How do AVRs handle unbalanced systems?

  • Thread starter Thread starter I_am_learning
  • Start date Start date
  • Tags Tags
    System
AI Thread Summary
AVRs typically sense line-to-phase voltage across all three phases to manage load imbalances. In cases of significant unbalance, such as one phase at 0.5 pu, the AVR would likely trigger protective relays to shut down the generator, as this indicates a critical fault. For minor imbalances, like 1.0, 1.0, and 0.8 pu, the AVR should ideally increase excitation to restore voltage levels. Larger machines often feature more complex control schemes, including manual and automatic settings to handle potential measurement errors. Overall, effective AVR operation is crucial for maintaining stability in isolated systems.
I_am_learning
Messages
681
Reaction score
16
(Referring to functioning of AVR on a system where an Isolated Synchronous Generator is supplying load to consumer)
What voltage do AVRs normally sense? I guess they must sense Line-to-phase voltage of all three phases. (and not just a single phase)
And when it detects that one phase is loaded and other phase is unloaded,
Say, the line to phase voltage reading of three phases comes out to be
A: 1 pu
B: 1 pu
C: 0.5 pu

What should AVR do now? Will it increase excitation slightly or what?
 
Engineering news on Phys.org
A large central station machine would be equipped with unbalance detection which would place voltage regulator to manual control, on presumption the unbalance was not real but caused by a failure in the metering circuitry.
a real unbalance that large would indicate something drastically wrong inside the generator and trip its protective relays, shutting it down immediately. ( i think on negative sequence, need a genuine power engineer to check me on that one.. Something that bad wrong would probably give differential too.)

a very small machine might only sense two phases.
it's common to sense phase AC for voltage control and phase B current for var control because they're 90 degrees out of phase, draw your triangle...
in which case your supposition could be right, regulator might try to raise voltage.
 
Last edited:
Thanks jim.
I agree that such a large unbalance would already trip some other protection circuit. So, let's talk about little less unbalance, say, 1.0, 1.0 and 0.8 pu.
For isolated system (used in places not fetched by the national grid), what type of AVR should be suitable?
I didn't quite get what you meant when you said -
" large central station machine would be equipped with unbalance detection which would place voltage regulator to manual control, [BOLD]on presumption the unbalance was not real but caused by a failure in the metering circuitry [/BOLD]."

In other words, ideally, what should the AVR be doing in such condition ?
 
the voltage regulator would see voltage decrease and try to raise it back up.

Some regulators sense all three phases , smaller ones only one.
So if regulator didnt look at affected phase it would remain oblivious.

it's a simple closed loop controller and you understanding is correct.

The bigger the machine the more elaborate the schemes to handle "What If's "


Most large regulators have a "manual" section called "BASE"
and an Auto section that adds or subtracts a small amount to BASE
and a null-meter that shows how much auto corection is applied.
That way if the auto quits or goes haywire you simply turn it off.
A huge imbalance would be interpreted as a measurement error and the automatic section would be automatically switched off.
Operators tweak the Base adjustment to keep auto-correction near zero so that should an unexpected transfer out of AUTO occur it will be bumpless.
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...