How Do You Calculate Transformer kVA Rating Based on Site Measurements?

AI Thread Summary
To calculate the kVA rating of a transformer based on site measurements, first note the current readings: Ir at 163A, Iy at 150A, and Ib at 147A. The line-to-line voltage is 415V, which is consistent with a three-phase system. The kVA can be calculated using the formula kVA = (√3 × Voltage × Current) / 1000, where the voltage is the line-to-line voltage. It's important to ensure that the transformer rating exceeds the calculated kVA to accommodate load variations. Accurate voltage readings are crucial, as discrepancies can affect the final kVA calculation.
engnr.in.trng
Messages
1
Reaction score
0
Hi,

I've just got into my electrical engineering course and I need some help with a question of mine here.

During a site visit, we were shown a main LT panel which has switchgears, ammeters and different kinds of relays and the distribution network from that panel. In the main LT panel I've noted down the current readings as Ir - 163A, Iy - 150A and Ib - 147A. The Line to Line voltage is 415 V at 50 Hz and Line to Neutral voltage is 230V at 50 Hz.

From the above details, how would I calculate the kVA rating of transformer? The primary side voltage of the transformer is 11 kV and the secondary side voltage is 415V and the frequency is 50 Hz.
 
Engineering news on Phys.org
Welcome.

You have recorded inconsistent voltages. The voltage between phases will be √3 = 1.732 times the neutral to phase.

World standards have moved to 230V and 400V for single phase and three phase respectively.
The 415V you report suggests distribution is still 240V.

The transformer rating will need to be greater than the KVA observed.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top