Thermodynamics: Control Volume flow through radiatior

Click For Summary
SUMMARY

The discussion focuses on calculating the outlet temperature of air passing through a car radiator, where air enters at 50 km/hr and 25°C, while water enters at 200°C and exits at 180°C. The energy balance equations for both air and water are established, with the assumption of ideal gas behavior for air and constant pressure conditions. The final calculations suggest an air mass flow rate of 16.5 kg/s and an outlet temperature of approximately 35.7°C, indicating significant heat removal from the water.

PREREQUISITES
  • Understanding of thermodynamic principles, particularly energy balance equations.
  • Familiarity with ideal gas laws and specific heat capacities (C_p and C_v).
  • Knowledge of heat transfer concepts in fluid systems.
  • Ability to perform calculations involving mass flow rates and enthalpy changes.
NEXT STEPS
  • Study the application of the first law of thermodynamics in control volume analysis.
  • Learn about the properties of water and air at various pressures and temperatures.
  • Investigate the use of specific heat capacities in different thermodynamic processes.
  • Explore advanced heat exchanger design principles and performance calculations.
USEFUL FOR

Mechanical engineers, thermodynamics students, and professionals involved in HVAC systems or automotive thermal management will benefit from this discussion.

aznkid310
Messages
106
Reaction score
1

Homework Statement



Air enters a car radiator at 50 km/hr, 25 C. The radiator is 1 m2 facial area. 2 kg/s of water enters the radiator from the engine at 10 bar, 200 C and leaves at 10 bar, 180 C. What is the temperature of the air as it leaves the radiator?

Homework Equations



I did an energy balance for air and then for water, but I am not sure which terms can be ignored. After i obtain these eqns, i can set them equal to each other and solve for T (from
Q =m(c_p)(Change in T))?

The Attempt at a Solution



For Air: W = Q + (m)(h_in + [(v_in)^2]/2 +g*z_in - h_out - [(v_out)^2]/2 -g*z_out)

m = mass flow rate
Q = heat flow rate
W = work flow rate
h = enthalpy
v = velocity

I assume W, z_in, z_out are zero and also that m_in = m_out

So i get Q = m(h_in - h_out + [(v_in)^2]/2)

For water:

Q = m(h_out - h_in) = (0.2)(762.8 - 2827.9) = -2065.1 kW
 
Physics news on Phys.org
Hi aznkid. You've almost got it. On the right track anyway.

The problem gives you air velocity into the radiator but not out of the radiator. From that I'd simply assume the velocity out is equal to the velocity in, so your velocity terms in your equation:
Q = m(h_in - h_out + [(v_in)^2]/2)
also drop out and you're left with the change in enthalpy for the air.

Now the only part of the problem you really haven't resolved is how to determine mass flow rate of air. How do you think you can determine mass flow rate of air? Note the variables you're given:
- Velocity
- cross sectional area
- Inlet temp
 
Can i assume its an ideal gas?

Then i can use the ideal gas eqn to get specific volume v: pv = RT, where R = 8.314/MW

Next, m = VA/v [(velocity*area)/specific volume]?
 
aznkid310 said:
Can i assume its an ideal gas?

Then i can use the ideal gas eqn to get specific volume v: pv = RT, where R = 8.314/MW

Next, m = VA/v [(velocity*area)/specific volume]?

You sure can.
 
You can assume ideal gas in order to calculate specific volume, or just look up density for air at standard conditions.
 
So can i assume standard air pressure of 101.325 kPa?

Then once i find Q, i can use Q = mc(change in T) to find T?

What would my c be?
 
aznkid310 said:
So can i assume standard air pressure of 101.325 kPa?
Sure... If they don't give you atmospheric pressure, just assume it's standard conditions.

aznkid310 said:
Then once i find Q, i can use Q = mc(change in T) to find T?

What would my c be?
I think you're asking whether to use Cv or Cp.

Consider it this way.

mCp(dT) calculates a change in enthalpy.

mCv(dT) calculates a change in internal energy.

Do you know which one is applicable here?
 
Since it's constant pressure, would it be C_p?

v = RT/p = (8.314)(298)/(101.325) = 0.8458 m^3/g = 845.8 m^3/kg

m = (13.89 m/s)(1 m^2) / (845.8 m^3/kg) = 0.0164 kg/s

Then Q = m*c_p*(T_2 - T_1), where Q = 2065.1 kW (from h20 calculated before)

2065.1 kW = (0.0164 kg/s)*(1.005 kJ/kg k)*(T_2 -298K)

T_2 = 125592.26 K

This seems wrong
 
Last edited:
For water at 10 barg, saturation temp is 184 C which means the water is going in superheated and coming out subcooled.

For water at 10 bara, saturation temp is 179.4 C which means the water is going in and coming out superheated.

Let me guess... this problem was made up by a grad student, right? lol

Let's just assume the person that created this problem meant for the water to be liquid in and out. I'll use 170 C inlet and 150 C outlet at 10 barg.. You should get an energy removal of roughly 177 kW. (or 237 hp) so the power removed his HUGE. A very large truck might approach this much heat rejection at full tilt, but that’s way more than a car.

Also, I’m getting an air mass flow rate of 16.5 kg/s and an outlet temperature of roughly 35.7 C.

Give it another shot.
 
  • #10
Was there a particular reason you chose 170C and 150C?
 
  • #11
aznkid310 said:
Was there a particular reason you chose 170C and 150C?
um... yea. because it's less than the saturation pressure of water at 10 barg, and because specific heat is roughly constant over the range of pressure and temperature you're looking at so I would want to maintain the 20 degree C dT.
 

Similar threads

  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 10 ·
Replies
10
Views
4K
  • · Replies 2 ·
Replies
2
Views
5K
  • · Replies 4 ·
Replies
4
Views
3K
Replies
12
Views
2K
Replies
17
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 9 ·
Replies
9
Views
3K
Replies
3
Views
4K