Boosting a petrol generator with a car battery?

Click For Summary

Discussion Overview

The discussion revolves around the feasibility of using a petrol generator in conjunction with a car battery to start a 2.2 kW electric motor, which may draw significantly higher current during startup. Participants explore various methods to manage the motor's startup load and the complexities involved in wiring and system integration.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant suggests using a car battery with a 12V-230V inverter to assist the generator during the motor's startup, but questions the complexity of the wiring.
  • Another participant mentions the need to phase the inverter and generator outputs together and inquires about the motor's specifications, such as power factor and whether it is single-phase.
  • Some participants argue that a battery may not be beneficial and suggest alternatives like a frequency changer or soft-start options for the motor.
  • Several participants emphasize that the generator's capacity must exceed 3 kW to handle the startup surge, with estimates suggesting at least 5-7 kW may be necessary.
  • One participant describes a practical experience with a generator barely starting a 2 hp air compressor, indicating that a larger generator is required for reliable operation.
  • Discussion includes mechanical solutions such as using a flywheel or a centrifugal clutch to manage startup loads, with some participants expressing concerns about the feasibility of these solutions.
  • There are suggestions for using NTC thermistors or SCR-based soft start circuits to limit startup current.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the best approach to handle the motor's startup load. Multiple competing views are presented regarding the use of batteries, mechanical solutions, and the necessary generator capacity.

Contextual Notes

Participants note the importance of understanding the specific motor load and characteristics, as well as the potential for complications in implementing various solutions. There are unresolved questions about the exact requirements and limitations of the proposed methods.

Who May Find This Useful

This discussion may be useful for individuals exploring options for starting electric motors with petrol generators, particularly in contexts where startup current is a concern.

hyphagon
Messages
7
Reaction score
0
TL;DR
Want to run an electric motor from a petrol generator but the startup load of the motor is too large. Could a car battery supplement the generator to start the motor?
Hi All,

So i am looking to buy a petrol generator to run a 2.2KW electric motor. I was thinking of getting a 3KW model which under normal conditions this should be ok - but on start up I've been told an electrical motor draws 6 to 10 times the normal load, which is way too high for the generator. So I am wondering if I could could hook up as well a car battery on a 12v- 230v invertor?

My logic is when the motor starts it draws on both the generator and battery, then once started only draws on the generator.

Is this possible and how complex would the wiring be? On a sidenote getting a more powerful generator is not feasible as it would require around 18KW which costs thousands!

Many thanks,
 
Engineering news on Phys.org
You would have to somehow phase the inverter and generator outputs together.

What is the motor spinning when it first starts? A heavy fan? Have a look into soft-start options for your motor.

Is this 240V single phase?

What is the power factor of the motor? This will be written as PF or cosΦ on the rating plate. Most generators will allow for a start-up surge, so you won’t need an 18 kVA (note units and research!). You may, however, need a bit more headroom than 3 kVA for a 2.2 kW motor.
 
  • Like
Likes   Reactions: sophiecentaur and Rive
Battery is no good. It can be done but more pain than gain.
In case you want to apply some overkill then you can add a frequency changer into the mix. But that's really an overkill. Better go with what @Guineafowl suggested.
 
  • Like
Likes   Reactions: sophiecentaur
It heavily depends on the motor load and if the motor is for example inverter driven and has a soft start.

As an example my little diy 3kw diesel generator can start and run my portable compressor, the same compressor will pop a 20A breaker (120V) if started when its cold.
 
  • Like
Likes   Reactions: sophiecentaur
I couldn't remember the motor, so quick google image search the compressor is:
1.1Hp continuous, 15A, 120V, 2pole induction machine.

The generator was load tested, will deliver 3kw continuous resistive load (heaters), but is over-fueling a little, anything much above that, the diesel starts to slow down and stall.

If the motor you want to start is 2.2kw mechanical output, then I would say 3kW generator is not enough, but 5-6kW should do the job.
 
I once had a gasoline generator rated 4 kW continuous and 4.5 KW peak. It would just barely start my 2 hp air compressor, then easily run the compressor up to its full rated pressure. It would easily start my 1.5 hp table saw. Extrapolating from that, a 2.2 kW motor would need a generator rated for at least 7 kW peak power.

