Advise on Drawing: Get Expert Opinion

  • Thread starter Thread starter ismat143
  • Start date Start date
  • Tags Tags
    Advise Drawing
Click For Summary

Discussion Overview

The discussion revolves around seeking expert advice on a drawing related to motor protection, specifically addressing overload and short circuit conditions. The scope includes technical explanations regarding motor protection devices and their configurations.

Discussion Character

  • Technical explanation

Main Points Raised

  • One participant describes overload as a condition where there is too much load on the motor, noting that overload relays are typically configured to handle this situation for a specific duration, such as 150% of full load for 60 seconds.
  • Another participant explains that a short circuit is a fault condition, with miniature circuit breakers (MCBs) designed to protect against these faults by tripping at a much faster rate, typically between 0.1 to 0.5 seconds after detecting the current.
  • It is mentioned that overload and short circuit protection devices serve different purposes in motor protection.
  • A suggestion is made to Google "Coordinated Motor Protection" for additional helpful information.

Areas of Agreement / Disagreement

Participants appear to agree on the definitions and functions of overload and short circuit protection, but the discussion does not explore any competing views or unresolved issues.

Contextual Notes

No limitations or unresolved mathematical steps are noted in the discussion.

Who May Find This Useful

Individuals interested in motor protection systems, electrical engineering, or related technical fields may find this discussion useful.

ismat143
Messages
10
Reaction score
0
Please See the drawing and Advise...
 

Attachments

  • Overload relay.jpg
    Overload relay.jpg
    33.6 KB · Views: 449
Engineering news on Phys.org
Overload - is just that - too much load on the motor, this is typically a long time ( relative to Short circuit issues) the OL Relay is configured for this case,, e.g. 150% of full load for 60 Seconds - etc.

A short circuit - is a fault, and the MCB is set up to protect for these cases, for example 5 to 10 x the Full load current, and this typically will trip in short ( 0.1 to 0.5 Sec after the Current is detected) or Instantaneous (as soon as the current is detected) -

The two device are protection for different types of problems.

Google Coordinated Motor Protection - that will probably be helpful.
 
Thanks
 
Thread locked.

ismat143 -- please check your PMs.
 

Similar threads

  • · Replies 15 ·
Replies
15
Views
2K
Replies
2
Views
1K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 54 ·
2
Replies
54
Views
10K
  • · Replies 4 ·
Replies
4
Views
1K
  • · Replies 7 ·
Replies
7
Views
2K
Replies
29
Views
2K
  • · Replies 26 ·
Replies
26
Views
5K
  • · Replies 26 ·
Replies
26
Views
5K
  • · Replies 6 ·
Replies
6
Views
2K