The discussion focuses on testing an Air Handling Unit (AHU) that requires a 30-degree temperature increase without exceeding a 500W energy input, while currently using 384W for four fans. Participants seek to calculate the temperature rise from the fans' energy input, accepting that all energy becomes heat in this sealed system. They also inquire about the necessary heater size if the fans alone do not achieve the desired temperature increase. The formula for calculating the temperature rise is confirmed as air volume multiplied by specific heat and power, leading to a significant temperature rise when applied correctly. Clarification on the calculations and potential heater requirements is essential for meeting testing criteria.
JaredJames
Messages
2,818
Reaction score
22
We are testing an Air Handling Unit, we need to raise the internal temperature by 30 degrees to pass the test, but cannot exceed an energy input of 500W.

It is a completely sealed unit.

We have four fans constantly running, consuming 384W. Firstly, how can I work out what temperature they will raise the unit to? The fan manufacturer says that all energy input becomes heat (due to it being a closed system, but please let's not debate this, just accept it for the purpose of this question and use the full 384W).

Secondly (if part 1 doesn't raise the temperature by 30 degrees), what size heater would we need to achieve the increase?

Box Dimensions: 1.2x1.2x3.0m
Fan Input: 384W
Must not exceed: 500W (but I would like some answers even if they do exceed it to show me what we would need to do to achieve the required temperature increase)


Also, is there a way to work out how many Watts are required to raise the temperature of air by 1 degree celsius in one hour?
 
Engineering news on Phys.org
jarednjames said:
The fan manufacturer says that all energy input becomes heat (due to it being a closed system, but please let's not debate this, just accept it for the purpose of this question and use the full 384W).
Nothing to debate - it's true!
Also, is there a way to work out how many Watts are required to raise the temperature of air by 1 degree celsius in one hour?
Air volume times specific heat times power = temperature rise.
 
russ_watters said:
Nothing to debate - it's true!

I know it's true, but I put that because with someone in work who didn't understand it I had to spend an hour explaining the concept to him and didn't fancy having to go through the same thing again.

russ_watters said:
Air volume times specific heat times power = temperature rise.

Thank you for this.
 
Hi, that gives me 4.23cubic metres of air, specific heat of 1.005kg/kg K and a power of 384W. Which is over 1600 when multiplied together, which is one hell of a temperature rise.

Is the formula correct or am I making a mistake somewhere?
 
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...