The discussion focuses on determining the appropriate diameter for a pipe to maintain a flow rate of 4000 gpm with a pressure drop of 32 psi over a length of 65 feet. Participants express concerns about the high velocity of 46 ft/s, which is typically too high for standard piping systems. It is noted that tapping into the existing line may alter the overall system pressure, potentially lowering it below the expected 32 psi. Calculations for pressure drop through a 6" ID pipe at the specified flow rate are confirmed to be approximately correct, estimating a drop of around 27 psi. The importance of considering downstream effects and system changes is emphasized in the context of the proposed setup.
coolkid
Hi all,
Need help determining what size diameter for some pipe. I just want someone to check my calculations, hopefully they're okay. I attached a quick sketch of the set up.
Here are the knowns:
Qmin = 4000gpm
ΔP = 32psi
L = 65ft
e(roughness of commercial steel pipe) = 0.00015ft
water properties:
ν = 1.08x10-5 ft^2/s
ρ = 1.94 slug/ft^3
Is it safe to assume since the discharge is below the source we can ignore the height change it and just pretend its a horizontal pipe?
Take a look at my calculations in the excel sheet I attached. The first tab is an estimation for the diameter, the 2nd tab is sort of a recheck, estimating Flow given diameter.
Thanks!
Are you trying to size a pipe to drop the pressure 32 psi to maintain a flow rate of 4000 gpm?
46 ft/s pipe velocity is, generally speaking, way too high for a typical piping system. Rarely do you see anyone putting 4000 gpm through a 6" pipe, I can't really think of any reason to do so.
No, the pressure where we will be taping an existing pipe reads 32psi. The new pipe will be discharging into an open container, 0psi. The reason we are adding this water pipe is because there is a container that is constantly too low, so I am proposing we need approximately 4000gpm of water from this new pipe supplying the tank.
What's downstream of this? Tapping this line will change the whole system.
This is a good point. With 4000 GPM coming out through this pipe, the pressure you have available may be lower than the 32 psi you have now.
Regardless, I checked your pressure drop calculations and they look about right. I get ~ 27 psi pressure drop through a 6" ID pipe at 4000 GPM, so I think your calculations should be pretty close.
I need some assistance with calculating hp requirements for moving a load. - The 4000lb load is resting on ball bearing rails so friction is effectively zero and will be covered by my added power contingencies. Load: 4000lbs Distance to travel: 10 meters. Time to Travel: 7.5 seconds Need to accelerate the load from a stop to a nominal speed then decelerate coming to a stop. My power delivery method will be a gearmotor driving a gear rack. - I suspect the pinion gear to be about 3-4in in...
How did you find PF?: Via Google search Hi, I have a vessel I 3D printed to investigate single bubble rise. The vessel has a 4 mm gap separated by acrylic panels. This is essentially my viewing chamber where I can record the bubble motion. The vessel is open to atmosphere. The bubble generation mechanism is composed of a syringe pump and glass capillary tube (Internal Diameter of 0.45 mm). I connect a 1/4” air line hose from the syringe to the capillary The bubble is formed at the tip...
Thread 'Calculate minimum RPM to self-balance a CMG on two legs'
Here is a photo of a rough drawing of my apparatus that I have built many times and works. I would like to have a formula to give me the RPM necessary for the gyroscope to balance itself on the two legs (screws). I asked Claude to give me a formula and it gave me the following: Let me calculate the required RPM foreffective stabilization. I'll use the principles of gyroscopicprecession and the moment of inertia. First, let's calculate the keyparameters: 1. Moment of inertia of...