Can you decouple the motor from the load, get it up to speed, then engage a clutch? A clutch can be as simple as a spring loaded idler pulley on a V-belt, such as is done on snowblowers. You would still need a generator larger than 3 kW.
 
jrmichler said:
I once had a gasoline generator rated 4 kW continuous and 4.5 KW peak. It would just barely start my 2 hp air compressor, then easily run the compressor up to its full rated pressure. It would easily start my 1.5 hp table saw. Extrapolating from that, a 2.2 kW motor would need a generator rated for at least 7 kW peak power.

Can you decouple the motor from the load, get it up to speed, then engage a clutch? A clutch can be as simple as a spring loaded idler pulley on a V-belt, such as is done on snowblowers. You would still need a generator larger than 3 kW.
^^^ This is why we need to know what the motor is driving. The higher end air compressors have an unloader valve that allows the motor to spin up before working against the pressure in the tank. A kind of mechanical soft-start.

As ever, you need to consider the whole system, not just the electrical side.

Edit: Where’s @jim hardy ? This would be just his cup of tea.
 
  • Like
Likes   Reactions: sophiecentaur
I have to agree - how to fix depends on the load. One " cheat" manually throttle the generator before starting the motor, or any way to get a flywheel on the generator shaft.
A VFD may also help.
But none of this may work on something like a compressor.
 
  • Like
Likes   Reactions: sophiecentaur
I think the flywheel solution is probably the only practical one. Allow the engine to wind up the flywheel with no load on the generator then apply the load. I would imagine that the generator could probably provide the initial high start current. It puts me in mind of the commentator at a Steam Traction Engine rally who referred to "instantaneous horse power", available from the massive flywheel, which was available when the engine was used as a Ploughing Engine and a large stone was encountered by the ploughshare.
On the whole, though, a bigger engine and generator are really what's called for if you want a reliable system. You could find long term problems with an overheated stator winding.
 
  • #10
From a physical point of view, a flywheel would be an elegant solution. However, obtaining a flywheel that somehow fits to a close-coupled genset and ensuring it’s properly balanced and doesn’t overload the running gear is going to be a challenge.

Also, the flywheel giveth, and the flywheel taketh away - assuming the genny is a pull-start, you’re going to need a thicker start rope!

We haven’t heard much from @hyphagon yet. Any thoughts?
 
  • #11
Guineafowl said:
assuming the genny is a pull-start, you’re going to need a thicker start rope!
A clutch could help sort that out and the flywheel could be external, on a separate shaft with a flexible linkage. It would need to be well bolted down and (of course) properly balanced. despite that, I am sure the mechanical solution would be the one to go for; the 'battery' idea would just be too problematical and probably very expensive.
I would do a lot of looking on eBay and Gumtree until something becomes available at a reasonable price and the smaller set could always be sold later to help with the cost. [Edit - if you just decide to upscale the installation]
Some people are 'mechanical' and some are not. Some have money to spend and others don't. The solution may or may not exist, depending on which combination the OP fits into.
 
Last edited:
  • #12
First, you have to find out the source of the problem. Is the motor start-up current due to the load connected or just the motor itself, or both.
One way to deal with the load is to use centrifugal clutch between the motor and the load. It would connect the load only when the motor reaches certain rpm.
If the problem is the motor startup current, you can limit that. One way is using NTC thermistors in series with the motor. They would limit the start up current but provide negligible resistance once hot.
Or use a SCR-based soft start circuit.
 

Similar threads

  • · Replies 5 ·
Replies
5
Views
5K
  • · Replies 11 ·
Replies
11
Views
2K
Replies
54
Views
12K
  • · Replies 74 ·
3
Replies
74
Views
10K
  • · Replies 5 ·
Replies
5
Views
3K
Replies
3
Views
3K
  • · Replies 14 ·
Replies
14
Views
8K
  • · Replies 23 ·
Replies
23
Views
18K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 11 ·
Replies
11
Views
6K