Surprising HVAC Lesson: Air Conditioning Costs in Philly vs. Vegas

AI Thread Summary
Air conditioning costs in Philadelphia are significantly higher than in Las Vegas due to differences in enthalpy and humidity levels. In Philadelphia, the design conditions result in an enthalpy of 39.0 btu/lb, while in Las Vegas, it is lower at 33.0 btu/lb, indicating that it is 18% hotter in Philly on a typical August day. This difference means that cooling requires 57% more energy in Philadelphia compared to Las Vegas. The closer the dry and wet-bulb temperatures are, the more energy is needed for conditioning. Understanding these factors is crucial for HVAC system design and energy cost calculations.
Messages
23,694
Reaction score
11,136
One of the guys I work with is taking a course in HVAC and since my boss used to teach it, we got a little lesson today (helping with the homework). The result of the conversation was the realization that it costs significantly more to air condition a building in Philadelphia than it does in Las Vegas. Surprising, huh? Here's the math though:

Indoor design conditions are for 75F and 50% relative humidity. That corresponds to an enthalpy of about 28.5 (btu/lb). In Philly, the design conditions (from NOAA data) are 92F dry bulb and 75F wet bulb (that's about 48% relative humidity). That corresponds to an enthalpy of 39.0. In Vegas, the conditions are 112F wb and 68F db (about 8% rh). Thats an enthalpy of about 33.

So the difference between the two enthalpies means its 18% hotter! in Philly than in Vegas on a typical August day and requires 57% more energy (10.5 vs 4.5 btu/lb of air) to cool outside air (your house is more complicated since much of the load is actually solar).
 
Engineering news on Phys.org
Not bad on your explanation. When I design systems and calculate annual energy costs, a good rule of thumb to use is the closer the dry and wet-bulb temperatures are to each other, the more energy you'll use to condition the space. Air conditioning systems cool 'sensibly' first, ie they change the dry bulb temperature. The last thing that they do is remove moisture, ie they drastically change the enthalpy, humidity, etc. Here in Houston, the design dry bulb is 96 and the wet bulb is 79 (depending on the source)--a resulting enthalpy over 42 btu/lbm!

Let me know if you have any further questions on the matter. The subject is still pretty fresh in my mind--I just took my Mechanical PE exam a few months ago.
 
How did you find PF?: Via Google search Hi, I have a vessel I 3D printed to investigate single bubble rise. The vessel has a 4 mm gap separated by acrylic panels. This is essentially my viewing chamber where I can record the bubble motion. The vessel is open to atmosphere. The bubble generation mechanism is composed of a syringe pump and glass capillary tube (Internal Diameter of 0.45 mm). I connect a 1/4” air line hose from the syringe to the capillary The bubble is formed at the tip...
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
I'd like to create a thread with links to 3-D Printer resources, including printers and software package suggestions. My motivations are selfish, as I have a 3-D printed project that I'm working on, and I'd like to buy a simple printer and use low cost software to make the first prototype. There are some previous threads about 3-D printing like this: https://www.physicsforums.com/threads/are-3d-printers-easy-to-use-yet.917489/ but none that address the overall topic (unless I've missed...
Back
Top