Harmonics in polyphase power system

AI Thread Summary
Harmonics in polyphase power systems arise from the interaction of multiple phases, leading to the cancellation of certain harmonic currents, particularly triplen harmonics, in line currents. The absence of triplen harmonics in line currents is due to their in-phase nature, which results in cancellation when summed across phases. Phase voltages may also lack odd harmonics, as these are similarly canceled by the balanced system. However, while triplen harmonics do not appear in line currents, they can still exist in phase-to-neutral voltages, allowing them to flow if a neutral connection is present. Understanding these dynamics is crucial for effective power system design and maintenance to mitigate harmonic-related issues.
mnada
Messages
21
Reaction score
0
"Harmonics in polyphase power system"

Dear All,
I have a problem in understanding how the harmonic currents exist in a load with no corresponding harmonic voltages?
The following figures with questions under explain what I mean

02328.png


This understood figure no issues about.

02330.png


In above figure, 2 question arise::rolleyes:

How the line currents are missing the triplen harmonics
How the phase voltage is missing the other odd harmonics except the triplen

02333.png
In the above figure::rolleyes:

How is the phase voltage missing all the harmonics while it's present in current.
Correct me if I am wrong: we can say that because triplen harmonics are in phase they cancel each other in the line cuerrent

Thank you
 
Engineering news on Phys.org


Any suggestion?
 


Re fig2,
How the line currents are missing the triplen harmonics
3rd harmonics are in phase as you noted.

Therefore third harmonic voltage cannot be produced between phases of a wye machine.
In your fig2 write KVL between any two phases and observe 3rd harmonic in one phase cancels the 3rd harmonic from other phase.

Since there's no 3rd harmonic phase to phase voltage and your load is connected phase to phase, that harmonic has no voltage to drive it. So with nothing to push it, that current cannot flow. (assuming linear load).
Another way to think of it is - since third harmonic current is in phase, it'd be coming out of all 3 phases in synch. How would it get back to generator to satisfy KCL ? Kirchoff's Current Law shows it could only return through neutral which has a high impedance volteter in it, so no current flows there. It is blocked by absence of neutral connection.

But if you replace that voltmeter with an ammeter it will indicate substantial 3rd harmonic current because each phase of load is in parallel with a phase of generator and 3rd harmonic voltage DOES exist phase to neutral. It can return via a neutral connection if one exists, like it would with an ammeter there.
That's why you have to be careful connecting a small 3 phase transformer to a large three phase source - what's insignificant harmonic content to the source might be real significant to the poor little transformer.

How the phase voltage is missing the other odd harmonics except the triplen
Sorry - i don't see that indicated on your fig2.

---------------------

Re last figure, which is unnumbered:
How is the phase voltage missing all the harmonics while it's present in current.
That one's kinda sneaky.
Look at that delta source . The three phases comprise a series connected loop. Since 3rd harmonic voltages are all in phase, they do not add to zero as does the fundamental.
So what you have is a short circuited supply for 3rd harmonic. 3rd harmonic current will flow around that delta winding in amount E3rd/Zmachine and the vast majority of the 3rd harmonic voltage is dropped across the machine's internal Z.. So your 3rd harmonic basically all stays in the machine.
But i believe the 5th and 7th would appear in phase voltage.

Correct me if I am wrong: we can say that because triplen harmonics are in phase they cancel each other in the line current
Again - without a return path they can't come out all 3 wires at once so they're blocked. Only place they can flow is around a delta winding.
I think the point of the exercise is probably to demonstrate that a delta winding shorts out third harmonic voltage effectively removing it. It'll clean up a sinewave for you.

hope this response triggers a bettre one from a genuine power engineer. I'm a lowly instrument guy.
 


Thank you. That really helped me to clear some points
 
for your question. Harmonics in polyphase power systems can be a complex topic to understand, but I will do my best to provide a clear explanation.

First, let's define what harmonics are in this context. Harmonics are frequencies that are multiples of the fundamental frequency in a power system. In a polyphase power system, there are multiple phases of power, typically three, that are out of phase with each other. This creates a balanced system where the sum of all the currents and voltages is zero.

Now, to address your questions:

1. How the line currents are missing the triplen harmonics?
The line currents are missing triplen harmonics because they are canceled out by the other two phases. In a balanced system, the sum of all the currents is zero, so any triplen harmonics present in one phase will be canceled out by the other two phases.

2. How the phase voltage is missing the other odd harmonics except the triplen?
Similarly, the phase voltage is missing the other odd harmonics because they are also canceled out by the other two phases. This is due to the balanced nature of the system.

3. How is the phase voltage missing all the harmonics while it's present in current?
The phase voltage is not completely missing all harmonics, it is just missing certain harmonics. This is due to the fact that the harmonics present in the current are canceled out by the other phases, while the fundamental frequency remains unchanged.

4. We can say that because triplen harmonics are in phase they cancel each other in the line current.
Yes, that is correct. Triplen harmonics are in phase with each other and therefore, when they are summed with the currents from the other two phases, they cancel out.

I hope this helps to clarify the concept of harmonics in polyphase power systems. It is important to note that harmonics can still cause issues in power systems, even if they are canceled out in the line currents. This is because they can still affect the voltage levels and cause problems with equipment. Therefore, it is important to properly design and maintain power systems to minimize the impact of harmonics.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...

Similar threads

Replies
2
Views
3K
Replies
26
Views
3K
Replies
9
Views
2K
Replies
3
Views
2K
Replies
13
Views
8K
Replies
2
Views
2K
Replies
6
Views
3K
Back
Top