Why Mineral Insulated Heating Cables have power output limit?

Click For Summary

Discussion Overview

The discussion revolves around the limitations of mineral insulated heating cables, specifically focusing on their power output per foot and maximum operating voltages. Participants explore various factors influencing these limitations, including the properties of magnesium oxide (MgO) used as insulation, thermal conductivity, and the implications of temperature gradients on performance.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Conceptual clarification

Main Points Raised

  • Some participants suggest that the dielectric strength of MgO insulation is higher than the maximum operating voltage, questioning why the voltage limit is around 2 kV.
  • There is a discussion about the thermal conductivity of MgO, with one participant providing a value of 45–60 W/m·K.
  • Participants debate whether the melting temperature of MgO establishes an upper limit to the operating temperature, with some asserting that it does not due to MgO's high melting point (~2,800 °C).
  • One participant notes that the high melting point of MgO limits the temperature gradient that can be maintained across the insulating annulus.
  • There are inquiries about the purpose of the non-conducting solid insulator in the cables, with responses indicating it serves to electrically insulate the heating element from the outer metallic sheath.
  • Concerns are raised about the performance of MgO as an insulator if it melts, with participants noting that while it has a high melting point, it will fail as an insulator if melted.
  • One participant questions the significance of the change in electric resistivity of MgO with increasing temperature and its impact on maximum voltage and power output limits.
  • Another participant mentions that dielectric properties are measured under ideal conditions, which may not apply to real situations, potentially affecting the voltage limits.
  • Discussion includes the impact of higher temperatures on the lifetime of resistors or fuses, suggesting that this could influence operating temperature limits.
  • Concerns are raised about the environmental effects of hot cables, such as the risk of fire or damage to nearby materials.
  • Participants discuss the relationship between maximum operating voltage and the electrical insulation requirements, suggesting that the current commercial heating cables are limited to 2 kV due to the insulation properties of MgO in field conditions.
  • There is a mention of the role of capacitance in power transmission through coaxial cables, with some participants arguing it is not significant at standard power distribution frequencies.

Areas of Agreement / Disagreement

Participants express multiple competing views regarding the factors that limit the power output and maximum operating voltage of mineral insulated heating cables. There is no consensus on the primary reasons behind these limitations, with various hypotheses and technical arguments presented.

Contextual Notes

Participants highlight limitations such as the dependence on real-world conditions versus ideal measurements, the need for thermal conductivity alongside electrical resistivity in insulation, and the implications of temperature gradients on heat transfer rates.

amrmohammed
Messages
44
Reaction score
0
Hello

Why does Mineral Insulated heating cables have such limited power output per feet and maximum operating voltages?
I thought it has to do with the dielectric strength of the MgO, that is used as an insulation in the coaxial cable, but the dielectric strength for MgO is higher than the current voltage limit. The highest voltage limit I read about was around 2 KV and the dielectric strength of MgO is around 10-35 KV/mm. What happens if you supply power over the rated maximum?
 
Engineering news on Phys.org
What's thermal conductivity of MgO?
 
45–60 W/m·K (Wikipedia)
 
Does the melting temperature of MgO establish an upper limit to operating temperature?
 
No it doesn't, MgO has a very high melting point (~2,800 °C)
 
amrmohammed said:
No it doesn't
And, that limits the temperature gradient that can be maintained across the insulating annulus, does it not?
 
Bystander said:
that limits the temperature gradient that can be maintained across the insulating annulus

Would you please elaborate? how does high melting temperature of the MgO in the annulus be a limitation to the maximum temperature gradient?
 
What's the purpose of a non-conducting solid insulator in the cables?
 
To electrically insulate the heating element from the outer metallic sheath
 
  • #10
How well can it perform that function as a melt?
 
  • #11
it will fail, but it has a very high melting point
 
  • #12
amrmohammed said:
it will fail, but it has a very high melting point
It sets an absolute upper limit to the temperature gradient that can be maintained across the insulation. (The practical limit is much less due to increased electrical conductivity of MgO as temperature increases.)
What does that limit to the temperature gradient imply as far as rate of heat transfer (power)?
 
