likes berkeman
I didn't think it possible to use a common neutral for out of phase power sources,vbut I'm just not grasping in a standard split phase transformer what happens in the neutral wire and why that works
 
It works because
the current in hot1 that returns through the neutral is out of phase with
the current in hot2 that returns through the neutral, so the two opposite currents in the neutral cancel.
If both hot circuits have a maximum resistive load, then there is no neutral current.
 
Baluncore said:
It works because
the current in hot1 that returns through the neutral is out of phase with
the current in hot2 that returns through the neutral, so the two opposite currents in the neutral cancel.
If both hot circuits have a maximum resistive load, then there is no neutral current.
I see what you are saying, that worst case, if L1 had 10 amps and L2 had 20 amps, the neutral wire might possibly have to carry all 30 amps as opposed to a split phase transformer neutral only carrying the difference of 10 amps. Thanks.
 
  • Like
Likes Baluncore
For the transformer, the neutral is effectively just a center-tap of a single winding (the 'ends' of the winding are the 2 'phases.'

Assuming that the inverters are completely 'floating,' you could theoretically share the neutral. This 'shared' conductor would have to be sized to carry the full current (sum) of both inverters. Your house probably isn't wired this way - DON'T!
 
  • Like
Likes hapster57
hapster57 said:
my question stems from having two single phase inverters and wanting to hook them up to a home panel board with a common neutral the two inverters will be randomly out of phase with each other,
Baluncore said:
This is a dangerous game. I recommend you avoid it.
If you don't know what you are doing, call a local electrician.
Dullard said:
Your house probably isn't wired this way - DON'T!

This is indeed a dangerous question from an inexperienced person. @hapster57 -- please do not do this. It is dangerous, against your local building codes, and puts you and your family at risk for fire. If you want to generate split phase power from an inverter, there are other ways to do that and be within your local building codes. Please do contact a local electrician with your questions.

Thread is closed.
 

Similar threads

  • · Replies 25 ·
Replies
25
Views
5K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 32 ·
2
Replies
32
Views
4K
  • · Replies 19 ·
Replies
19
Views
4K
Replies
9
Views
2K
  • · Replies 16 ·
Replies
16
Views
5K
  • · Replies 41 ·
2
Replies
41
Views
18K
Replies
21
Views
5K
  • · Replies 5 ·
Replies
5
Views
3K