Saladsamurai said:
You know what I don't like? They are called Laws yet after an hour of searching I have yet to find one derivation. I am sure it is out there (maybe), but I have had no luck.
I found one mention that the Bernoulli conditions need to be assumed.
Edit: I guess that it makes sense. A law is not actually derived so to speak. It is observed. I really just need to get my hands on some test results.
The affect of changing rpm is linear with fan speed because of geometry. When you spin a fan, it takes a certain size slug of air and moves it past the fan. Sping it twice, and it takes two slugs of air of that size and moves them past the fan. So there isn't really anything to derive for that part.
The part about the effect that has on pressure is "derived" (if you can even call it that) by taking two examples of Bernoulli's equation and setting them equal to each other (V and 2V, for example), similar to the way the various forms of the ideal gas law are generated.
The part about the effect that has on fan power is derived from the equation for power, in the same way.
They are just ratios of two applications of the appropriate equations.
So let me ask those in the field this: when, if ever, are the fan laws of any use?
I use them all the time to answer the following questions:
-Can I increase the airflow of this fan on this system without over-amping the motor, exceeding 60hz on the vfd, etc?
-Can I add a heat recovery coil to this system and still generate the airflow I need (without overamping the motor, exceeding 60 hz, etc...)?
-Why does lowering the resistance on this fan cause it to over-amp? (that's a really counterintuitive one)
-If I shut my outside air damper at night and circulate return air through the unit, what is my fan energy penalty?
-If I reduce my room air change rate by half at night due to a night set back mode, how much fan energy do I save?
-The fan is running at 50 hz, 80% of airflow and 60% of max fan rpm. What happens when I up it to 60 hz?
-How much energy/airflow does this broken damper, clogged coil, etc. cost me?
-If I cut my airflow in half, does the dP sensor on my air measuring station still have enough dP to measure the airflow?
Now sometimes you can read these directly from the fan curve, but particularly when you don't have a fan curve at hand, the affinity laws can be very useful for answering these questions.
So the affinity laws will not hold in a fan mapping test even if the fan speed is not held as a constant.
A fan mapping test
is a test! You measure every possible parameter you can to avoid errors from calculations. For example, as you close that damper and map the performace of that first fan at a constant rpm, applying the affinity law will give you a straight line for rpm vs airflow. But this fan doesn't perform exactly like the affinity laws predict (no fan does). So you want to actually measure all of these parameters for the test.
By virtue of the fact that in a fan mapping, there are varying resistances being applied, there will always be a pressure change. Thus, the conditions are not always constant and...
Well hold on - the fan laws still apply, they just aren't absolutely perfect. If you crank down on the damper for the test, the result you get should should follow
the applicable law to within a few percent. You just chose a fan law that doesn't describe the situation you are dealing with, that's all! The law you want is the one that relates flow and pressure.
The paremeters being discussed are:
rpm
pressure
velocity (cfm)
power
When you apply the affinity laws, you have to choose the law that describes the situation you are analyzing. If you make an adjustment that changes the resistance in the duct, you need to relate pressure, velocity and power. RPM hasn't changed, so there isn't any reason to use that law. Changing the resistance in the duct and changing the rpm are two completely separate ways of affecting the airflow.