The discussion focuses on the installation of the Startco Earth Detection SE 704 system for a 4160V, 1900 HP motor, specifically addressing nuisance tripping issues during motor startup. Participants inquire about the KVA code for the motor and whether the starting current is within the specifications of the Startco current transformers (CTs). The importance of considering the wye connection and third harmonic currents returning through the neutral is highlighted. Additionally, examining the CT output with an oscilloscope during startup is suggested to diagnose potential issues. The conversation emphasizes the need for careful analysis of motor windings' capacitance to earth and the CT's performance.
dorymill
Messages
1
Reaction score
0
Anyone ever install SE 704 Earth Detection (ground fault system)?
4160V 3 phase
1900 HP motor
detection level 100 Ma
resistance grounded supply max fault current 1 amp.

Nuisance tripping when starting the motor.
 
Engineering news on Phys.org
what's KVA code on motor?

is starting current within spec of that Startco gizmo's CTs?

Wye connection? remember third harmonic all returns through neutral...CT needs to wrap it too.
any idea of motor windings' capacitance to earth?

examine CT output with a scope during a start, if it's 180 hz you have an interesting situation.

just guesses

old jim
 
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top