The discussion revolves around AC circuit analysis involving a complex voltage applied to an inductive coil. The voltage expression is clarified, suggesting the first term should have a fundamental frequency rather than a multiple, leading to three distinct impedances for each frequency component. The calculations for instantaneous current, RMS voltage, RMS current, and power dissipated are detailed, with results indicating a total power dissipation of approximately 242 W. The importance of using superposition for analyzing multiple frequencies in the circuit is emphasized. Overall, the thread provides a comprehensive solution to the problem presented.
otester
Was wondering if anyone can confirm that I am on the right track or not?
I'm not sure whether Irms is meant to be a complex number not :/
Thanks in advance,
otester
A complex voltage v(t)=60sin(3wt)+15sin(3wt)+10sin(5wt) volts is applied to a coil of inductance 5mH and resistance 6(ohms). Determine, for a fudamental frequency of 100Hz, (a) an expression to represent the instantaneous value of current, (b) the rms voltage, (c) the rms current, (d) the power dissipated.
XL = 2(pie)fL
Impedance (Z) = R + jXL
RMS current (Irms) = Vrms/Z
w = (omega)
Power dissipated=(Irms)x(Vrms)
(a) XL = 2(pie)100x(5x10^-3) = 31.42(ohms)
Z = 6+j31.42
Irms = ( 60sin(3wt)+15sin(3wt)+10sin(5wt) ) / ( 6+j31.42 )
(b) Vrms = sqrt( (60^2+15^2+10^2)/2 ) = 44.3x0.707 = 31.32V
(c) Irms = 31.32 / ( 6+j31.42 ) = 5.22+j0.997
(In polar form: 5.31 @ 10.81 (degrees))
(d) Power dissipated = (31.32)x(5.31 @ 10.81) = 36.63 @ 10.81
A complete solution is offered.
I suspect that the first term of the given instantaneous voltage expression was meant to have an angular frequency of ω, not 3ω like the second term. Otherwise the two terms could simple by combined into a single term of 75 V magnitude (although this could be an intended trick for the student to catch). I will take the voltage expression to be:
v(t) = 60sin(ωt)+15sin(3ωt)+10sin(5ωt) volts
We are dealing with three frequencies and the circuit will exhibit three distinct impedances, one for each frequency component. We will use the superposition principle and deal with them separately.
##Z_1 = 6 + j 2\pi (f~L) = 6 + j \pi~Ω##
##Z_3 = 6 + j 2\pi (3f~L) = 6 + j3\pi ~Ω##
##Z_5 = 6 + j 2\pi (5f~L) = 6 + j5\pi~Ω##
Part (a) An expression for the instantaneous peak current
We divide each component of the peak voltage equation by the corresponding circuit impedance pertaining to its frequency. The results will be complex values. The magnitude of each result is the magnitude of the current term, while its phase angle is incorporated into the sin function of the time domain expression:
1) ##\frac{60}{6+j \pi} = 8.859~∠~-27.64°~~Amps##
2) ##\frac{15}{6 + j 2\pi} = 1.727~ ∠~-46.32°~~Amps##
3) ##\frac{10}{6 + j 5\pi} = 0.595~ ∠~-69.10°~~Amps##
##i(t) = 8.859sin(ωt - 27.64°) + 1.727sin(3ωt - 46.32°) + 0.595sin(5ωt - 69.10°)~~Amps##
Part (b) Determine the RMS voltage
The RMS values of the separate frequency components add in quadrature. So:
## V_{rms} = \sqrt{\left(\frac{60}{\sqrt{2}}\right)^2 + \left(\frac{15}{\sqrt{2}}\right)^2 + \left(\frac{10}{\sqrt{2}}\right)^2} = \sqrt{\frac{60^2 + 15^2 + 10^2}{2}} = 44.3~V##
Part (c) Determine the RMS current
Using the terms of the instantaneous peak current expression from part (a);
##I_{rms} = \sqrt{\frac{(8.859)^2 + (1.727)^2 + (0.595)^2}{2}} = 6.35~A##
Part(d) Determine the power dissipated
We'll sum the power dissipated at each frequency.
If V is an RMS voltage and I an RMS current and Φ the phase angle between current and voltage then the power is given by P = V*I cos(Φ). But if V and I are peak values, the √2 conversions to RMS of the voltage and current multiply, and the power becomes ½ V*I cos(Φ). We have all the peak voltage terms from the given information, and the peak currents and phases from part (a). So:
P = \frac{1}{2} [~~(60)(8.859) cos(-27.64°)\\
~~~~~~~~~~+ (15)(1.727) cos(-46.32°)\\
~~~~~~~~~~+ (10)(0.595) cos(-69.10°)~~] \\
~~= 241.9~W
So 242 W to three figures.
Likes gracy
@gneill you wrote a huge /Solution answer.Thank you so much!:smile:You are an awesome helper.
Thread 'A bead-mass oscillatory system problem'
I can't figure out how to find the velocity of the particle at 37 degrees. Basically the bead moves with velocity towards right let's call it v1. The particle moves with some velocity v2. In frame of the bead, the particle is performing circular motion. So v of particle wrt bead would be perpendicular to the string. But how would I find the velocity of particle in ground frame? I tried using vectors to figure it out and the angle is coming out to be extremely long. One equation is by work...