Induction Motor Slip decrease with frequency decrease for same load.

AI Thread Summary
The slip in an induction motor decreases with frequency under the same load due to the relationship between frequency and rotor speed, where lower frequency results in lower slip. At higher frequencies, no-load losses such as iron losses, ventilation, and bearing friction are more pronounced, contributing to higher slip. Windage losses are influenced by the square of the speed, meaning that as frequency decreases, these losses also decrease. The no-load current, primarily reactive, is about 30% of the rated current, and copper losses can rise with increased no-load conditions. Overall, with less power required to maintain rotor rotation at lower frequencies, the slip decreases even if the torque remains constant.
Physicist3
Messages
103
Reaction score
0
Hi,

Does anyone know or could help me understand the reasoning for the amount of slip within an induction motor decreasing with frequency under the same load conditions? I.e. For no external load, the slip is higher at 50Hz than at 20Hz etc? Thanks
 
Engineering news on Phys.org
What about internal load, ie bearing friction and windage loss?

Is windage proportional to speed2 or to speed3 ?
 
“No-load” it does not mean “no load at all”. There are no-load losses –iron losses, ventilation and friction-bearing losses and copper losses. The no-load current-mainly reactive-is about 30% of rated and copper [winding] losses could be elevated. As jim hardy already said, ventilation and friction are proportional with square of rpm, so less frequency less rpm [rpm=60*freq/p where p= no.of pole pairs] less slip. The iron losses decrease with the frequency and so the no-load current and in turn no-load copper losses. The mechanical power requested in order to maintain the rotor in rotation will decrease even if the torque remains constant P=T*(2*PI()*Freq:
P=T\omega=2\pi_fT
Less power less slip.
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...