Switching high voltages with arduino and a relay

  • Thread starter Thread starter William123
  • Start date Start date
  • Tags Tags
    Arduino Relay
Click For Summary
SUMMARY

This discussion centers on safely switching high voltages using an Arduino and a relay, specifically addressing the importance of correctly handling the phase, neutral, and ground wires. It is established that only the phase wire should be interrupted while maintaining the integrity of the neutral and ground wires to ensure safety. The relay mentioned has a contact rating of 10 amps for resistive loads at 120V and 240V AC, and 10A at 28V and 30V DC, but only 3 amps for inductive loads. Proper relay specifications must be consulted to avoid damaging the relay when switching inductive loads.

PREREQUISITES
  • Understanding of electrical wiring: phase, neutral, and ground connections
  • Familiarity with Arduino programming and relay control
  • Knowledge of relay specifications and ratings, particularly for inductive loads
  • Experience with electrical safety standards and practices
NEXT STEPS
  • Research "Arduino relay control for high voltage applications"
  • Study "Relay contact ratings for inductive vs. resistive loads"
  • Learn about "double insulated appliances and their safety requirements"
  • Explore "GHI Electronics Relay specifications for SRD-05VDC-SL-C"
USEFUL FOR

Electronics hobbyists, electrical engineers, and anyone interested in safely integrating Arduino with high voltage systems.

William123
Messages
39
Reaction score
0
Hello

I came across this video on youtube where a guy was switching a lightbulb on and off with an arduino and a relay ().
I was bothered by how he left out the phase wire (look at the image at 4 mins and 53 sec in). People mostly seem to be complaining about how he is breaking the ground wire, and I can see why that is wrong too, but shouldn't he also be using all three wires aswell? Even if he was breaking the phase wire and left out the ground wire then wouldn't it be unsafe to use this "adapter" with appliances that need to be grounded? If I were to do this then I would try to make the adapter like an extension of the wall outlet by connecting all three wires in both ends and breaking the phase wire, that way you could use it for appliances that are either grounded or not. Am I right or wrong?

Also, I saw another video of a guy who was switching a light bulb on and off in the same way and he was using a plug that looked kind of like the 2 prong euro plug (he had wired it up himself). To do this safely, you would have to look for a lightbulb/socket that are double insulated right?

Regards
 
Engineering news on Phys.org
William123 said:
Hello

I came across this video on youtube where a guy was switching a lightbulb on and off with an arduino and a relay ().
I was bothered by how he left out the phase wire (look at the image at 4 mins and 53 sec in). People mostly seem to be complaining about how he is breaking the groIf I were to do this then I would try to make the adapter like an extension of the wall outlet by connecting all three wires in both ends and breaking the phase wire, that way you could use it for appliances that are either grounded or not. Am I right or wrong?

Also, I saw another video of a guy who was switching a light bulb on and off in the same way and he was using a plug that looked kind of like the 2 prong euro plug (he had wired it up himself). To do this safely, you would have to look for a lightbulb/socket that are double insulated right?

Regards

Didn't watch the vid, but yes, you want the phase to be the only one interrupted. Everything else should be as if this 'switch' is not even there. In the USA the neutral is NEVER EVER supposed to be interrupted. And of course the ground is the same.
 
  • Like
Likes   Reactions: berkeman, Asymptotic, jim mcnamara and 1 other person
What @Averagesupernova said. The 'hot' wire should be the only one switched.

Another thing ... the presenter stated 10 amp contact ratings at 120V and 240V AC voltage, and 10A at 28V and 30V DC. This is true for resistive loads (1), but contact rating is 3 amps for inductive loads. The small fan in the video should be low current and under the 3 amp rating, but even so, switching inductive loads reduces contact life, and it is a good idea to look closely at the https://www.ghielectronics.com/downloads/man/20084141716341001RelayX1.pdf relay specifications.

(1) For form A contacts. Couldn't make out the relay part number in the video, but it was SRD-05VDC-SL-C in a photograph I found online describing the HL52S relay board. Current rating for form C contacts is 7 amps at 240 VAC and 28 VDC.
 

Similar threads

  • · Replies 7 ·
Replies
7
Views
1K
Replies
37
Views
7K
Replies
17
Views
3K
  • · Replies 10 ·
Replies
10
Views
2K
Replies
12
Views
4K
  • · Replies 4 ·
Replies
4
Views
4K
  • · Replies 11 ·
Replies
11
Views
5K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 14 ·
Replies
14
Views
4K
  • · Replies 19 ·
Replies
19
Views
4K