Calculating Pump Rate for Open Loop Cooling System: Basic Model

AI Thread Summary
To calculate the required pump rate for an open loop cooling system, the heat generated by the device and the temperature of the incoming water are critical factors. The basic equation for flow rate can be derived from the energy balance, using the formula M=E/(c*deltaT), where M is the mass flow rate, E is the power removed, c is the specific heat capacity, and deltaT is the temperature change. To maintain the water temperature below a certain threshold, adjustments must be made for thermal resistance between the object and the water, which can necessitate a higher flow rate. For example, if the device dissipates 2W and the thermal resistance is 3C/W, the maximum allowable temperature for the water must be recalculated to ensure effective cooling. Understanding these relationships will help in determining the necessary flow rate to keep the system within desired temperature limits.
JaredC
Messages
3
Reaction score
0

Homework Statement


I am trying to find out the rate at which I need to pump water into a device generating a specific amount of heat to keep it at a low temperature. I have not taken thermodynamics yet, and so I am trying to use a very basic model. The water is pumped through a copper pipe.

I know the following:

- Temperature of incoming water
- length and diameter (both inner and outer) of the copper pipe
- The total heat being generated by the device

I am looking for an equation that will have these as independent variables and give me the needed flow rate of the water.

Again I am looking for a ballpark answer, so if there are some other assumptions I have to make, like uniform heating, I can get away with it.

Homework Equations


unkown

The Attempt at a Solution


I have tried looking around the internet but am not familular enough with the material to know what I am looking for.

Any help would be greatly appreciated, even if it's just pointing me in the right direction.
 
Physics news on Phys.org
You'll want to think of it in SI units, but one equation burned into my memory is BTU/hr=GPM*500*ΔT.
'500' is the weight of water (~8.34 lb/gal under standard conditions) * 60 (converting GPM to GPH).
1 BTU is the energy required to change the temperature of 1 pound of water by 1°F.
1 watt = 3.412 BTU/hr

Perform a Google search on "heat transfer copper pipe", and explore the results.
 
The energy required to heat water is...

E=MC*deltaT

Where
m is the mass
C is the specific heat capacity
DeltaT the temperature change

So rearrange...

M=E/(c*deltaT)

dm/dt=(dE/dt)/(c*deltaT)

dm/dt is the water flow rate in kg/s
dE/dt is the power removed in Watts or Joules per second.
 
@CWatters
How can I find out the change in the water's temperature? It seems like it would also vary with the change in flow.
 
JaredC said:
How can I find out the change in the water's temperature? It seems like it would also vary with the change in flow.

Yes it does.

Lets say you want the object to be kept below 45C. If you assume the object is in good thermal contact with the water then you don't want the water to exceed 45C. You say the incoming water temperature is known (call it 20C) so the change in water temperature must be less than the difference between these values

deltaT = 45-20=25C

The equation (in post #3) gives you the minimum flow rate required to stop the water rising more that that much.

In practice you may need a slightly higher flow rate to account for any thermal resistance between the object and the water. For example if the object dissipates 2W and the thermal resistance between the object and water is 3C/W then the max temperature of the water must be lower. Instead of 45 degrees the water must be..

45 - (2*3) = 39C

If the incoming water is still 20C then the change in water temperature must be kept down to

deltaT = 39-20 = 19C

Since deltaT is the denominator the equation shows you need a higher flow rate to achieve a lower deltaT.
 