Wiring functioning prior to fusing?

  • Thread starter Thread starter PhiowPhi
  • Start date Start date
  • Tags Tags
    Wiring
Click For Summary

Discussion Overview

The discussion revolves around the current-carrying capacity of 18AWG wire, specifically whether it can function normally at 70-75A continuously, given that its fuse current is rated at 82A. Participants explore the implications of wire resistance, insulation melting, and the potential for increased current capacity with cooling systems.

Discussion Character

  • Debate/contested
  • Technical explanation
  • Exploratory

Main Points Raised

  • Some participants question if 18AWG wire can handle 70-75A continuously, noting that it is rated for 82A but may melt at that threshold.
  • One participant cites a chart indicating that 18AWG wire is rated for only 7A, suggesting that a larger gauge, such as 4AWG, would be necessary for 75A.
  • Another participant shares an anecdote about an 18AWG cord used in a vacuum cleaner rated for 10A, discussing the temperature rise associated with higher currents and the concept of thermal runaway.
  • Concerns are raised about the construction of inexpensive cords, with one participant noting that the wire may not be continuous and could fail at the insulation's melting point rather than the wire's melting point.
  • Participants express apprehension about the safety of terminations in molded wall plugs, suggesting they may not support high currents effectively.

Areas of Agreement / Disagreement

Participants express differing views on the current capacity of 18AWG wire, with some asserting it can handle 70-75A and others arguing it is rated for much lower. The discussion remains unresolved, with multiple competing views present.

Contextual Notes

There are limitations regarding the assumptions made about wire ratings, insulation types, and the conditions under which ampacity is determined. The discussion does not resolve these assumptions or provide definitive answers regarding safety or performance.

PhiowPhi
Messages
203
Reaction score
8
I have a wire of a certain volume, the fuse current is rated at 82A(18AWG wire), can the wire still function normally at 70-75A continuously? I understand that at 82A the wire will melt, but can it still function normally at 75A? The resistance of the wire is about 0.042 ohms, just wanted to see if it can handle that amount of current, would the insulator melt?

Maybe provided with reasonable cooling or heat transfer system, we could make it beyond 82A maybe to 100A+?
 
Engineering news on Phys.org
PhiowPhi said:
I have a wire of a certain volume, the fuse current is rated at 82A(18AWG wire), can the wire still function normally at 70-75A continuously? I understand that at 82A the wire will melt, but can it still function normally at 75A? The resistance of the wire is about 0.042 ohms, just wanted to see if it can handle that amount of current, would the insulator melt?

Maybe provided with reasonable cooling or heat transfer system, we could make it beyond 82A maybe to 100A+?
What's the application? Can you provide a lot more information about this?
 
PhiowPhi said:
I have a wire of a certain volume, the fuse current is rated at 82A(18AWG wire), can the wire still function normally at 70-75A continuously? I understand that at 82A the wire will melt, but can it still function normally at 75A? The resistance of the wire is about 0.042 ohms, just wanted to see if it can handle that amount of current, would the insulator melt?

Maybe provided with reasonable cooling or heat transfer system, we could make it beyond 82A maybe to 100A+?

Whoa, my chart says that 18AWG wire is rated for 7 amps, not 75. To get 75 A, you need 4AWG or better.

The conditions for ampacity of a given gauge are:
Conductor ampacity based on copper conductors with 75°C or higher insulation in an ambient temperature of 30°C
 
  • Like
Likes   Reactions: berkeman
@ Mr Phi
Have you used a vacuum sweeper at home? MIne says it's 10 amps and the cord is 18 AWG and the cord gets warm to the touch when i vacuum the floor.
10 amps is the rating for #18 portable cord with 90 degC insulation, type SJOOW
http://www.awcwire.com/productspec.aspx?id=portable-cord-sjoow-cable
and the vacuum cleaner factory uses the smallest they can get away with .
Depending on price of copper, #18 90degC might be cheaper than #16 60degC .What would be the temperature rise at 75 amps ?
(75/10)2 X whatever is temperature rise at 10 amps?
Precise measurements by UnScientificWildA**Guess method indicate a modest 5degF rise at 10 amps,
so at 75 amps i'd expect a (75/10)2 X 5 = 187.5 degF rise.
And that'd raise the resistance of the copper by 0.004 per degC ,
and 187.5/1.8 X .004 = 75% more ohms,
further increasing power dissipated in the cord hence raising its temperature even more.
That's Thermal Runaway, where the positive feedback takes over, and it's how fuses work.

Probably your 80 amp melt current for #18 is for bare wire in air , not insulated and not in conduit. Did they give a time?

Tap into your everyday experiences when contemplating such musings. Learning is mostly discovering what you already know.

old jim
 
Last edited:
  • Like
Likes   Reactions: Merlin3189 and berkeman
jim hardy said:
Probably your 80 amp melt current for #18 is for bare wire in air , not insulated and not in conduit

You mean melting point for solid wire bare in air. Cheap stranded house wire is not braided or twisted, short strands are just laid into a channel of the insulator. So the wire fails at the insulator's melt temperature, not the metal's melt temperature. Buy an extension cord in the dollar store, then cut open the wire to see what I mean. It is shocking (no pun) to see how little metal they put in those cords, and if they show an AWG rating on the label, I doubt if it is accurate.
 
anorlunda said:
short strands are just laid into a channel of the insulator.

You mean they're not even continuous from end to end ? That's scary.
 
jim hardy said:
You mean they're not even continuous from end to end ? That's scary.
Agreed, that is scary. I haven't seen that myself, but I don't take apart inexpensive cords or wire. Yikes.
 
Worse yet is the termination in the molded wall plug. Talk about getting warm.
 
dlgoff said:
Worse yet is the termination in the molded wall plug. Talk about getting warm.
Yeah, no wall socket will support that current. Thread closed.

@PhiowPhi -- PM me the answers to my questions, and I'll re-open the thread...
 

Similar threads

  • · Replies 29 ·
Replies
29
Views
20K
  • · Replies 9 ·
Replies
9
Views
3K
Replies
3
Views
6K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 2 ·
Replies
2
Views
6K
  • · Replies 5 ·
Replies
5
Views
4K
Replies
5
Views
5K
  • · Replies 8 ·
Replies
8
Views
3K