Why do we use the 3phase and not the 4phase or other phase supply?

  • Thread starter Thread starter Faraz Murtaza
  • Start date Start date
  • Tags Tags
    Phase Supply
Click For Summary

Discussion Overview

The discussion centers on the reasons for the preference of three-phase electrical systems over four-phase or other multi-phase systems in generation and transmission. Participants explore various technical, historical, and economic factors influencing this choice.

Discussion Character

  • Technical explanation
  • Debate/contested

Main Points Raised

  • Some participants suggest that three-phase systems are preferred due to economic factors and historical decisions made by early pioneers like Tesla.
  • Others propose that the balanced load in three-phase systems eliminates the need for a neutral wire, making it efficient for AC transmission.
  • A participant mentions the Star-Delta transformation as a relevant concept in the context of three-phase systems.
  • Concerns are raised about the potential for two-phase systems to cause synchronous motors to run less smoothly compared to three-phase systems.
  • Technical details are provided regarding the power delivery in three-phase systems, including calculations involving line and phase voltages.
  • Confusion over terminology related to line voltage and phase voltage is noted, with clarifications provided on their relationships.

Areas of Agreement / Disagreement

Participants express various viewpoints on the reasons for using three-phase systems, with no consensus reached on a single definitive answer. The discussion remains unresolved regarding the advantages and implications of alternative phase systems.

Contextual Notes

Limitations include potential confusion over electrical terminology and the need for further clarification on the implications of different phase systems on motor performance and power delivery.

Faraz Murtaza
Messages
32
Reaction score
0
why do we use the 3phase and not the 4phase or other phase supply?

please answer...
 
Last edited by a moderator:
Engineering news on Phys.org


do you mean 3 phase instead of 4 wire systems, or do you mean 3 phase instead of more than 3 live wires ? If the first, no need for the neutral if load is balanced amongst the live phase conductors as in AC transmission, although 4 wire is common at the lower distribution voltages main lines that directly supply customers. Three phase has become the norm for AC transmission, due primarily to economics. And Tesla. Some research was done awhile ago on 6 phase systems during the EMF issues of health concerns, but nothing was ever implemented of significance.
 
Last edited:


I think its due to Star-Delta transformation.
Transmission using delta , 3 wire(no neutral) and users star formation
 


PhanthomJay said:
do you mean 3 phase instead of 4 wire systems, or do you mean 3 phase instead of more than 3 live wires ? If the first, no need for the neutral if load is balanced amongst the live phase conductors as in AC transmission, although 4 wire is common at the lower distribution voltages main lines that directly supply customers. Three phase has become the norm for AC transmission, due primarily to economics. And Tesla. Some research was done awhile ago on 6 phase systems during the EMF issues of health concerns, but nothing was ever implemented of significance.

thanx for your supportive answer bt i think you did not get my question..ok let me elaborate it further that my question was...why do we use the 3 phase supply like in generation, transmission etc,,and why these devices are not supplied 2phase or 1phase supply??
please elaborate!
 
Last edited by a moderator:


I think that the only answer to this is that Tesla decided to use three phase, and once the early infrastructure was laid down there was no point in changing to any other combination.
Why Tesla went for three phase I don't know but would guess that it's a compromise between fears that two phase power would cause synchronous motors to run less smoothly then three phase and the extra cost of cabling that would be needed by four phase.
As an after thought and I'm having real trouble visualising it, would a two phase motor run in the same direction every time you started it?
 


In a three phase AC system, the voltages between wires are time wise 120 degrees apart , and same with the current. With some vector algebra, the power delivered can be shown to be equal to (root 3)(V)(I) , where V is the voltage difference between any 2 phase conductors. For a 115 kV phase -to - phase 3 phase line, carrying 1000 amps in each conductor, this is about 200 MW of power assuming unity power factor and no line losses. Now with a single phase line (2 wire system with neutral return), you only get 115 MW out of it for the same current...it's economics...and other factors already mentioned.
 


PhanthomJay said:
In a three phase AC system, the voltages between wires are time wise 120 degrees apart , and same with the current. With some vector algebra, the power delivered can be shown to be equal to (root 3)(V)(I) , where V is the voltage difference between any 2 phase conductors. For a 115 kV phase -to - phase 3 phase line, carrying 1000 amps in each conductor, this is about 200 MW of power assuming unity power factor and no line losses. Now with a single phase line (2 wire system with neutral return), you only get 115 MW out of it for the same current...it's economics...and other factors already mentioned.

There are a couple of problems here by confusing V line and V phase (VL =VP/Root 3) in the first case V is VP in the second V is VL.

Power in a 3 phase system P= 3*VL*I (the 3 comes from the fact that that you have the same I on three conductors)

VL=VP/(root3) so P=(root3)*VP*I

BUT if you are taking power from a single phase P=VL*I
 


The terminology is confusing. For a three phase AC line, the voltage between any 2 phases, A to B, A to C, or B to C, is called the line voltage, V_ l, or what I refer to as the phase to phase voltage. The voltage between anyone phase and ground is called the phase voltage, V_p, or what I refer to as the phase to ground voltage, and where V_l = (root 3)V_p.
For a 3 phase 115 kV phase to phase line voltage, V_l = 115, V_p = 66, and Power = (root 3)(V_l)(I_l) or 3 (V_p)(I_l) if you wish, same result.
 


ok thanks phantomjay...
 

Similar threads

  • · Replies 9 ·
Replies
9
Views
3K
Replies
13
Views
4K
Replies
7
Views
3K
  • · Replies 19 ·
Replies
19
Views
4K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 17 ·
Replies
17
Views
4K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 54 ·
2
Replies
54
Views
10K
Replies
4
Views
2K