Small gas engine electric generator ?

Click For Summary
SUMMARY

Connecting two generators, specifically a 10 hp 4.5 kW generator and a 5.5 hp 3 kW generator, to power a house is not advisable due to insufficient current capacity. The 4.5 kW generator provides only 15 amps, while the air conditioning unit requires 30 amps at 240 volts, and the dryer also demands 30 amps at 220 volts. Proper synchronization of generators requires matching frequency, phase angle, and amplitude, which is complex and risky without specialized equipment. The recommended solution is to either use a generator designed for parallel operation or to split the load between the two generators.

PREREQUISITES
  • Understanding of generator specifications (e.g., horsepower, kilowatt rating)
  • Knowledge of electrical load requirements for household appliances
  • Familiarity with generator synchronization techniques
  • Awareness of safety protocols when working with electrical systems
NEXT STEPS
  • Research generator synchronization methods and equipment, including syncroscopes
  • Explore generators designed for parallel operation, such as Honda models
  • Learn about load balancing techniques for multiple generators
  • Investigate the electrical requirements of household appliances to determine power needs
USEFUL FOR

This discussion is beneficial for homeowners considering backup power solutions, electricians, and anyone interested in generator operation and synchronization techniques.

zanegrey
Messages
1
Reaction score
0
hi,
i want to know if i can tie 2 generators together to get enough amps to run my house.

i have an older 10 hp 4.5 k watt genset and a 5.5 hp 3 k watt genset.

the 4.5 k genset is a 240 plug in but only 15 amps

my ac is 240 at 30 amps
and dryer require 220 at 30 amps.


thanks
 
Engineering news on Phys.org
Doesn't sound like a good idea to me. Even if you could, you wouldn't have enough current to run your house.
BTW Welcome to PF
 
If you want to run the AC and dryer at the same time, those generators aren't powerful enough.
 
I'm not an expert, and have never done this, but there seems to be very few replies, so here's something I found when I quickly googled your query yesterday (the warnings, pitfalls, and a method for linking the generators):

http://yarchive.net/car/rv/generator_synchronization.html

When you're trying to put generators in parallel, it's best to use generators designed for this purpose (I think there're a few Hondas that do this). Otherwise, you'll need to match frequency, phase angle, and (preferably) amplitude, or else danger ensues (mostly to the generators, but also possibly to you and your house).

These aren't exactly the necessities of life, however. If you're going off the grid, or want to prepare for (prolonged) power outages, could you rough it? That or just buy a bigger generator.
 
I think it is a bit dodgy to parellel up two different generators.. Tricky enough if they are identical. Trying to alter frequency and phase with simple generators wouldn't be easy.

You could get large circulating currents. You would need a syncroscope (expensive??) to get the phasing right and suitable switch gear.

Why do you need to do it anyway??

Only other way is the split the load between the two.. Much safer.
 

Similar threads

Replies
9
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
0
Views
2K
  • · Replies 9 ·
Replies
9
Views
3K
  • · Replies 1 ·
Replies
1
Views
1K
Replies
24
Views
6K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 21 ·
Replies
21
Views
10K
  • · Replies 1 ·
Replies
1
Views
2K