Single phase transformer and net KVA output

  • #1
anand raj
17
0

Homework Statement


a 4 kva, 230/115 volt, 400 HZ, single phase transformer originally designed for use in air crafts, is available in a laboratory for obtaining 115 volt supply from standard 230 volt,50 HZ mains if overloading of the device is not permitted then net kva output is...

Homework Equations


The Attempt at a Solution

[/B]
here frequency is varying voltage remaining the same
kva being proportional to frequency
x = kva output for 50 HZ
4/x = 400/50
x = 0.5 kva
i don't know whether it is right or wrong, but the answer is this.
 
Physics news on Phys.org
  • #2
The wording of the question seems to imply (but stops short of stating unequivocally) that the transformer is to deliver 115V at 50Hz. I can't offer a technical opinion, but according to this reference http://www.edn.com/design/component...sformer-at-a-frequency-it-wasn-t-designed-for
For a power transformer designed for 115VRMS at 400 Hz but used at 60 Hz, the input voltage must not exceed 115×60/400 = 17.25 VRMS

Perhaps others can offer a critique of the suggested scheme.
 