The discussion focuses on the differences between overload and short circuit protection in motor systems. Overload conditions occur when the motor experiences excessive load, typically triggering an overload relay after a set duration, such as 60 seconds at 150% of full load. In contrast, short circuits are immediate faults that activate a miniature circuit breaker (MCB) designed to trip quickly, usually within 0.1 to 0.5 seconds, at 5 to 10 times the full load current. Both devices serve distinct protective functions for electrical systems. The thread concludes with a suggestion to research "Coordinated Motor Protection" for further understanding.
ismat143
Messages
10
Reaction score
0
Please See the drawing and Advise...
 

Attachments

  • Overload relay.jpg
    Overload relay.jpg
    33.6 KB · Views: 430
Engineering news on Phys.org
Overload - is just that - too much load on the motor, this is typically a long time ( relative to Short circuit issues) the OL Relay is configured for this case,, e.g. 150% of full load for 60 Seconds - etc.

A short circuit - is a fault, and the MCB is set up to protect for these cases, for example 5 to 10 x the Full load current, and this typically will trip in short ( 0.1 to 0.5 Sec after the Current is detected) or Instantaneous (as soon as the current is detected) -

The two device are protection for different types of problems.

Google Coordinated Motor Protection - that will probably be helpful.
 
Thanks
 
Thread locked.

ismat143 -- please check your PMs.
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...
Back
Top