How much air (maximum) can pass through a 10 cm diameter pipe which is 15 meters long vertically? m3/h scale
Hello kind people of PF

I am looking to mount a fan on one end of a pipe but I'm not sure how much air can the pipe transfer. (Volumetric flow rate)

The pipe is vertical and 15 meters long.It has a diameter of 10 cm. I'm looking to push air from top to bottom using a fan.

Need to know the maximum volumetric flow rate of the pipe on a m3/h scale.

Thank you!

Edit: I got the answers I was looking for and posted a statement in my last comment.Don't try this at home. Lol
 
Last edited:
Engineering news on Phys.org
  • #2
Welcome to PF!
Anon_Miner said:
I am looking to mount a fan on one end of a pipe but I'm not sure how much air can the pipe transfer. (Volumetric flow rate)

The pipe is vertical and 15 meters long.It has a diameter of 10 cm. I'm looking to push air from top to bottom using a fan.

Need to know the maximum volumetric flow rate of the pipe on a m3/h scale.
It depends strongly on how powerful your fan is.
 
  • #3
russ_watters said:
Welcome to PF!

It depends strongly on how powerful your fan is.
Thanks for your reply!

Yes I know that but I wanted to know the maximum capacity of the pipe itself so I don't buy a fan too powerful and waste my money on extra power that will be of no use.
 
  • #4
What kind of flow rates and pressures are you looking for?
 
  • Like
Likes Anon_Miner
  • #5
Chestermiller said:
What kind of flow rates and pressures are you looking for?

I really would like to install a fan that can move 11000 m3/h of air through the pipe but I'm not sure if the pipe can in fact transfer that amount of air.

If 11000 is not a possibility, how about 5500 m3/h of air? Can the pipe support this much air flow?

Pressure is of no consequence.

I only need to know how much air I can move through the pipe.
 
  • #6
11000 m^3/hr is the same as 3.06 m^3/s. The cross sectional area of the pipe is 0.00785 m^2. What kind of flow velocity does this represent, and how does it compare with the speed of sound?
 
  • Like
  • Informative
Likes Anon_Miner, Lnewqban and russ_watters
  • #7
Anon_Miner said:
I really would like to install a fan that can move 11000 m3/h of air through the pipe but I'm not sure if the pipe can in fact transfer that amount of air.

If 11000 is not a possibility, how about 5500 m3/h of air? Can the pipe support this much air flow?

Pressure is of no consequence.

I only need to know how much air I can move through the pipe.
That volume is impossible to achieve for a duct of that diameter.
Is there any way to increase the sectional area of that duct or the number of ducts.
 
  • Sad
Likes Anon_Miner
  • #8
Anon_Miner said:
Yes I know that but I wanted to know the maximum capacity of the pipe itself so I don't buy a fan too powerful and waste my money on extra power that will be of no use.

Anon_Miner said:
I really would like to install a fan that can move 11000 m3/h of air through the pipe but I'm not sure if the pipe can in fact transfer that amount of air.

If 11000 is not a possibility, how about 5500 m3/h of air? Can the pipe support this much air flow?
I'll let you do the math as @Chestermiller suggests, but will add to his point that the speed of sound is the limiting factor on flow through a duct.
Pressure is of no consequence.

I only need to know how much air I can move through the pipe.
Well you need to know pressure in order to size/select the fan. It'll also help you pick the car engine you'll need to run it. :wink:
 
  • Informative
Likes Anon_Miner
  • #9
Lnewqban said:
That volume is impossible to achieve for a duct of that diameter.
Is there any way to increase the sectional area of that duct or the number of ducts.

There are 2 pipes. They have the same diameter (10 cm).
So if 11000 m3/h is impossible for one pipe, then how about 5500 m3/h per pipe? will that work?
 
  • #10
Chestermiller said:
11000 m^3/hr is the same as 3.06 m^3/s. The cross sectional area of the pipe is 0.00785 m^2. What kind of flow velocity does this represent, and how does it compare with the speed of sound?

russ_watters said:
I'll let you do the math as @Chestermiller suggests, but will add to his point that the speed of sound is the limiting factor on flow through a duct.

Well you need to know pressure in order to size/select the fan. It'll also help you pick the car engine you'll need to run it. :wink:

Let me explain my exact situation

There is a room which has some devices in it. The air intake of these devices is 10880 m^3/h. The room has no other air intake except for 2 pipes that are both 10 cm in diameter.

I'm looking to put forward fans on one end of the pipes to supply the air demanded by these devices.

