Russell Ensslin
- 18
- 0
What is the neutral wire? Why do we need that?
meBigGuy said:The current flows out of HOT and into NEUTRAL (through the load) while the voltage on HOT is POSITIVE. When the voltage on HOT momentarily goes to zero there is no current flow. Then, when the voltage on HOT goes negative the current flows out of NEUTRAL and into HOT (through the load). The current can flow into or out of NEUTRAL (through the load) depending on whether HOT is positive or negative voltage. The current can flow in either direction through the load. In almost all cases it doesn't matter to the load which way the current flows, which is why it can accept AC voltage directly, like a toaster or a filament light bulb. (we will skip the exceptions for now).
Russell Ensslin said:So if the Neutral is grounded near the source, won't that break the circuit? In other words; if the load comes from the hot leg to the resistance (application) then to the Neutral (ground) why do we call it the Neutral not Ground?
Russell Ensslin said:And why can't we ground it at the resistance like DC?
Russell Ensslin said:The application doesn't care if the load is positive or negative, as long as there is current carrying voltage back and fourth; or in one direction for that matter, as long as there is current.
davenn said:Greetings Russell
welcome to PF
"The neutral is connected to ground in several common places ..."
If the neutral connects to the ground then why not ground it at the device? Why carry the load back to supply after the application if it's going to be grounded before it gets back to the transformer?
Russell Ensslin said:If the neutral connects to the ground then why not ground it at the device? Why carry the load back to supply after the application if it's going to be grounded before it gets back to the transformer?
Yes. This is correct. I just wanted to post a couple of my favorite images from http://ecmweb.com/bonding-amp-grounding/grounding-vs-bonding-part-1-12jaus tail said:if there is any insulation failure in the appliance n if you touch the metallic edge, then leakage current may flow from appliance edge to ground through your body. but if the appliance is grounded, then the leakage current will flow through the ground wire.
a ground wire isn't supposed to carry current under normal conditions. though the secondary of transformer is grounded, current won't flow through it under normal conditions.
From the same website that I posted the previous images from ...jaus tail said:Current always flows through least resistive path.
Understanding how electricity flows through a circuitOne of the most dangerous ideas circulating in the electrical industry is that electricity follows the path of least resistance. But if it did, not a single one of our electronic gadgets would work.
You are asking a very important question here. You should go through all of the Grounding vs Bonding parts. I'll provide some quotes, followed by images, that I consider high points from those parts.jaus tail said:Thanks for the X1 to X0 to Ground then where? That what i was thinking while posting what i said. But then what happens in case of fault? Like when lightning strikes or in case of insulation failure of appliance where current leaks to the appliance body and could give the user a shock if the appliance isn't grounded.
Like the current indicated by green arrow in the diagram. That current goes to ground but doesn't return to the appliance from where it is leaking.
Maybe there must be two separate grounds: one at load end and one at secondary transformer:
![]()
Any insight would be helpful...
.The Earth's resistance is too great for it to be an effective bonding jumper. Very little fault current returns to the power source winding if the Earth is the only fault-current return path. ...
Properly grounding and bonding service equipment improves safety while eliminating a common cause of power quality problems. You just have to make the right connections in the right places. If you think in terms of providing a low-impedance ground-fault path back to the source, you'll have no problem.
The benefits of proper bonding include clearing faults, preventing shock, and reducing fires. Grounding provides a low-impedance path for lighting, and properly grounded systems operate as intended. Improperly grounded systems create fertile ground for power quality problems.
The preferred practice is to not use the grounded conductor (neutral) as the effective ground-fault current path. Instead, you should install an equipment grounding (bonding) conductor with the feeder conductors to the building or structure ...
this quote and image is from http://ecmweb.com/content/earth-not-bonding-jumper... electrons that leave a power supply are trying to get back to their source, not back to the earth. However, lightning is trying to get to earth.
... bonding jumpers tie the grounding system together through a reliable low-impedance path.
What is X1? X0? Is there an image somewhere?Windadct said:J-T -- the current needs to flow in a loop. If it goes X1 - X0 - Ground- then to where? -- Be careful with the thought "Current always flows through least restive path." - this can be misleading thinking that ALL of the current flows in the least restive path; when we have 2 or more paths the current will divide and the least restive will carry more current than the higher restive path.
Russel - the Neutral is part of the circuit normally, it is A (as opposed to the only) return path to the source. The process of grounding ( earthing) is primarily for safety, but has other benefits when well applied, such as affecting power quality, noise, etc.
Why would you think this?Windadct said:( but apparently my opinion here sucks)
Russell Ensslin said:So the un-spent electrons need to get back to the source? Is that it? If the electrons come out of the hot leg and go into the appliance and get spent as work why then does anything need to get back to the source?
Davenn said:In an AC system, the electrons don't really go anywhere, they just move rapidly back and forward about a point/position ( oscillate)
Your light globe in your house will never see the electrons that are moving in the wire in the generator at the power station
Russell Ensslin said:Does the ampacity start out with say 20 amps and then the vacuum cleaner use say 3 amps and then the remaining 17 amps return as spent current
that's right ... no amps are being spent, the number of amps going into a load is the same as the number coming out of the load back to the power supply.Russell Ensslin said:So if the Amps arent being spent then the voltage must be what is being reduced by some measurable amount.
Russell Ensslin said:So if an electron could be called a charged particle and the voltage could be considered the amount of that charge and the little booger only wiggles on the wire outside the appliance (never goes in) then the amount of charge (voltage) on the charged particle must be diminished.?
Russell Ensslin said:One ohm is zero resistance. Right?
start a new thread of your own with the above Q, rather than hijacking some one elses threadBringitondown said:Hi Folks,
Didn't know what other thread to ask this on.
I have an electrical power eng book which keeps referring to negative current with respect to thyristors. Am I missing something here, is there such a thing. Current always flows from high to low potential. So if your terminal voltage is reversed to allow current to flow in the other direction, it is still a positive current flow?thanks
Any suggestions.
Russell Ensslin said:I thought that the equipment grounding was the bonding to the ground fault current path to trip the breaker.