Last edited:
  • Like
Likes   Reactions: amrmohammed
  • #13
The limitation in temperature gradient should limit the rate of heat transfer, as additional power will increase the temperature of the heating wire and thus exceed the maximum temperature gradient to the surrounding. but does the change in the electric resistivity of MgO with increasing temperature that significant? most of the available heating cable have a maximum of only 600 V and MgO have a very high dielectric strength!
 
  • #14
Please refer to this pdf file. The resistivity of MgO do decrease with temperature but it is still very high.
resistiity.png


and in http://www.emersonindustrial.com/en-US/documentcenter/EGSElectricalGroup/products_documents/heating_cables/commercial_heating_cables/commercial_pipe_tracing/mi_comm_pipe_trace_cable/308-SA-001_Mineral_Insulated_heater_cable_lit.pdf , the resistivity of the heating wire is presented and it is very small that it will always be much less than the resistivity of MgO insulation (using the graph above) so I though there should be no worry from short circuit, however they set a maximum temperature of 350 C and maximum voltage of 600 V. What is wrong with my understanding of this data and graphs?
 
Last edited by a moderator:
  • #15
  • Like
Likes   Reactions: amrmohammed
  • #16
The lifetime of a resistor or fuse is reduced at higher temperatures.
For a resistive heating element, the cost of replacement following failure can be the factor that requires limits to the operating temperature.
 
  • #17
I can't find any mention here,m of the effect of having a hot cable on its environment. (Setting fire to floor joists and melting nearby PVC cabling etc.) Surely that must be relevant. Or is it there 'by implication' in the rest of the spec of the cable?
 
  • #19
Yeah. I guess the design of the heater would take that into account. If the cable gets red hot then it would be mounted safely, by design.
 
  • #20
Baluncore said:
The lifetime of a resistor or fuse is reduced at higher temperatures.

That will limit the operating temperature (different from temperature gradient across the insulator that @Bystander mentioned), how is that related to the limit on maximum operating voltage? I guess the voltage limit should be somehow related to the dielectric strength of the insulator or the electrical properties of one of heating cable's components.

sophiecentaur said:
If the cable gets red hot then it would be mounted safely

That is true and there is a maximum sheath temperature set and published by IEEE. However, in many applications this is not a concern (like underground pipes and downhole oil heating) and the heating cable still have the same limit on the operating voltage and power output.
 
  • #21
Power is transmitted through coaxial conducting cables that is insulated by a dielectric material, could capacitance play any rule?
 
  • #22
amrmohammed said:
Power is transmitted through coaxial conducting cables that is insulated by a dielectric material, could capacitance play any rule?
Capacitance only becomes a problem above kHz frequencies. It is not important at 50Hz or 60Hz power distribution frequencies. Parallel capacitance is probably an advantage at power frequencies as it will slightly improve the power factor of the normally inductive grid.

amrmohammed said:
That will limit the operating temperature (different from temperature gradient across the insulator that @Bystander mentioned), how is that related to the limit on maximum operating voltage? I guess the voltage limit should be somehow related to the dielectric strength of the insulator or the electrical properties of one of heating cable's components.
You seem confused.
The thread title is “Why Mineral Insulated Heating Cables have power output limit? ”
Maximum operating voltage determines electrical insulation requirements.
The durability requirement is determined by the maximum specified operating temperature of the inner conductor.

The mineral insulation needs to be both thermally conductive and electrically resistive.
 
  • Like
Likes   Reactions: amrmohammed
  • #23
Baluncore said:
Maximum operating voltage determines electrical insulation requirements.

So to sum up, current commercial heating cables handle a maximum of 2 kV, because the currently available insulation (MgO) can not insulate higher voltages in field conditions?
 
  • #24
... and conductors (heating elements) with high enough resistance to function as heating elements (10-100 W/m) at applied voltages greater than 2 kV are too fragile.
 
  • Like
Likes   Reactions: amrmohammed

Similar threads

  • · Replies 38 ·
2
Replies
38
Views
6K
  • · Replies 19 ·
Replies
19
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 27 ·
Replies
27
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 10 ·
Replies
10
Views
5K
Replies
4
Views
5K
  • · Replies 10 ·
Replies
10
Views
6K
  • · Replies 9 ·
Replies
9
Views
5K
  • · Replies 10 ·
Replies
10
Views
2K