I was looking to put a fan with 11000 m3/h capacity on one pipe to reduce my expenses. but now that it seems one pipe can not support that much of air flow; I'll be looking to put 2 fans with 5500 m3/h capacity on both pipes.

the devices exhaust the air they intake out of the room, which is why I thought since the amount of air intake and air output are very close, there will be no change in the pressure of the room.
 
  • #11
I'm a little confused by this. It seems like the intake and output velocities of these pipes will be extremely high. We're talking higher than severe hurricane and tornado velocities. Does this system already exist? What about the intakes to the room? What are these like?
 
  • Like
Likes Lnewqban
  • #12
Anon_Miner said:
There are 2 pipes. They have the same diameter (10 cm).
So if 11000 m3/h is impossible for one pipe, then how about 5500 m3/h per pipe? will that work?

A regular blower can normally push between 70 and 90 cubic meters per hour through one 10 cm diameter duct.
Any flow forced to go beyond the speed of 20 meters per second creates much noise and requires high pressure fans.

For the amount of ventilation you need, we are talking about one round duct of 80 centimeters of diameter or of a wall louver of 1 meter x 1 meter.

Sorry, Anon, you will need to find an alternate solution to satisfy the air intake requirements of those devices.
Are you sure all of those will be running simultaneously?
 
Last edited:
  • Like
Likes Anon_Miner and russ_watters
  • #13
Anon_Miner said:
Let me explain my exact situation
Thank you!
There is a room which has some devices in it. The air intake of these devices is 10880 m^3/h. The room has no other air intake except for 2 pipes that are both 10 cm in diameter.
[snip]
the devices exhaust the air they intake out of the room, which is why I thought since the amount of air intake and air output are very close, there will be no change in the pressure of the room.

I'm looking to put forward fans on one end of the pipes to supply the air demanded by these devices.
So they take air from inside the room and exhaust it out of the room? Is this a new room or is there currently something providing make-up air at the same airflow?

Unless the pressure difference were huge (enough to collapse the room), the airflow into and out of a room will always be equal.
I was looking to put a fan with 11000 m3/h capacity on one pipe to reduce my expenses. but now that it seems one pipe can not support that much of air flow; I'll be looking to put 2 fans with 5500 m3/h capacity on both pipes.
I suspect you don't know how to select such a fan, and I implore you to keep going with the analysis so you don't make a mistake that costs you thousands of dollars.

Why can't you bring more and/or larger ducts into the room?
 
  • Like
Likes Anon_Miner
  • #14
Lnewqban said:
A regular blower can normally push between 70 and 90 cubic meters per hour through one 10 cm diameter duct.
Any flow forced to go beyond the speed of 20 meters per second creates much noise and requires high pressure fans.

For the amount of ventilation you need, we are talking about one round duct of 80 centimeters of diameter or of a wall louver of 1 meter x 1 meter.

Sorry, Anon, you will need to find an alternate solution to satisfy the air intake requirements of those devices.
Are you sure all of those will be running simultaneously?

I was already planning on using high pressure fans so that is not a problem.

But how much noise are we talking about for moving 5500 m3/h of air through a 10 cm pipe? because the pipes are within walls of a building that has people living inside. will the noise be overwhelming or just a minor nuisance?

unfortunately building/enlarging additional pipes is not possible.

Thanks for taking the time to help me!
 
  • #15
russ_watters said:
Thank you!

So they take air from inside the room and exhaust it out of the room? Is this a new room or is there currently something providing make-up air at the same airflow?

Unless the pressure difference were huge (enough to collapse the room), the airflow into and out of a room will always be equal.

I suspect you don't know how to select such a fan, and I implore you to keep going with the analysis so you don't make a mistake that costs you thousands of dollars.

Why can't you bring more and/or larger ducts into the room?

Unfortunately making additional customization is not a possibility.

The room has always been there but was never used in such manner I'm planning to use it.

This was the kind of fan I was planning to use but apparently the noise of the air traveling through the pipe will make the people living above hell. (The pipes have passed within the walls from the roof to the room).

And the reason I can't bring larger ducts to the room is because this room is kinda in the basement and 3 floors are above it. So there is no way of bringing additional ducts without making drastic changes to the building.

Nevertheless I appreciate your time and efforts!
 
  • #16
Chestermiller said:
I'm a little confused by this. It seems like the intake and output velocities of these pipes will be extremely high. We're talking higher than severe hurricane and tornado velocities. Does this system already exist? What about the intakes to the room? What are these like?
It doesn't exist but I was planning to make it work. However I hadn't accounted for the speed of the air traveling through the pipes and the noise it will make. Such a stupid mistake by me.
The room has no other intakes except for these two pipes.
Anyway thanks for your time!
 
