Variable resistor & inductor connected to alternator

AI Thread Summary
Connecting a variable resistor, inductor, and capacitor in series with a synchronous generator affects the turbine and generator by altering the torque angle, which influences the generator's performance. As electrical load increases, the torque angle increases, leading to a misalignment between the stator and rotor fields, resulting in back electromotive force (back emf). This back emf is out of phase with the normal voltage and indicates that the generator is supplying both reactive and real power. The relationship between torque angle and back emf is crucial, as the angle determines the amount of torque required to maintain synchronization. Overall, the interplay between active and reactive power significantly impacts the generator's operation and efficiency.
CraigH
Messages
221
Reaction score
1
A simple 2 pole alternator (a synchronous generator), is powered by a steam turbine. The amount of steam to the turbine is kept constant with a constant pressure ##p##, flow rate ##\dot{q}##, and power ##P##.

If a variable resistor, inductor, and capacitor are connected in series to the electrical power output of the generator, what will be the effect on the turbine and generator ?

The frequency of electrical power supplied by the generator must remain constant, because it is a synchronous generator so the frequency of electrical power output is inherently locked to the frequency of the prime mover. (In this case the steam turbine, which is constant).

So what is the effect on the turbine and generator?

I understand that it is something to do with the torque angle of the generator. A bigger electrical load increases the torque angle, but why?

Also, when the torque angle increases from zero the field of the stator no longer perfectly aligns with the field of the motor, so now a back emf is generated across the generator## ^1##. But how exactly does this all change when the resistance, inductance, and capacitance of the electrical load is changed?

##^1## This is a separate question, but why does a non zero load angle mean a back emf is generated? What is the relationship between torque angle and back emf? Am I also correct in saying that this back emf is out of phase with the "normal" voltage induced because of the rotating field of the rotor, and hence the generator also supplies reactive power as well as real power?
 
Engineering news on Phys.org
If a resistor is connected, it will consume active power.
An inductor will comsume reactive power.
A capacitor will produce reactive power.

The generator must produce or consume all these types of power (nobody else to do it). In case of reactive power, the angle between generated voltage and current will be ±90 degrees. In case of active power, the angle will be 0 degrees. When active and reactive power are combined, the angle between voltage and current will be somewhere in between 0 and 90 degrees. This phaseshift will influence the torque angle.

But even if you connect only a resistor, the angle between the magnetic fields from the stator and the rotor will change, because the resistor consumes active power, and therefore the gap between the rotor and the stator must yield a torque. This torque increases as the angle increases from 0 (minimum torque) to ±90 degrees (maximum torque). The torque is proportional to sin(angle).

The calculations regarding the torque angle are complex, because the generator has inductance and resistanse in its stator, which are included in the circuit as a whole.
 
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...