Question about inductive motor and load filter.

  • Thread starter Thread starter Starwatcher16
  • Start date Start date
  • Tags Tags
    Filter Load Motor
Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
1 reply · 3K views
Starwatcher16
Messages
53
Reaction score
0
I have a 3 phase 3 pole inductive motor with a VFD that is tripping the breker even before it ramps up. The breaker is set to allow its inrush current without tripping.

There is about 400 feet of wire between this motor and its busbar.

After a load filter was installed for this motor, there have been no problems with it.

If this load filter a power correcting device? Is the reason the motor was tripping that the apparent power on the return part of the sin wave exceeding the breakers trip limit?
 