  • #17
Anon_Miner said:
Nevertheless I appreciate your time and efforts!
Wait a minute. Is it possible that you placed a decimal wrong and thus overestimated the air needed by 10x or 100x?

What are the devices in that room that take the air in? Where does the air go?
 
  • Like
Likes Anon_Miner
  • #18
anorlunda said:
Wait a minute. Is it possible that you placed a decimal wrong and thus overestimated the air needed by 10x or 100x?

What are the devices in that room that take the air in? Where does the air go?
Hi
There are 16 devices. Each device has 2 fans. Each fan has an air intake of 340 m3/h.
340*2*16 was my calculation that got me to 10880 m3/h.
The devices are ASIC miners.
As for the air output, I have built an exhaust per device that takes their air output, out of the room.
But since supplying the air needed by the devices seem improbable, everything goes down the drain.
 
  • #19
So basically if i try to move 5500 m3/h of air through a 10 cm diameter pipe, it will reach a speed of 194.52 m/s which is like 700 km/h!:oldlaugh:

I feel really stupid right now:headbang:
Would delete this post if I knew how.

Sorry guys for wasting your time with my negligence before posting here.
And thank you for your replies and efforts. I really appreciate it. You guys are the best. PF is the best.
 
  • #20
Anon_Miner said:
...I feel really stupid right now:headbang:
Would delete this post if I knew how.
...
Don't feel bad.
The incorrect approach is to try to ventilate all these devices that only need to be cooled.

The function of those built-in fans of the devices is to move cool air over the internal electronic components, which temperature should be kept low.
To remove the generated heat away from the electronic components is all is needed.
Those fans were designed to recirculate the air of the room, not outdoors dusty air.
The gradual heating of that room air makes the fan move excessive air over the electronic parts, just to play on the safe side.

The proper way to achieve that cooling is by installation of air conditioning equipment that keeps carrying the heat from the air of the room to the outdoors.
In other words, rather than moving that generated heat out using huge volumes of air, liquid, which can reach higher temperature differential, is doing the work.
You can calculate the capacity of the air conditioning equipment by computing the power consumption of all the devices.

Please, read this related thread:
https://www.physicsforums.com/threads/where-do-i-put-this-server-rooms-air-exhaust.984172/

You are welcome :smile:
 
Last edited:

What is the definition of volumetric flow rate of a pipe?

The volumetric flow rate of a pipe is the volume of fluid that passes through a given cross-sectional area of the pipe per unit time. It is typically measured in units of cubic meters per second (m3/s).

How is the volumetric flow rate of a pipe calculated?

The volumetric flow rate of a pipe can be calculated by multiplying the cross-sectional area of the pipe by the average velocity of the fluid passing through it. This can be represented by the equation Q = A * v, where Q is the volumetric flow rate, A is the cross-sectional area, and v is the average velocity.

What factors can affect the volumetric flow rate of a pipe?

The volumetric flow rate of a pipe can be affected by several factors, including the diameter of the pipe, the viscosity of the fluid, the pressure difference between the two ends of the pipe, and any obstructions or bends in the pipe that may cause turbulence.

How is the volumetric flow rate of a pipe measured?

The volumetric flow rate of a pipe can be measured using various instruments such as flow meters, pitot tubes, or ultrasonic sensors. These instruments measure the velocity of the fluid and use it to calculate the volumetric flow rate.

What are some common applications of knowing the volumetric flow rate of a pipe?

The volumetric flow rate of a pipe is important in many industries, including water and wastewater treatment, oil and gas production, and chemical processing. It is also used in plumbing and HVAC systems to ensure proper flow and distribution of fluids. Additionally, it is crucial in designing and maintaining efficient and safe transportation systems, such as pipelines and water distribution networks.

Similar threads

  • Mechanical Engineering
Replies
4
Views
829
  • Mechanical Engineering
Replies
2
Views
2K
Replies
5
Views
1K
  • Mechanical Engineering
Replies
15
Views
820
  • Materials and Chemical Engineering
Replies
1
Views
440
  • Mechanical Engineering
Replies
31
Views
2K
Replies
8
Views
2K
  • Aerospace Engineering
Replies
10
Views
715
  • Mechanical Engineering
Replies
4
Views
2K
Replies
3
Views
2K
Back
Top