What is the charging current for a 120 ampere-hour storage battery?

  • Thread starter Thread starter da-outcast
  • Start date Start date
  • Tags Tags
    Current
AI Thread Summary
To charge a 120 ampere-hour storage battery in 8 hours, the charging current can be calculated by dividing the ampere-hours by the charging time, resulting in a current of 15 amperes. For a lead-acid battery designed for a continuous discharge of 180 amperes over 5 hours, the time to discharge at a steady current of 220 amperes can be determined using a proportion, yielding approximately 4.5 hours. The discussion emphasizes the simplicity of these calculations, suggesting that they do not require complex RC equations. Participants also engage in light-hearted banter about the problem's complexity. Overall, the conversation highlights basic principles of battery charging and discharging calculations.
da-outcast
Messages
2
Reaction score
0
Charging current

I am total stumped on the following to questions so if someone could show me how to get started that would be good thanks.

1) A storage battery rated at 120 ampere-hours is to be fully charged at constant current in 8 hours. Calculate the charging current.

2) A lead-acid battery is designed to give continuous discharge of 180 amperes for 5 hours. Calculate the time it will be discharged by a steady current of 220 amperes.
 
Last edited:
Physics news on Phys.org
Why don't you use the RC equations for charging and discharging? I would assume you can treat a rechargable battery like a capacity in series with a resistor.
 
Hint: ampere-hours is a product.
 
DDuardo, were you teasing?

1) A storage battery rated at 120 ampere-hours is to be fully charged at constant current in 8 hours. Calculate the charging current.
A current is measured in amperes. To go from ampere-hours to amperes, you divide by hours! Think about it.

2) A lead-acid battery is designed to give continuous discharge of 180 amperes for 5 hours. Calculate the time it will be discharged by a steady current of 220 amperes.
This is really a "proportion" problem. Let t be the time required by the 220 ampere current. Then x is to 220 as 5 is to 180.
Or, in more modern terms, x/220= 5/180.
 
Thank you, HallsofIvy. Yes, it was a joke. I was trying to make the poor guy complicate the problem even further seeing how you just have to multiple a couple of numbers to get the solution. :smile:
 
Gosh, you're evil!
 
I multiplied the values first without the error limit. Got 19.38. rounded it off to 2 significant figures since the given data has 2 significant figures. So = 19. For error I used the above formula. It comes out about 1.48. Now my question is. Should I write the answer as 19±1.5 (rounding 1.48 to 2 significant figures) OR should I write it as 19±1. So in short, should the error have same number of significant figures as the mean value or should it have the same number of decimal places as...
Thread 'A cylinder connected to a hanging mass'
Let's declare that for the cylinder, mass = M = 10 kg Radius = R = 4 m For the wall and the floor, Friction coeff = ##\mu## = 0.5 For the hanging mass, mass = m = 11 kg First, we divide the force according to their respective plane (x and y thing, correct me if I'm wrong) and according to which, cylinder or the hanging mass, they're working on. Force on the hanging mass $$mg - T = ma$$ Force(Cylinder) on y $$N_f + f_w - Mg = 0$$ Force(Cylinder) on x $$T + f_f - N_w = Ma$$ There's also...
Back
Top