Single phase transformer and net KVA output

Join the discussion
Registration is free. Ask a follow-up in this thread, or start your own.
1 reply · 3K views
anand raj
Messages
17
Reaction score
0

Homework Statement


a 4 kva, 230/115 volt, 400 HZ, single phase transformer originally designed for use in air crafts, is available in a laboratory for obtaining 115 volt supply from standard 230 volt,50 HZ mains if overloading of the device is not permitted then net kva output is...

Homework Equations


The Attempt at a Solution

[/B]
here frequency is varying voltage remaining the same
kva being proportional to frequency
x = kva output for 50 HZ
4/x = 400/50
x = 0.5 kva
i don't know whether it is right or wrong, but the answer is this.
 
Physics news on Phys.org
The wording of the question seems to imply (but stops short of stating unequivocally) that the transformer is to deliver 115V at 50Hz. I can't offer a technical opinion, but according to this reference http://www.edn.com/design/component...sformer-at-a-frequency-it-wasn-t-designed-for
For a power transformer designed for 115VRMS at 400 Hz but used at 60 Hz, the input voltage must not exceed 115×60/400 = 17.25 VRMS

Perhaps others can offer a critique of the suggested scheme.