The average power of AC is calculated using the formula IVcosθ, where I and V are RMS values and θ is the phase difference. In common applications like lamps and computers, it may be reasonable to assume a phase difference of zero, leading to a power factor (PF) of 1 for resistive loads. However, devices like fans and motors typically have lower PFs, which can vary significantly based on the equipment used. Higher power equipment generally has a PF above 0.8, while smaller devices may have a PF around 0.9, but this can fluctuate. Overall, while some assumptions can be made for specific types of equipment, caution is advised due to the variability in PF across different devices.
kelvin490
Gold Member
Messages
227
Reaction score
3
We know that the average power of A.C. is IVcosθ, where I and V are RMS and θ is the phase difference. I would like to ask in common application, such as power of a lamp, computer, fan etc. Can we simply assume the phase difference is zero and get a fairly accurate answer? Thank you.
 
Engineering news on Phys.org
I'm sure others with more knowledge in this area will post a better response. Power Factor for switching power supplies that qualify for UL or other certs control the PF so essentially (0 - EDIT, this should be 1) for that one. Incandescent light bulbs are for the most part (0 - EDIT this should be 1) as well. Fans or other motor appliances are probably not. There are/were devices that are sold to view the power factor (watt wizzard I think was one) and other devices that are suppose to compensate to yield lower usage for those devices.

So to answer your question, no I don't think you can assume a power factor of (0 - EDIT this should be 1) because one location may have many fans, or other devices that might cause a 5 - 10% difference. However, if your location is just electronics and lights you might be able to assume PF of (0 - EDIT this should be 1).

Others will chime in and provide a better answer.
 
Last edited:
  • Like
Likes 1 person
The power factor of a resistive or a perfectly corrected load is 1.00
The PF of a lossless inductor or capacitor is zero.

You can assume that all higher power equipment will have a PF better than 0.8
Very small items may have a worse PF but they will only be using small amounts of AC current.

So you can assume PF is 0.9 +/– 0.1 for any approved electrical product.
You can only assume for filament lamps and resistive element heaters that PF = 1.00
 
  • Like
Likes 1 person
Baluncore, thank you. Many years since I used PF remember the concepts, but the number slipped my mind. I should have looked up. Thank you for the correction.
 
  • Like
Likes 1 person
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...