Power factor correction (capacitor in parallel with inductive load)

In summary, the conversation discusses the use of capacitors in parallel and series to compensate for inductive loads. While a parallel capacitor can be smaller and only needs to compensate for the fixed inductive current, a series capacitor would need to be larger and its value would have to change with load. The installation of a capacitor in parallel would result in the full supply voltage being available for the real load, while the voltage may not be equal to the source voltage due to the inherent inductance, resistance, and capacitance of the transmission line. The use of capacitors, as well as inductors, in series and parallel is also mentioned in relation to improving voltage regulation and managing reactive power. The conversation also includes a link for further information
  • #1
FionaZJ
16
0
Why we must install capacitor in parallel to inductive load? Why not install it in series?
 
Engineering news on Phys.org
  • #2
The real and reactive currents of a partially inductive load are not in series, they are in parallel. The real component of current is load dependent. The inductive component, or magnetising current is usually independent of load.
A parallel capacitor will operate at the supply voltage and needs to compensate most of the fixed inductive current. It can be quite a small capacitor.

If a series capacitor was used it would be necessary for the real current also to flow through the correction capacitor. It would need to be a big capacitor and the value would have to be changed with load.
 
  • Like
Likes anorlunda and cnh1995
  • #3
Is it capacitor will draw all the voltage source in parallel?
 
  • #4
FionaZJ said:
Is it capacitor will draw all the voltage source in parallel?
Voltages across the inductive load and the capacitor will be equal since they are in parallel. But the capacitor voltage may not be equal to the source voltage as there can be some resistance in between the source and the inductor.
 
  • #5
Oh.okay. All of you Thank you!
 
  • #6
I guess if you add capacitor in series to load, then you're introducing an additional 'current-dependent voltage drop' element across line.

V load = V source - V capacitor.

So if load changes, then load current changes, so the voltage drop across capacitor will also change as it depends in Load current times the Xc, so the voltage available for load will also change. Not sure we want that.
At low voltage motor torque will reduce, and bulbs will go dim.
 
  • #7
So if we install capacitor in parallel, there will be full voltage supplied available?
 
  • #8
Not really. The transmission line will have inherent inductance, resistance, and capacitance which depend on:
length of line
proximity to other conductors
whether ac or dc voltage

So voltage across load is source voltage minus the transmission line voltage drop.

Not sure if I am right with the below part:
Capacitors are put in series in lines to improve over all voltage regulation. This is done at source end. The series capacitor will nullify the line inductance to some extent so the line impedance reduces.

While at the generating end we have capacitors in parallel or tap changing transformers to keep voltage constant.

Likewise even inductors are installed in series and parallel. A series reactor is useful to limit short circuit current and starting current.
A shunt reactor is useful during light loads. At light loads the system is highly capacitive due to the C banks. This causes high voltage. So the shunt reactor absorbs this VAR.
 
  • Like
Likes cnh1995
  • #9
Too hard to understand[emoji28]
 
  • #11
FionaZJ said:
So if we install capacitor in parallel, there will be full voltage supplied available?
Yes. The inductive magnetising current will be stable when running. The power factor correction capacitor will have the full supply voltage across it so it will cancel most of the inductive component. The real load will have the full supply voltage across it.

jaus tail said:
Not really. The transmission line will have inherent inductance, resistance, and capacitance which depend on:
length of line
proximity to other conductors
whether ac or dc voltage

So voltage across load is source voltage minus the transmission line voltage drop.
I think jaus tail is writing about neutralisation of regional transmission lines while I am writing about neutralisation of local electric motors.
 
  • Like
Likes jaus tail

1. What is power factor correction?

Power factor correction is the process of improving the overall power factor of an electrical system. This is achieved by adding a capacitor in parallel with an inductive load, which helps to balance out the reactive power and increase the efficiency of the system.

2. Why is power factor correction important?

Power factor correction is important because it helps to reduce energy waste and improve the efficiency of an electrical system. A low power factor can result in higher energy bills and strain on the electrical grid, so correcting it can save money and reduce environmental impact.

3. How does a capacitor in parallel with an inductive load improve power factor?

When a capacitor is added in parallel with an inductive load, it creates a capacitive reactance that offsets the inductive reactance of the load. This helps to balance out the reactive power, resulting in a higher power factor and improved efficiency.

4. What types of loads benefit from power factor correction?

Any load that has a high inductive component, such as motors, transformers, and fluorescent lighting, can benefit from power factor correction. These types of loads can cause a low power factor and waste energy without correction.

5. How do I determine the correct size of a capacitor for power factor correction?

The correct size of a capacitor for power factor correction can be determined by calculating the reactive power of the load and the desired power factor. This calculation can be done using a power factor correction calculator or consulting with a qualified electrician.

Similar threads

  • Electrical Engineering
Replies
1
Views
1K
  • Electrical Engineering
Replies
16
Views
1K
  • Electrical Engineering
Replies
8
Views
1K
Replies
12
Views
2K
  • Electrical Engineering
Replies
2
Views
605
Replies
2
Views
951
Replies
28
Views
1K
Replies
8
Views
960
  • Electrical Engineering
Replies
8
Views
305
  • Electrical Engineering
Replies
3
Views
1K
Back
Top