Why Do Some Kw/h Meters Reverse Direction with 415V Single Phase Loads?

  • Thread starter Thread starter cnf9115
  • Start date Start date
  • Tags Tags
    Phase
AI Thread Summary
When a single-phase 415/480 volt load is connected, one kWh meter may reverse direction while others operate normally, even with correct line and load connections. This reversal could be linked to the power factor correcting capacitor across the phases or an imbalance caused by the single-phase load. The discussion suggests that a detailed diagram of the connections is necessary to confirm proper polarity and identify any potential miswiring. Questions arise about whether the reversing meter's readings correspond to the other meter's readings in a negative manner, indicating a two wattmeter connection. The complexity of the situation highlights the need for further clarification and understanding of phasor notation and electrical principles.
cnf9115
Messages
2
Reaction score
0
When a single phase 415 / 480 volt load is connected, one Kw/h meter will turn in the right direction whilst the other will turn in the reverse direction. This is the case whether the load is a welder or flood light or inductive heater. Can anybody please explain the reason why?
 
Engineering news on Phys.org
Are the "Line" and "Load" connections the same, or if a current sensor is used, they are probably reversed. Otherwise you have provided very little info.
 
Hi Windadct, thanks for your reply. The situation is like this. We have a normal 3 phase installation with 3 single phase Kwh meters. All are connected correctly IE line and load tails are correctly oriented at the meter connections. The meters all turn in the correct direction when normal single phase or 3 phase loads are connected. However, when a single phase 415 volt load is connected (supplied by 2 of the 3 meters) one of the meters will stop and turn in reverse until that particular load is switched off at which time, the reversing meter will resume turning in the right direction. I was wondering if the cause might be due to the power factor correcting capacitor across the 2 phases perhaps. NB this also occurs with single phase 480volt loads where power is supplied by a single phase (centre tap) transformer where the output is 2 actives and one neutral.
I hope that this makes it a little clearer.
 
Hello Again - best bet will be to develop a detailed diagram of the connections, and visually confirm each connection and polarity. e.g. not how you think or believe it is connected, but how you know it is. I am thinking there is a connection on the wrong phase, etc.
 
cnf9115 said:
when a single phase 415 volt load is connected (supplied by 2 of the 3 meters) one of the meters will stop and turn in reverse
Does that reversing meter gives a reading which is the same as the reading of the other meter, though negative, over a set period of time?
 
Does that amount to a two wattmeter connection?

Is it possible that with unbalance due to single phase load, one meter legitimately turns backward? And true power is the sum of the two?

Anybody fresh on phasor notation ?

It's not clear to me whether you are describing a system with intermediate voltage taps.
"Meterman's Handbook" is the Bible on this subject - see
http://books.google.com/books?id=ZE...e&q=two wattmeter meterman's handbook&f=false
 
I'm hoping the OP answers my question here, so I can then finish the explanation.
 