Voltage drop calculations for CCVT's and Current TF's?

Click For Summary
SUMMARY

This discussion focuses on voltage drop calculations for cables used in instrumentation, specifically for Current Transformers (CT) and Capacitive Coupling Voltage Transformers (CCVT) connected to a relay (SEL421). The scenario involves a 300-foot run of #9 AWG cable with a resistance of 0.000729 ohms/ft, carrying a CT current of 5A and a potential of 67V. Participants emphasize the importance of considering voltage drop, especially over long distances, and suggest that if the voltage drop exceeds 5%, a larger gauge cable may be necessary to ensure accurate measurements.

PREREQUISITES
  • Understanding of Current Transformers (CT) and Capacitive Coupling Voltage Transformers (CCVT)
  • Familiarity with voltage drop calculations in electrical systems
  • Knowledge of AWG (American Wire Gauge) standards and cable specifications
  • Basic principles of relay operation and input requirements
NEXT STEPS
  • Research voltage drop calculation formulas for long cable runs
  • Learn about the specifications and limitations of the SEL421 relay
  • Investigate the impact of cable gauge on voltage drop and measurement accuracy
  • Explore best practices for selecting conductors in high-voltage applications
USEFUL FOR

Electrical engineers, instrumentation specialists, and technicians involved in substation design and maintenance, particularly those working with protective relays and voltage/current measurement systems.

this1ssteve
Messages
2
Reaction score
0
I have not found a straightforward explanation on how to perform voltage drop calculations for cables used for instrumentations purposes. Suppose you have Current Transformer (CT) and Potential Transformer (PT) connections coming into a relay (IE SEL421). If we have a cable that runs from the yard equipment to the panels, let's say 300 Feet, using a #9 cable rated at 0.000729 ohms/ft, and we want the CT current to be 5A and the Potential coming into the relay to be at 67V, how do we determine this?
 
Engineering news on Phys.org
this1ssteve said:
I have not found a straightforward explanation on how to perform voltage drop calculations for cables used for instrumentations purposes. Suppose you have Current Transformer (CT) and Potential Transformer (PT) connections coming into a relay (IE SEL421). If we have a cable that runs from the yard equipment to the panels, let's say 300 Feet, using a #9 cable rated at 0.000729 ohms/ft, and we want the CT current to be 5A and the Potential coming into the relay to be at 67V, how do we determine this?

Welcome to the PF.

What's a CCVT? And what's a TF?
 
this1ssteve said:
I have not found a straightforward explanation on how to perform voltage drop calculations for cables used for instrumentations purposes. Suppose you have Current Transformer (CT) and Potential Transformer (PT) connections coming into a relay (IE SEL421). If we have a cable that runs from the yard equipment to the panels, let's say 300 Feet, using a #9 cable rated at 0.000729 ohms/ft, and we want the CT current to be 5A and the Potential coming into the relay to be at 67V, how do we determine this?
I looked at the specs of the relay. Will the terminals even except a 9 AWG wire? Anyway, why are you needing to determine a voltage drop? Here's a snip from the relay's data sheet for the CT & PT inputs.

CT&PT input specs.jpg


If you don't get 67 volts from the PT when at the nominal line voltage, surely the relay software can provide a way to compensate I would think.

Regards
 
Berkeman:
-CCVT = Capacitive Coupling Voltage Transformer (used in Electrical Substations to step down huge potentials for metering purposes for protective relays)
-TF= Short for Transformer

Dlgoff:
So here is the scenario. We have a huge substation with very long runs between outdoor equipment and indoor relays. Let's say a protective relay needs to measure voltage and current on a line. It utilizes CCVT's (essentially to step down the huge voltages from the kilovolt level to 115V/67V) and CT's (Current transformers that are located on the bushings of a circuit breaker to step down the current from say 2000A to 5A) to be inputted into a protective relay in the control house. Well let's say the control house is located 1000 feet away and those cables are being ran with #9 AWG conductors from the outdoor equipment to the control house. With such a large run, there would be some sort of voltage drop to take into consideration. If there is too much loss (over 5% or so) you would need to size your cable to a bigger gauge. On a side note, the #9 conductor feeds into a panel, which has interconnecting wires that fit the size needed for the relay input.

I suppose my question is:
1) Would voltage drop be needed to be taken into consideration? It's not like the current or potential is being applied to a load, it is being used for measurement purposes, much like an ammeter or voltmeter on multimeter.
2) If so, how do we go about doing this? For CT's, I am not sure if I am doing the secondary voltage current correctly (Vsec=Vpri *(Nsec/Npri) ). For the CCVT's, I am clueless.
 

Similar threads

Replies
12
Views
3K
  • · Replies 16 ·
Replies
16
Views
3K
  • · Replies 12 ·
Replies
12
Views
2K
  • · Replies 3 ·
Replies
3
Views
4K
Replies
35
Views
5K
  • · Replies 8 ·
Replies
8
Views
15K
Replies
3
Views
2K
  • · Replies 21 ·
Replies
21
Views
3K
  • · Replies 20 ·
Replies
20
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K