- #1
fourthindiana
- 162
- 25
I noticed that the outdoor fan on my residential, split-system heat pump stopped working in mid-October. I don't know for sure exactly when my outdoor fan on my heat pump stopped working. It might be that my outdoor fan did not work for months before I noticed that the outdoor fan did not work in mid-October.
My outdoor fan motor on my heat pump is a PSC motor. My outdoor unit of my heat pump has a Dual Run Capacitor (DRC). My DRC is a 40/5 DRC. When I checked the capacitance on my DRC on my outdoor unit several days ago, the capacitance from common to fan was only 743 nanofarads, which is .743 microfarads. I replaced the old, defective DRC with a new 40/5 DRC. The capacitance on my new DRC from common to fan was 5.03 microfarads. When I put a new DRC in my outdoor unit, the outdoor fan worked for about 24 hours. Then, after about 24 hours, the outdoor fan stopped running in heat mode.
I Ohm'ed out the fan motor and found that the resistance from the start wire of the outdoor fan to the common wire of outdoor fan is 2.1 Ohms. Start wire of outdoor fan to run wire of outdoor fan reads OL (infinite resistance) on my multimeter. Run wire of outdoor fan to common wire of outdoor fan is also OL. This proves that the fan motor (or the fan motor's wires, anyway) is defective.
Furthermore, I used an amp clamp to check the amperage draw on the common wire of my outdoor fan motor. The Full Load Amps on the nameplate of my outdoor unit is .77 amps. This means that the LRA should be around 3.85 amps. When I first turned the setting on the thermostat from "Off" to "Heat Mode", the amperage stayed at zero amps for a few minutes. Then, after a few minutes, the amperage on the common wire of the outdoor fan motor went up to 2.7 amps for about a second. Then the amperage gradually dropped down to zero amps over the next 30 seconds or so. Then the amperage just stayed at zero amps for the next 5 minutes or so until I removed the amp clamp from the common wire.
I think that both the resistance readings I got on the C-S-R wires of the fan motor and the amperage draws (or non-existent amperage draws) on the common wire of the outdoor fan motor conclusively prove that the outdoor fan motor is defective.
From the information I have given, could my original, defective Dual Run Capacitor (that only had .743 microfarads) have caused the outdoor fan motor on my heat pump to go bad?
If so, how does a defective Dual Run Capacitor, with insufficient capacitance from common to fan, cause a fan motor to go bad?
My outdoor fan motor on my heat pump is a PSC motor. My outdoor unit of my heat pump has a Dual Run Capacitor (DRC). My DRC is a 40/5 DRC. When I checked the capacitance on my DRC on my outdoor unit several days ago, the capacitance from common to fan was only 743 nanofarads, which is .743 microfarads. I replaced the old, defective DRC with a new 40/5 DRC. The capacitance on my new DRC from common to fan was 5.03 microfarads. When I put a new DRC in my outdoor unit, the outdoor fan worked for about 24 hours. Then, after about 24 hours, the outdoor fan stopped running in heat mode.
I Ohm'ed out the fan motor and found that the resistance from the start wire of the outdoor fan to the common wire of outdoor fan is 2.1 Ohms. Start wire of outdoor fan to run wire of outdoor fan reads OL (infinite resistance) on my multimeter. Run wire of outdoor fan to common wire of outdoor fan is also OL. This proves that the fan motor (or the fan motor's wires, anyway) is defective.
Furthermore, I used an amp clamp to check the amperage draw on the common wire of my outdoor fan motor. The Full Load Amps on the nameplate of my outdoor unit is .77 amps. This means that the LRA should be around 3.85 amps. When I first turned the setting on the thermostat from "Off" to "Heat Mode", the amperage stayed at zero amps for a few minutes. Then, after a few minutes, the amperage on the common wire of the outdoor fan motor went up to 2.7 amps for about a second. Then the amperage gradually dropped down to zero amps over the next 30 seconds or so. Then the amperage just stayed at zero amps for the next 5 minutes or so until I removed the amp clamp from the common wire.
I think that both the resistance readings I got on the C-S-R wires of the fan motor and the amperage draws (or non-existent amperage draws) on the common wire of the outdoor fan motor conclusively prove that the outdoor fan motor is defective.
From the information I have given, could my original, defective Dual Run Capacitor (that only had .743 microfarads) have caused the outdoor fan motor on my heat pump to go bad?
If so, how does a defective Dual Run Capacitor, with insufficient capacitance from common to fan, cause a fan motor to go bad?