The discussion clarifies the specifications of an old transformer with input ratings of 115V at 1.2A (approximately 140W) and output ratings of 40,000V at 2mA (approximately 80W). The transformer operates with a Power Factor (PF) of 0.57, indicating a phase angle of about 55 degrees between input voltage and current. The primary fuse is identified as a Bussmann type MDL rated at 1.2A, and the transformer is suggested to be suitable for both 60Hz and 400Hz applications, likely indicating its use in aircraft. Caution is advised due to the high voltage output.

PREREQUISITES
  • Understanding of transformer specifications and operation
  • Knowledge of Power Factor (PF) and phase angle concepts
  • Familiarity with AC voltage ratings and frequency (Hz)
  • Awareness of electrical safety protocols when handling high voltage
NEXT STEPS
  • Research transformer operation principles and efficiency losses
  • Learn about Power Factor correction techniques
  • Investigate Bussmann fuse types and their applications
  • Explore high voltage safety measures and handling procedures
USEFUL FOR

Electrical engineers, hobbyists working with transformers, and anyone involved in high voltage applications will benefit from this discussion.

teroenza
Messages
190
Reaction score
5
Can someone help me better understand the specs for this old transformer I found? I'm confused why the input and output power see to differ greatly (115V*1.2A ~140W while 40,000V*2mA~ 80W).

Also, the fuse rating is unclear to me. Does that mean 1 and 2/10 amp?

Untitled-picture-r0u753.png
 

Attachments

  • Untitled-picture-r0u753.png
    Untitled-picture-r0u753.png
    73 KB · Views: 839
Engineering news on Phys.org
Here is a basic description.

The input is rated in Volt-Amps, not Watts. Using the nameplate ratings, the Power Factor (PF) is about 0.57. Since a transformer is coils of wire, it has Inductance, and an Inductance opposes any change in the current flowing thru it. That means, for instance, that the peak current in an inductor (the primary of the transformer) lags, or occurs later than, the voltage peak.

A PF of 0.57 means the phase angle between the input voltage and the input current is about 55 degrees; with a full electrical cycle of the input AC being 360 degrees.

In an actual, physical, transformer there are also losses in the core and in the resistance of the windings that need to be accounted for to get a precise answer. For this specific transformer one of the limiting factors for output current is likely the temperature of the secondary winding. It uses very fine wire to get many more turns to step up the input voltage. A long piece of small diameter wire has a relatively high resistance which means it gets hot with just a little current flowing thru it.
 
It doesn't appear to be a transformer per se. Output is 0 to 40 kV DC at 2 mA max.

0-115/125 V AC at 60/400 Hz suggests it may have been made to operate from aircraft (400 Hz) as well as from 60 Hz U.S. line supply.

It is probably old; been awhile since nameplates used "CY" (cycles) or CPS (cycles per second) instead of Hz (Hertz).

Primary fuse is a Bussmann type MDL (250V, slow blow, 1/4 x 1-1/4", glass tube) rated one and two-tenths (1-2/10) amps.

Be careful. Handling 40 kV at 2 mA requires a respectful nature.
 
Asymptotic said:
It doesn't appear to be a transformer per se. Output is 0 to 40 kV DC at 2 mA max.

0-115/125 V AC at 60/400 Hz suggests it may have been made to operate from aircraft (400 Hz) as well as from 60 Hz U.S. line supply.

It is probably old; been awhile since nameplates used "CY" (cycles) or CPS (cycles per second) instead of Hz (Hertz).

Primary fuse is a Bussmann type MDL (250V, slow blow, 1/4 x 1-1/4", glass tube) rated one and two-tenths (1-2/10) amps.

Be careful. Handling 40 kV at 2 mA requires a respectful nature.
It also might mean there is only one fuse of a rating 2/10 amp.
 
arydberg said:
It also might mean there is only one fuse of a rating 2/10 amp.
True, but primary current rating is 1.2 amps. This is 100% of a 1-2/10 amp rated fuse, but 600% of a 0.2 amp fuse.
 
Couldn't find this particular supply, but suspect it is similar to several available at Surplus Sales of Nebraska like the one pictured below.

HiV Supply.jpg
 

Attachments

  • HiV Supply.jpg
    HiV Supply.jpg
    15.6 KB · Views: 440
Thank you all for the information. I should have noticed off the bat that it's output was DC. After finding it, my original idea was to build a Jacob's ladder, but <2mA of output current seems too low.
 
teroenza said:
but <2mA of output current seems too low.
Try it and see.

Oh, and let us know too.
 

Similar threads

  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 10 ·
Replies
10
Views
4K
  • · Replies 7 ·
Replies
7
Views
6K
  • · Replies 8 ·
Replies
8
Views
3K
Replies
14
Views
3K
Replies
6
Views
3K
  • · Replies 10 ·
Replies
10
Views
6K
  • · Replies 15 ·
Replies
15
Views
5K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 10 ·
Replies
10
Views
4K