DaveE said:
That post was just wrong. And no, they can't happen with any passive load network in steady state, IMO. Of course that doesn't include transformers or other induced voltages.
But as I said, I'm a bit confused about what others mean when they mention them. It seems like a catch-all phrase like "stray" or "parasitic", but not literally circulating. OTOH, I suppose all currents circulate, what with conservation of charge...
Transformers are passive; do you mean resistive, as post #1 described?
What I mean by "circulating" is this: The delta of branches form a loop. If a positive current of the same value is added to the current in each branch of the delta, the directions of those added currents travel in the same direction around the loop--they "circulate" around the loop.
Post #1 made no mention of impedances or voltages, just line and phase currents. It is possible, given only the phase currents to determine the line currents.
The problem is underdetermined (
https://en.wikipedia.org/wiki/Underdetermined_system), so the solution for the line currents is not unique; there an infinite number mathematical solutions, but the physics of the situation may rule out some, or all but one.
For example, if we have a vector of phase currents [1,2,-3] and transform that to line currents as I showed in post #19, we get a line current vector of [-1,5,-4] which transforms back to a phase current vector of [1,2,-3].
We can represent the 3 line or phase currents as a vector, for example phase currents [1,2,-3]. This vector has a Euclidean length (norm) of sqrt(1^2+2^2+3^2) = sqrt(14). If we add 1 to each current (this is adding a circulating current of 1) we have another solution, a current vector [2,3,-2], which has length sqrt(17), larger than the norm of the currents with no circulating current. Of all the infinity of solutions for the phase currents with line currents of [-1,5,-4], the one with no circulating current is [1,2,-3], and it has the smallest norm. AND, it is the only one that is physically possible if circulating phase current is impossible.
The same thing applies in the other direction.
Starting with phase currents of [1,2,-3], perform the transformation to line currents.
We get line currents of [-1,5,-4]; add 100 amps in the direction of the delta to each line current. Then we would have line currents of [99,105,96]. These line currents don't add up to zero, so they are physically impossible. But if we premultiply them by the transformation matrix to convert back to phase currents, we get [1,2,-3]; these added currents are ruled out as solutions by the physics of the situation, but they satisfy the math. Knowing only currents (no impedances, that is), the problem is underdetermined, and it has an infinite number of (mathematical) solutions, but all but one are ruled out by the physics of the circuit if circulating current is impossible.
As an aside

, can you answer Baluncore's question in post #23: "Why do you deny the existence of circulating currents in reactive AC systems ?"