Why Does Higher Zp in ASHRAE 62.1-2007 Indicate Lower Ventilation Efficiency?

  • Thread starter Thread starter Great Smoky
  • Start date Start date
AI Thread Summary
Higher Zp values in ASHRAE 62.1-2007 indicate a greater percentage of outside air, yet they correlate with lower ventilation efficiency (Ev) as shown in table 6-3. This counterintuitive relationship arises because increased outside air often leads to overventilation in certain zones, requiring more outside air to maintain effective ventilation. Ventilation efficiency measures how well ventilation is delivered to occupants, not just the quantity. A system with lower efficiency necessitates more outside air to achieve the same effective ventilation. The most efficient systems are those where all zones require the same outside air fraction.
Great Smoky
Messages
8
Reaction score
0
There is an equation in this standard for a primary outdoor air fraction: Zp=Voz/Vpz (eqn 6-5) which is pretty much a percentage of outside air where Voz is the outside airflow and Vpz is the primary airflow.

But then it shows in table 6-3 in the same standard that the higher the Zp value, the lower the ventilation efficiency (Ev). I would guess that the higher Zp (percentage outside air), the higher efficiency it should be.

This is a big mystery for me. Am I seeing things or interpreting it wrong? Anybody who has experience with this standard and can help would be greatly appreciated.
 
Engineering news on Phys.org
I don't have a copy of this at home (I'll check tomorrow at work to verify...), but ventilation efficiency is the efficiency at which ventilation is delivered to the occupants, not the quantity delievered. So a system with a lower ventilation efficiency requires more outside air to achieve the same effective ventilation.
 
So I checked the standard and my answer was sort of correct, but incomplete:

Since outside air is mixed with return air at the unit, the only way to ensure a zone with an unusually high OA need gets what it needs is to increase the OA fraction of the unit. This results in some zones being overventilated. So the most efficient system is one where each zone needs the same OA fraction.
 
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...
I need some assistance with calculating hp requirements for moving a load. - The 4000lb load is resting on ball bearing rails so friction is effectively zero and will be covered by my added power contingencies. Load: 4000lbs Distance to travel: 10 meters. Time to Travel: 7.5 seconds Need to accelerate the load from a stop to a nominal speed then decelerate coming to a stop. My power delivery method will be a gearmotor driving a gear rack. - I suspect the pinion gear to be about 3-4in in...