Supplied complex power from source vs consumed by load

Click For Summary
SUMMARY

The discussion focuses on calculating the total complex power consumed by a load in a three-phase system, using the formula S = 3VaIa*. The calculated total complex power supplied from the source is 2592W + j3456 VAR, while the power consumed by the load, derived from the load impedance of 5 + j6 and load current of 12<-53.13A, is initially calculated as 720W + j864VAR. Participants confirm that the load power must be multiplied by 3 to account for the three-phase system, leading to a total of 2160W + j2592VAR. The load power factor is determined to be 0.64 lagging.

PREREQUISITES
  • Understanding of complex power calculations in AC circuits
  • Familiarity with three-phase power systems
  • Knowledge of load impedance and current phasors
  • Proficiency in using the formula S = I²Z for power calculations
NEXT STEPS
  • Study the derivation of complex power in three-phase systems
  • Learn about the implications of load impedance on power factor
  • Explore the use of phasor diagrams in AC circuit analysis
  • Investigate the effects of line impedance on total power calculations
USEFUL FOR

Electrical engineers, students studying power systems, and professionals involved in AC circuit analysis will benefit from this discussion.

eehelp150
Messages
235
Reaction score
0

Homework Statement


upload_2016-10-27_0-28-37.png

upload_2016-10-27_0-28-49.png


Homework Equations


S= 3VaIa*

The Attempt at a Solution


After transformation:
upload_2016-10-27_0-30-5.png

Ia = 120<0 / (6+8j) = 12<-53.13 A
Total complex power = 3 * Va * Ia* = 3*120<0 * 12<53.13 = 2592W + j3456 VAR
This is the power supplied from source. What would be the power consumed by load?
 

Attachments

  • upload_2016-10-27_0-28-36.png
    upload_2016-10-27_0-28-36.png
    10.1 KB · Views: 559
Physics news on Phys.org
eehelp150 said:
What would be the power consumed by load?
You know the load impedance and load current. How will you determine the active and reactive power associated with the load?
 
cnh1995 said:
You know the load impedance and load current. How will you determine the active and reactive power associated with the load?
Load impedance = 5 + j6
Load current = 12<-53.13A
I*I*Z
?
 
eehelp150 said:
Load impedance = 5 + j6
Load current = 12<-53.13A
I*I*Z
?
Yes. Take magnitudes only.
S=I2Z.
 
Last edited:
cnh1995 said:
Yes. Take magnitudes only.
S=I2Z.
So 144 * (5+j6)
?

power of (1+j2)= 144 * (1+2j)
and
(load) = 144*(5+j6)
combined become 864W + j1152VAR

but the total complex power is 2592W + j3456VAR

Is it right for these values to not match?
 
Last edited:
eehelp150 said:
So 144 * (5+j6)
Yes.
eehelp150 said:
Is it right for these values to not match?
Yes. Can you say why?
 
cnh1995 said:
Yes.

Yes. Can you say why?
Is it because it's 1/3 of the "actual" circuit?
Do I need to multiply by 3 to get the total complex power consumed by load?

If no, does this look correct?
720W + j864VAR

Load power factor:
S = sqrt(Q^2+P^2) = 1124VA
PF = P/S = 720/1124 = 0.64 lagging (Q>0)
correct?
 
eehelp150 said:
Is it because it's 1/3 of the "actual" circuit?
Do I need to multiply by 3 to get the total complex power consumed by load?

If no, does this look correct?
720W + j864VAR

Load power factor:
S = sqrt(Q^2+P^2) = 1124VA
PF = P/S = 720/1124 = 0.64 lagging (Q>0)
correct?
Well, you calculated the total power for three phases. So, you should multiply the load power by 3. But they are not equal because out of total input power, some power is associated with the line impedance 1+j2 ohm. Remaining power is fed to the load.
 
cnh1995 said:
Well, you calculated the total power for three phases. So, you should multiply the load power by 3. But they are not equal because out of total input power, some power is associated with the line impedance 1+j2 ohm. Remaining power is fed to the load.
If the prompt is:
Calculate the total complex power consumed by the load and determine the load's power factor

Do I use what I calculated (720W + j864VAR) or do I need to multiply that by 3?
 
  • #10
eehelp150 said:
If the prompt is:
Calculate the total complex power consumed by the load and determine the load's power factor

Do I use what I calculated (720W + j864VAR) or do I need to multiply that by 3?
You should multiply by 3. You have transformed the circuit into its per phase equivalent. Total power will be thrice the per phase power.
eehelp150 said:
power of (1+j2)= 144 * (1+2j)
and
(load) = 144*(5+j6)
combined become 864W + j1152VAR
Here, while applying S=I2Z, you should consider the magnitude only. If you want to use the phasor form, you should take the conjugate of the current i.e. (IZ)(I*).
 
  • #11
cnh1995 said:
Well, you calculated the total power for three phases. So, you should multiply the load power by 3. But they are not equal because out of total input power, some power is associated with the line impedance 1+j2 ohm. Remaining power is fed to the load.
If the prompt is:
Calculate the total complex power consumed by the load and determine the load's power factor

Do I use what I calculated or do I need to multiply that by 3?
cnh1995 said:
You should multiply by 3. You have transformed the circuit into its per phase equivalent. Total power will be thrice the per phase power.

Here, while applying S=I2Z, you should consider the magnitude only. If you want to use the phasor form, you should take the conjugate of the current i.e. (IZ)(I*).
So magnitude of (5+j6) = sqrt(61)?
 
  • #12
eehelp150 said:
Calculate the total complex power consumed by the load and determine the load's power factor
cnh1995 said:
You should multiply by 3. You have transformed the circuit into its per phase equivalent. Total power will be thrice the per phase power.
For load power factor, you can use the single phase equivalent network since it is a balanced network.
eehelp150 said:
So magnitude of (5+j6) = sqrt(61)?
Yes.
 
  • #13
cnh1995 said:
For load power factor, you can use the single phase equivalent network since it is a balanced network.

Yes.
so load would be 3 * 144*sqrt(61)?
How do i get power factor from this?
 
Last edited:
  • #14
eehelp150 said:
so load would be 3 * 144*sqrt(61)?
How do i get power factor from this?
If the load impedance is R+jX, what would its power factor?
 

Similar threads

  • · Replies 18 ·
Replies
18
Views
2K
  • · Replies 2 ·
Replies
2
Views
6K
  • · Replies 6 ·
Replies
6
Views
4K
  • · Replies 18 ·
Replies
18
Views
3K
  • · Replies 13 ·
Replies
13
Views
2K
Replies
2
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 40 ·
2
Replies
40
Views
5K
  • · Replies 5 ·
Replies
5
Views
2K
Replies
2
Views
4K