Could 9th Harmonic Be Causing Noise on Local Telephone Company's System?

  • Thread starter Thread starter WFO
  • Start date Start date
  • Tags Tags
    Bell Harmonic
AI Thread Summary
A local telephone company has reported noise issues on their system, linked to a significant 9th harmonic found on the power line. The rural utility has minimal industrial load, with the only notable equipment being a 1200 Hp gas line pump, which does not seem to be the source of the harmonic. The discussion suggests that the noise could be influenced by nearby pipelines and cathodic protection systems. Filters are available to mitigate the issue, and the conversation highlights the importance of proper grounding and potential use of optical isolation equipment. Addressing these factors may help resolve the noise problem affecting the telephone system.
WFO
Messages
26
Reaction score
0
We have a local telephone company complaining to our utility that they have noise on their system. We have investigated and found a fairly significant 9th harmonic on the power line. This seems to play havoc with phone systems.

What is a likely cause of a 9th harmonic? We are a rural utility with little industrial load. The area in question, however, has a lot of pipelines and cathodic protection.
I understand there are filters readily available. Where are they to be found and how much are they likely to cost?
 
Engineering news on Phys.org
What is a likely cause of a 9th harmonic? We are a rural utility with little industrial load.
What types of industrial load do you have. I would think it's coming from some type of equipment.
I understand there are filters readily available. Where are they to be found and how much are they likely to cost?
http://www.nepsi.com/pmfilt.htm"
 
Last edited by a moderator:
The only industrial load is a 1200 Hp gas line pump, which does not appear to be the culprit (i.e., the harmonic still exists when the pump is down). The rest of the area is rural load.
The link was good, but I was looking for something the phone company could put on their equipment.
 
If you are very rural, the power company may have installed a line conditioner (step-up transformer) to combat voltage drop over long runs. There is one 1/10th of a mile from me. The power company had been trying to serve this entire road with a single-phase hot line and a ground, but the boom in housing out here made that a problem. I don't know if such equipment could induce such a harmonic, but that would be place to start.
 
Is the telephone equipment in a substation? You might to be able to use some type of optical isolation equipment but you are going to have to share a common ground. If the equipment is in a substation, have you looked at how well you're grounding?
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...