Voltage drop calculation in 3 phase unbalance circuit

Click For Summary
The discussion focuses on calculating total voltage drop in a three-phase unbalanced circuit, specifically from a source to individual loads connected to a distribution board (DB-A). The user, Kelvin, seeks clarification on how to calculate voltage drop when only one load is active and whether to use different voltage drop factors and voltages based on the load configuration. He also questions how to approach voltage drop calculations in scenarios with unbalanced loads, particularly when varying load sizes are present. The complexities arise from the need to determine the appropriate voltage drop factors for different sections of the circuit. Overall, the discussion highlights the challenges in accurately assessing voltage drop in unbalanced systems.
ben1000
Messages
1
Reaction score
0
Dear All,

I’m facing some problem when I try to determine the total voltage drop (%) from the source to the load.

Assume the condition as follow:

1. DB-A is serving 3 number of individual load (#1,#2 and #3) , each 100m away from DB-A, single phase, 5kw, pf=0.85, V=240V,by using individual cable 2Core, 16mm2 PVC/SWA/PVC copper cable (2.7mV/m/A).

2. The incoming power supply (415V, 3 phase) to serve DB-A is also 100m away, using 4Core, 16mm2 PVC/SWA/PVC copper cable (2.3mV/m/A).

For calculate total voltage drop from the source to the load #1. I’m using formula as follow:

Assume all three loads are on.
Total connected load under DB-A = 15kw = 15/0.85/0.7188= 26.085A

Load #1 = 5kw = 5/0.85/0.24 = 26.04A

VD (source to DB-A) = [(100m x 2.3mV/m/A x 26.085)/1000/415V] x 100%
= 1.45%

VD (DB-A to load #1) = [(100m x 2.7mV/m/A x 26.04)/1000/240V] x 100%
= 2.93%

VD total = 1.45% + 2.93 % = 4.38%

My question is how to determine the total voltage drop (%) at load #1 if the load #2 & #3 are off. Or let said load #2 and #3 is disconnected from DB-A
I’m confused which VD factor of cable and applied voltage should I applied when calculate VD (source to DB-A). 2.3mV/m/A or 2.7mV/m/A? 415V or 240V? The serving cable is 4 Core, but it just like using 4 Core as 2 Core by only serving load #1.

My second question is how about when there is unbalance load. Assume load # 1 now is 10kw, #2 and #3 are 5kw each. All single phase. How am I going to determine the V.D (%) from the source to DB-A? (Three load are on) should I assume it as balanced? If I do so, does it actually reflect the total V.D (%) suffer at load #1?

Thanks for your help

From
Kelvin
 
Engineering news on Phys.org
I am trying to understand how transferring electric from the powerplant to my house is more effective using high voltage. The suggested explanation that the current is equal to the power supply divided by the voltage, and hence higher voltage leads to lower current and as a result to a lower power loss on the conductives is very confusing me. I know that the current is determined by the voltage and the resistance, and not by a power capability - which defines a limit to the allowable...

Similar threads

Replies
38
Views
6K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 7 ·
Replies
7
Views
5K
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 12 ·
Replies
12
Views
2K
Replies
11
Views
3K
Replies
9
Views
20K
  • · Replies 1 ·
Replies
1
Views
7K
  • · Replies 4 ·
Replies
4
Views
5K
  • · Replies 17 ·
Replies
17
Views
12K