3 Phase Systems Theory and Procedure -- Determining Average Power

Click For Summary
SUMMARY

This discussion focuses on the analysis of average power in three-phase systems, specifically comparing delta and wye configurations. The first scenario involves delta-connected impedances of 60 + j30 Ω, while the second scenario uses wye-connected impedances of 40 + j10 Ω. The procedures for calculating average power differ based on the configuration and the given voltages, with specific formulas such as S = 3|Ia|^2(Zy) for delta and S = (3 * Vp^2) / (Zp complex conjugate) for wye. Understanding the distinction between line and phase voltages is crucial for accurate calculations.

PREREQUISITES
  • Understanding of three-phase power systems
  • Familiarity with complex impedance (Z) and its representation
  • Knowledge of delta and wye configurations in electrical circuits
  • Proficiency in using phasor notation for voltage and current
NEXT STEPS
  • Study the conversion between delta and wye configurations in detail
  • Learn about calculating average power in three-phase systems using complex power (S)
  • Explore the implications of line versus phase voltage in circuit analysis
  • Investigate the use of complex conjugates in power calculations
USEFUL FOR

Electrical engineering students, circuit designers, and professionals involved in power system analysis will benefit from this discussion, particularly those focusing on three-phase systems and power calculations.

OmniNewton
Messages
105
Reaction score
5

Homework Statement


Consider the 3 following Scenarios:
1.
upload_2016-12-7_17-12-31.png


2.
upload_2016-12-7_17-13-5.png

rms value of line voltage is 208 V

Three equal impedances, 60 +j30 W each, are delta-connected to a 230-V rms, three-phase circuit. Another three equal impedances, 40 +j10 W are wye-connected across the same circuit at the same points.

Homework Equations


S = 3|Ia|^2(Zy)
P = Real Component (S)

The Attempt at a Solution


How come when analyzing circuit one the procedure for determining the average power is to
1. find the line current Ia which is simply 110<0 divided by the impedance (Z(delta)/3 + 2)
2. calculate S = 3|Ia|^2(Zy) where Zy =(Z(delta)/3 + 2)
3. take the real component of S and that is your average power.

But when analyzing circuit 2 the procedure is:
1. Convert Van = 208 to Vp = 208/ root(3)
2. compute S by using S = (3 * Vp^2)/ (Zpcomplex conjugate)
3. take the real component of S and that is your average power.

And when analyzing circuit 3 the procedure is:
1. Find the line current
2. compute S by using S = (3 * Vs * (complex conjugate of line current)
3. take the real component of S and that is your average power.

Essentially I am kind of confused about what this Vp, Zp are that is used in the second consideration. Also why for every one of these scenarios the procedure for getting average power is different and the previous methods do not work. All of these examples seem the exact same is what really confuses me. What makes these 3 analyses different? How do I know what procedure to follow? I am doing self study so any help that can be provided is greatly appreciated.

Thank you in advanced!
 
Last edited:
Physics news on Phys.org
OmniNewton said:
How come when analyzing circuit one the procedure for determining the average power is to
1. find the line current Ia which is simply 110<0 divided by the impedance (Z(delta)/3 + 2)
2. calculate S = 3|Ia|^2(Zy) where Zy =(Z(delta)/3 + 2)
3. take the real component of S and that is your average power.
In this method, they have first converted the delta impedance into its star equivalent impedance and then Zstar=Zdelta/3 is used. Then of course the 2Ω line resistances come in series with the load impedances in the respective phases, so you see the term Z/3+2 ohm in the equation.
OmniNewton said:
Convert Van = 208 to Vp = 208/ root(3)
Van=Vphase and in star, Vph=Vline/√3. Are you sure the problem says Van=208 V?
OmniNewton said:
But when analyzing circuit 2 the procedure is:
1. Convert Van = 208 to Vp = 208/ root(3)
2. compute S by using S = (3 * Vp^2)/ (Zpcomplex conjugate)
3. take the real component of S and that is your average power.
You can use the procedure in circuit 1 for this circuit too. This is already in star configuration, so you need not divide the load impedance by 3 as you did for circuit 1. But here, you do not have any line impedance and hence, you do not have a "voltage-divider" in the line. So, instead of calculating the line current like in circuit 1, you can directly use the given voltage to find the power.
OmniNewton said:
And when analyzing circuit 3 the procedure is:
1. Find the line current
2. compute S by using S = (3 * Vs * (complex conjugate of line current)
3. take the real component of S and that is your average power.
This is the "general" procedure and can be applied to any balanced three phase network.
 
Last edited:
  • Like
Likes   Reactions: OmniNewton
Oh I see thank you very kindly for taking the time to explain this. Yes problem 2 does say that the line voltage is that value.
 
Last edited:
OmniNewton said:
Yes problem 2 does say that the line voltage is that value.
That means Vab=208V, not Van as you have written.Van=208/root3 V.
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
Replies
2
Views
4K
  • · Replies 2 ·
Replies
2
Views
6K
Replies
3
Views
3K
  • · Replies 11 ·
Replies
11
Views
2K
  • · Replies 5 ·
Replies
5
Views
8K
Replies
11
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K