50Hz HV Transmission line question

Click For Summary
SUMMARY

This discussion focuses on calculating the absorbed power in a 50 Hz high-voltage transmission line using complex ABCD parameters. The user provided specific values from Table C, including A1=0.8698, A2=0.03542, B1=47.94Ω, B2=180.8Ω, C1=0 S, C2=0.001349 S, D1=0.8698, and D2=0.03542. The user calculated the sending-end voltage (Vs) and current (Is) and derived the absorbed power (P) as approximately 378,000 watts. The discussion emphasizes the importance of using the complex conjugate of the current when calculating power.

PREREQUISITES
  • Understanding of complex power calculations in electrical engineering
  • Familiarity with ABCD parameters for transmission lines
  • Knowledge of reactive power and power factor concepts
  • Proficiency in using complex numbers for electrical analysis
NEXT STEPS
  • Study the application of ABCD parameters in different transmission line configurations
  • Learn about the significance of reactive power and its impact on power systems
  • Explore methods for improving power factor in electrical systems
  • Investigate advanced techniques for power calculations using phasor analysis
USEFUL FOR

Electrical engineers, power system analysts, and students studying transmission line theory will benefit from this discussion, particularly those interested in complex power calculations and transmission line performance analysis.

David J
Gold Member
Messages
140
Reaction score
15

Homework Statement


[/B]
This question was raised on the 11th January 2015 but that thread appears to be no longer active now. There are 2 parts to the question (a) and (b). Initially I am only trying to work on (a)

Figure shows a 50 Hz, high-voltage, transmission line. The relationships between the sending and receiving end voltages and currents are given by the complex ABCD equations:

mimetex.gif


mimetex.gif


where 'S' stands for sending-end and 'R' stands for receiving-end

(a) Given the parameter values in TABLE C and an open-circuit received voltage measured as 88.9 kV, calculate the values of
mimetex.gif
and
mimetex.gif
and hence the power
mimetex.gif
absorbed from the supply by the transmission line on open circuit.

The Table C values are :-

##A_1=0.8698##
##A_2=0.03542##
##B_1=47.94\Omega##
##B_2=180.8\Omega##
##C_1=0 S##
##C_2=0.001349 S##
##D_1=0.8698##
##D_2=0.03542##

Homework Equations


[/B]
##V_s=V_R\left(A_1+jA_2\right)+I_R\left(B_1+jB_2\right)##

##I_s=V_R\left(C_1+jC_2\right)+I_R\left(D_1+jD_2\right)##

The Attempt at a Solution


[/B]
##V_s=V_R\left(A_1+jA_2\right)+I_R\left(B_1+jB_2\right)##

The receiving end is open circuit so there cannot be any current flow so ##I_R=0##

##V_s=88900\left(0.8698+j0.03542\right)+0\left(47.94\Omega+j180.8\Omega\right)##

##V_s=\left(77325.22+j3148.84\right)+0##

So ##V_S=77325.22+j3148.84## or ##77389.31\angle2.33^0##

##I_s=V_R\left(C_1+jC_2\right)+I_R\left(D_1+jD_2\right)##

##I_s=88900\left(0+j0.001349\right)+0\left(0.8698+j0.03542\right)##

So ##I_s=j119.93##

To find the absorbed power

##P_{SO}=V_SI_S##

So ##\left(77325.22+j3148.84\right)\left(j119.93\right)##

So ##P_{SO}=-377640.38+j9273613.63##

In the post from 2015 this same calculation was made and I have shown it below

Now the power should be calculated by

P=Real{VsIs*}

P=Real{(77325.22+j3148.84)(j119.93)}

P=377565w

In the earlier post answer they only included the real value (P=377565w) which I suppose is ok so my calculation, in that case, is pretty close apart from the fact that my value is negative.
The question is asking for a value of power in watts so do I just assume that even though the calculation appears negative it is actually positive ??

My question is why is my value different ?? Have I made a mistake somewhere with this calculation ??

Appreciated as always


 
Physics news on Phys.org
Remember that when calculating power using complex values for voltage and current that you should use the complex conjugate of the current :wink:
 
ok so the complex value of current is ##0+j119.93## so the complex conjugate of ##0+j119.93## would be ##-j119.93## ?

In that case

##\left(77325.22+j3148.84\right)\left(j119.93\right)##

becomes

##\left(77325.22+j3148.84\right)\left(-j119.93\right)##

which gives me ##377640.38 + (-j9273613.63)##

am I heading in the right direction with the above ? It makes more sense but I am still not getting the same values as others got and also, if this is correct then what do I do with the imaginary part, ##-j9273613.63## ?
 
David J said:
ok so the complex value of current is ##0+j119.93## so the complex conjugate of ##0+j119.93## would be ##-j119.93## ?
Yes.
In that case

##\left(77325.22+j3148.84\right)\left(j119.93\right)##

becomes

##\left(77325.22+j3148.84\right)\left(-j119.93\right)##

which gives me ##377640.38 + (-j9273613.63)##

am I heading in the right direction with the above ? It makes more sense but I am still not getting the same values as others got and also, if this is correct then what do I do with the imaginary part, ##-j9273613.63## ?
Your result looks okay to me. Given the original three significant figure of the received voltage you should be good with three figures for the power. I'd attribute any differences to rounding/truncation of intermediate values. If you can supply a link to the original thread I can take a look to see what happened there.

The imaginary part of the power represents reactive power. While the power supply has to provide this power to its load, the load cannot convert it to useful work (only real power does work). Power companies don't like high reactive power components because it represents wasted "effort" to supply it for no benefit to the customer (or themselves). The associated concept is "power factor" which represents how much a given load skews the phase of the current waveform from the voltage waveform. You don't have to do anything with this component of the power in the context of the current problem.
 
Good Morning and thanks for the info. I worked out a final answer of 378000 watts or 378KW

The initial post I was looking at can be reached via the link below. It was created on the 11th January 2015. I think it may actually still be active but there are no recent updates to any of the questions

https://www.physicsforums.com/threads/50-hz-high-voltage-transmission-line.791633/

Thanks again for your help with this
 